I ran some tests today using my Turnigy Reaktor 300W on a 90Ah Winston cell to confirm the SOC versus different charge voltage data that I posted in page one of this thread.
In summary using a charge voltage of 3.60 volts at an end current of 0.45A (C/200) as my 100%SOC reference i found that.
3.70V(14.8V)@C/50 end current = 100.15%SOC
3.60V(14.4V)@C/50 end current = 99.94%SOC
3.55V(14.2V)@C/50 end current = 99.83%SOC
3.50V(14.0V)@C/50 end current = 99.68%SOC
3.45V((13.8V)@C/50 end current = 99.41%SOC
3.40V(13.6V)@C/50 end current = 98.91%SOC
Here are the details of my tests for anyone who is interested.
I first discharged the battery to around 80%SOC
I them set the charger to charge the battery to 3.40 volts with a charge current of 18A (C/5) and an end current 1.8A (C/50)
I then boosted the voltage to 3.45 volts. The cell took 0.447Ah (0.50%SOC) to go from 3.397 volts @C/50 end current to 3.448 volts @C/50 end current
I then boosted the voltage to 3.50 volts. The cell took 0.242Ah (0.27%SOC) to go from 3.448 volts @C/50 end current to 3.498 volts @C/50 end current
I then boosted the voltage to 3.55 volts. The cell took 0.135Ah (0.15%SOC) to go from 3.498 volts @C/50 end current to 3.549 volts @C/50 end current
I then boosted the voltage to 3.60 volts. The cell took 0.100Ah (0.11%SOC) to go from 3.549 volts @C/50 end current to 3.599 volts @C/50 end current
I then kept the charge voltage at 3.60 and changed the end current to 0.45A (C/200). The cell only took 0.052Ah (0.06%SOC) to go to the reduced end current
I then boosted the voltage to 3.70 volts and reset the end current to 1.8A (C/50). The cell took 0.135Ah (0.15%SOC) to go from 3.50 volts @C/50 end current to 3.55 volts @C/50 end current
This fits with my previous tests and fills in some holes it the previous data.
Simon
Try our solar cost and savings calculator
Charging efficiency LifePO4
Collapse
X
-
-
well I did not imply you should Top Balance on your working system. But if you want to know what the capacity of each cell is requires a Top Balance and full discharge. From that you can determine what the AH capacity is of the weakest cell and its 90% SOC is. Example let's say your cell ranges from 101 on the lowest, and 115 AH on the highest. You re-balance at the Bottom, then charge and put in 92 AH. Disconnect the batteries from the controller and inverter, and let it rest several hours. Then measure OCV and you have found the magic Float voltage number specifically for your batteries. That will be around 13.6 volts. Maybe as low as 13.5 or as high as 13.7.I have zero interest in top balancing. I'll charge with my Midnite classic to 13.6v. Then I'll remove the battery and use the pl8 to discharge at a 10 amp rate to 10v, recording the ah draw. I'll then reinstall the battery, charge to 13.8v and repeat. Sound like a reasonable test?
However that is time consuming and splitting hairs. So if all you want to do is charge to 13.8, go for it. Just remember it is not an exact science and not to get confused if you only end up with say a 5% difference. Your actual Full charge voltage can be as low as 13.7 and as high as 13.9.
Lihium batteries are no different than Pb batteries. To charge them fully is a voltage as low as 2.25 vpc to 2.45 vpc. It is a Range. To find the exact number for your batteries takes some experimenting to zero in on it. With PB batteries you just measure the Specific Gravity to find the right voltage. With LFP you have to do it with Discharge/Charge test. It is up to you to find out what you are willing to do and spend time doing it. In the end the difference in voltage is so small, you discover it was just splitting hairs and you end up finding the sweat spot at say 13.64 volts. You spent hours for a .04 volt difference which your controller does not have the resolution to obtain. Been a while since I worked with Midnite Solar, but if I recall correctly you set to 13.6 or 13.7 volts. There is no 13.64. or 4-digit resolution. .
Leave a comment:
-
I have zero interest in top balancing. I'll charge with my Midnite classic to 13.6v. Then I'll remove the battery and use the pl8 to discharge at a 10 amp rate to 10v, recording the ah draw. I'll then reinstall the battery, charge to 13.8v and repeat. Sound like a reasonable test?Leave a comment:
-
Your PL8 is intended to be a Top Balance Charger. You can certainly use it for that or if you know how it works can use it another way.
Assuming you already have the initial balance, wire all the cells in series, make a Balance Plug, and Fully charge the Batteries using the Balanced Mode.. This is Top Balance and will charge every cell to 100% SOC. It will take the batteries to 14.4 volts and hold until current tapers to a set value. There are two ways you can do this. Either through the Balance Plug configuration A. Painfully slow. Best is Configuration B using the high current port, and finishes on Balance Plug. However you are going to need a Power Supply either way.
I assume you know how to operate the software. For Top Balance you need to figure out how much charge current your DC Power Supply can supply. Hopefully at least 10 amps or this is going to take a long time. 40 amps is perfect. So you are going to set the Charge rate yto as high as youf DC power supply can go say 20 amps/
Set cell end voltage to 3.6 volts. Set End Charge current at 3-Amps
Charge you rbattery and it will be TOP BALANCED.
When done allow to rest a hour.
Now set up the Discharge to 10 amps and end 2.5 vpc.
Now when it discharged it stops when the first cell reaches 2.5 volts. That is your lowest capacity cell. The other 3 will still have capacity left. That is Top Balance failure. All you are going to know is what the weakest cell capacity is and that dictates full Capacity of the pack. If you use this method, you loose your Bottom Balance.
From there connect all cells in Parallel and reblance.
So if you weak cell is say 95 AH you have your TARGET. Once you Bottom Balance again, connect the cells back in series and use the PL8 only using the High Current function and no Balance plug. Charge until you pump in .either 95 AH of the weakest cell or 95% of the weakest cell should get it to roughly 90%. Disconnect and allow to rest. Measure OCV and see exactly what 90% OCV SOC is for your batteries. It is going to be around 13.6 volt +/- .05 volts.
If you are really curious and want to know every cell capacity charge each one to 3.6 volts current taper to 3 amps. Discharge at 10 amps to 2.5 volts and note Capacity of each cell. Find th elowest capacity cell say 98 AH and not it.
Perform Bottom Balance again and then connect back in series. If 98 AH is th eweakest you want to pump in roughly 90 AH to get to 90% or 88 to 89 AH. Let th epack rest and note OCV. Shoul dbe around 13,6 volts +/- .05 volts.
Those two methods are the only way to find the exact OCV for your batteries. But I can tell you this. It is a waste of time splitting hairs, but will teach you something, but maybe worth it. I have done it and never again. I know Bottom Balance, Float to 13.6 volts is close enough. I do not worry about 1 to 3% inaccuracy splitting hairs.
What you will learn is it is important to just monitor cell voltages from time to time when they near fully discharged and nearly fully charged. Sooner or later a cell is going to crap out. You cannot stop it and will need replaced. Don't sweat the littttle details. When charged up look for 13.6 volts at 0 Amps with all cell voltages roughly 3.4 vpc, the weak one will be ever so slightly higher than the others and you know which one it is. Likewise let them ggo low from time to time down to 2.8 or so. They should all be roughly equal at the Bottom. A bad cell is going to stick out like a TranvestiteLeave a comment:
-
Your test is invalid with the LVD set at 12.7 volts, nor are you using meter quality equipment to measure Amp Hours. Use your PL8 and fully discharge to 2.5 vpc.
The only possible way to measure LFP or any battery capacity is a FULL DICHARGE TEST. Any other method is INVALID. 12.7 volts on your system is meaningless under any load or charge rate. You keep forgetting OCV.
By your logic you can take your fully charge 100 AH cells, put a 100 load on them and the voltage will fall instantly below 12 volts and conclude they are discharge when in FACT they are not even remotely close to being fully discharged. At 100 Amps would take 36 seconds to drop from 100 AH to 99 AH.
If you really want to measure the Capacity of the cells you are going to have to use your PL8. Fully charge the cells, discharge at 10 amps until cell voltage reaches 2.5 volts. Any other method is Invalid.
You keep getting stuck that battery voltage is an exact science of SOC. It is NOT, it is a Ball Park indicator only on a fully rested OCV. 3.4 vpc is roughly 90%, 3.45 is roughly 100%. You need to get past that and quit getting stuck.
I'm not opposed to doing this. Would I need to have the balance connector attached for the full discharge test on the pl8? Or can I just run the pack in series through the banana jacks?Leave a comment:
-
Your test is invalid with the LVD set at 12.7 volts, nor are you using meter quality equipment to measure Amp Hours. Use your PL8 and fully discharge to 2.5 vpc.
The only possible way to measure LFP or any battery capacity is a FULL DICHARGE TEST. Any other method is INVALID. 12.7 volts on your system is meaningless under any load or charge rate. You keep forgetting OCV.
By your logic you can take your fully charge 100 AH cells, put a 100 load on them and the voltage will fall instantly below 12 volts and conclude they are discharge when in FACT they are not even remotely close to being fully discharged. At 100 Amps would take 36 seconds to drop from 100 AH to 99 AH.
If you really want to measure the Capacity of the cells you are going to have to use your PL8. Fully charge the cells, discharge at 10 amps until cell voltage reaches 2.5 volts. Any other method is Invalid.
You keep getting stuck that battery voltage is an exact science of SOC. It is NOT, it is a Ball Park indicator only on a fully rested OCV. 3.4 vpc is roughly 90%, 3.45 is roughly 100%. You need to get past that and quit getting stuck.Last edited by Sunking; 06-20-2016, 06:05 PM.Leave a comment:
-
Hold it right there. In my video, I charged to 13.6v and discharged to 12.7v, withdrawing 48.5ah. Then I charged to 13.8v and discharged to 12.7v, withdrawing 50.0ah. Are you trying to tell me 1.5ah is 10% of battery capacity? It's not. It's 1.5% of battery capacity. According to your logic, I charged to 98.5% at 13.6v and 100% at 13.8v.
No Sir that is not accurate, you can fully charge the cells at 3.45 vpc or 13.8 volts on 4S. What is getting in your way is misinformation and misunderstanding what you are being told. This is Karaks issue and passing it on to you. There are a few ways to fully charge a Lithium battery, but you only need to know two of them to understand what is going on.
1. Is the Only way you and Karak knows and is spread around the Internet. It is the basis of every BMS system out there, and every Charger made specifically for lithium battery. It is the CCCV (Constant Current - Constant Voltage) method. Exact same method you use for lead acid batteries with 1 modification. You charge at Constant Current, say C/5/ C10, 1C whatever rate you want as long as it is greater than C/10 and 1C or less. You apply constant current until the cell voltage reaches 3.6 to 3.7 volts per cell (rather it is 3.6 to 3.7 depends om manufacture and model). Once you reach 3.6 vpc you hold 3.6 vpc until the charge current tapers to C/33 or 3% of C. For a 100 AH Cell would be 3 amps. Terminate charge and disconnect. Once you disconnect and allow the cell to rest the voltage will bleed off to roughly 3.45 volts which is 100% SOC OCV for LiFeP04. Let me say that again: Once you disconnect and allow the cell to rest the voltage will bleed off to roughly 3.45 volts which is 100% SOC OCV for LiFeP04. You need to understand if the resting Open Circuit Voltage is 3.45 volts the cell is 100% Got it?
2. Method 1 sucks for Solar. To use that method with solar means if you are charged up by noon, you disconnect the panels and they will not come back on till the next day. You are on battery power from that point on til next day. What a waste right? You could be utilizing solar power. You could use Solar power if the rest of the day instead of batteries if you FLOAT the batteries. Well you can Float the batteries, no problem at all. It is dome at OCV.
So the second method is choose a SOC OPEN CIRCUIT VOLTAGE point you want to operate at. There is that word again, OPEN CIRCUIT VOLTAGE. Remember? So if you want 100% set your voltage to 13.8 volts and forget about it. All FLOAT means is it is a CCCV algorythim, but we do not terminate the charge at any point. We just let it FLOAT. When the batteries reach 13.8 volts, current will taper toward 0 Amps. When it reaches 0 Amps the batteries are fully charged and Float. Panels are not disconnected. If you use power, the panels supply the power assuming the demand does not exceed what the panels can generate. You conserve battery power until the sunsets.
Now should you charge to 100%. Not IMO or any other person who knows about lithium batteries. We can double the cycle life by limiting to 90% SOC. Can you do that. Will heck yes you can silly, lower the damn voltage from 13.8 to 13.6 volts. Your GBS cells are fully charge with a OCV of 3.45 volts or 13.8 on 4S. 90% is roughly 3.4 vpc OCV or 13.6 volts.
Leave a comment:
-
Well you do need to build a Balance Plug, But if you intend to Bottom Balance, Dot not use any Balance Charging method or you effed up your bottom balance. The Balance plugg wil just monitor the cell voltaes and shut down if any cell goes outside a safe range.I followed this guy's procedure: https://youtu.be/J2WvQre8sAQ
I think it's probably fine, but I really should create a 4S balance connector for the PLCP8 so I can charge/discharge on the bench.
Bu tif you intend to Bottom Balance, you need to nail it perfectly and if you have the PL8 is the right tool to do it correctly, But it can only be dome one way to nail it. Connect your Inverter up and turn on as much load as you can for a fast discharge. Monitor the cell voltages. If one drops to 2.5 volts or less stop. If not let it run until your Inverter LVD operates at 10.5 volts. Your cells should rest at around 2.6 to 2.7 volts when th eLVD operates.
Pull the straps off and connect all 4 cells in parallel. Set the PL* to discharge at 10 amps to 2.4 volts. When the cells reach 2.4 volts, the PL8 will disconnect and the voltage will recover. Reset to 5 amps and 2.4 volts and repeat. Keep doing this until the cell voltages rested for a hour or two are 2.4 to 2.5 volts. Let them sit over night connected in parallel but nothing else connected.
THE DO NOT CROSS LINE is 2.0 Volts. Once the cells set rested at 2.4 to 2.5 volts is perfect Bottom Balance and ready to go.Leave a comment:
-
No Sir that is not accurate, you can fully charge the cells at 3.45 vpc or 13.8 volts on 4S. What is getting in your way is misinformation and misunderstanding what you are being told. This is Karaks issue and passing it on to you. There are a few ways to fully charge a Lithium battery, but you only need to know two of them to understand what is going on.I had to chuckle out loud at that. I think everyone else had good feedback too, for the record, but I do tend to find your explanations a little easier to parse. In everyone else's defense, I found myself referring to the battery as "full" a lot in that video, when I damn well know it's not really full unless I charge it to 14.4v. I understand why everyone describes it that way at 13.8 or 13.6 volts when the battery stops accepting amps.
1. Is the Only way you and Karak knows and is spread around the Internet. It is the basis of every BMS system out there, and every Charger made specifically for lithium battery. It is the CCCV (Constant Current - Constant Voltage) method. Exact same method you use for lead acid batteries with 1 modification. You charge at Constant Current, say C/5/ C10, 1C whatever rate you want as long as it is greater than C/10 and 1C or less. You apply constant current until the cell voltage reaches 3.6 to 3.7 volts per cell (rather it is 3.6 to 3.7 depends om manufacture and model). Once you reach 3.6 vpc you hold 3.6 vpc until the charge current tapers to C/33 or 3% of C. For a 100 AH Cell would be 3 amps. Terminate charge and disconnect. Once you disconnect and allow the cell to rest the voltage will bleed off to roughly 3.45 volts which is 100% SOC OCV for LiFeP04. Let me say that again: Once you disconnect and allow the cell to rest the voltage will bleed off to roughly 3.45 volts which is 100% SOC OCV for LiFeP04. You need to understand if the resting Open Circuit Voltage is 3.45 volts the cell is 100% Got it?
2. Method 1 sucks for Solar. To use that method with solar means if you are charged up by noon, you disconnect the panels and they will not come back on till the next day. You are on battery power from that point on til next day. What a waste right? You could be utilizing solar power. You could use Solar power if the rest of the day instead of batteries if you FLOAT the batteries. Well you can Float the batteries, no problem at all. It is dome at OCV.
So the second method is choose a SOC OPEN CIRCUIT VOLTAGE point you want to operate at. There is that word again, OPEN CIRCUIT VOLTAGE. Remember? So if you want 100% set your voltage to 13.8 volts and forget about it. All FLOAT means is it is a CCCV algorythim, but we do not terminate the charge at any point. We just let it FLOAT. When the batteries reach 13.8 volts, current will taper toward 0 Amps. When it reaches 0 Amps the batteries are fully charged and Float. Panels are not disconnected. If you use power, the panels supply the power assuming the demand does not exceed what the panels can generate. You conserve battery power until the sunsets.
Now should you charge to 100%. Not IMO or any other person who knows about lithium batteries. We can double the cycle life by limiting to 90% SOC. Can you do that. Will heck yes you can silly, lower the damn voltage from 13.8 to 13.6 volts. Your GBS cells are fully charge with a OCV of 3.45 volts or 13.8 on 4S. 90% is roughly 3.4 vpc OCV or 13.6 volts.
That is you not understanding exactly what you are being told and my failure to communicate. So let's see if we can get on the same page. You can take a lithium battery to 0 Volts with little or no damage. That is not what kills them. What kills them is being reversed polarity. So how does that happen should be your question?. Glad you asked.I remember asking you what happens if I pull the battery past a certain (I don't remember exact voltage, but it was intended to be battery EMPTY voltage, so... low) voltage under high amp load. You gave me a slingshot analogy and told me once I let it go I could never get it back.
The answer is simple, when adjacent cells still have capacity left in them to drive discharged cells negative below 0 volts. That is the fatal flaw of Top Balance systems. If you were to measure each cell capacity on the PL8, they are not equal. Tolerance is 10%. So your cells can range from 90 to 110 AH. You need to make sure you understand that point.
So we Top Balance your batteries and fully charge them to max capacity. You have 3-cells at 110 AH and one cell at 90 AH. OK now we discharge and we have discharged 90 AH. You 90 AH cell is now 2.5 volts, and the rest of your cells still have 20 AH capacity left in them so pack voltage is say 12.1 volts, and you are unaware you have a flat cell. It falls off the cliff and now have reverse current flowing through it and reverses polarity and is destroyed.
Realistically that is highly unlikely in a 4 S system, or even 8 and sometimes up to 16S. Reason is simple you have 1 cell with reverse polarity, and even if th eother 3 cells were fully charged at 3.4 volts only give you 10.2 voltts on the pack. Your Inverter turned off at 10.5 volts. You system will notice 3 volts missing on a 12 volt system. If you charge up and only see 10.2 volts you know something is WRONG.But what about say a 32, 45, or 100S system. 3, 6 or 9 volts low is not a problem at much higher voltages. On a 32S or 96 volt system full charge is 110 volts and discharged is 80 volts. So if you see say 100 volts is perfectly normal, but you could easily have 2 cells reversed and dead.
However what if we change the reference point to 0% SOC at 2.5 vpc? We know on a 4S system 10 volts is fully discharged. All cells have 0 AH at 2.5 vpc. When we charge them in series they all have the exact same capacity. Now when we discharge all cells arrive at 2.5 volts at the same time. No cell has the energy to drive the adjacent cell into reverse polarity. You eliminated the possiblity altogether. You would not even need a disconnect device, your Inverter shut off automatically at 10.5 volts or 2.625 vpc. Heck you could hook a load up to the cells and take pack voltage to 0 volts if you wanted.
So if you Bottom Balance, use an Inverter, and a external LVD you have 3 lines of deffence. First is th eLVD set to a extremely conservative 12 volts or 3.0 vpc with 10 to 15% capacity left in the cells. Second line of Defense is your Inverter shuts off at 2.625 vpc. If those two modes fail you Bottom Balanced and they cannot over discharge themselves anyway.
One caveat. Over a period of time, the cells age and can drift. That can be months or years. To protect yourself routinely check cell voltage at the Bottom and Top. Re-balance only as needed.
OK but it does not have Lockout or reconnect logic. Not that it matters. If you had somethin glike an Orion BMS, it is a PLC or Program Loop Controller.The Victron BP-220 LVD has a 90 second delay at a given set point voltage. I stated I would raise my set point because I'm not sure what 90 seconds at high amp draw will do to the battery's resting voltage. I figure I'll start high and work my way down until I'm as low as I can get while still being sure it won't damage the battery.
Well, yes and no. The BP-220 can accept an external signal to disconnect the battery. I was thinking I might try using the Victron BMV-700's AH trigger alarm relay output to send this signal. But yeah, if I use the BP-220 purely in voltage set point mode, it's going to operate off of the voltage sag, not the resting voltage. I understand that.
By default it will operate LVD if one of two conditions are met:
If any cell drops below 2.5 volts form more than 30 seconds.
If any cell drops below 2 volts for more than 2 seconds.
If the LVD operates, it LOCKS OUT the LVD until every cell is 3.3 volts or greater. Meaning it will not reconnect until you recharge the batteries. However the Orion BMS i sof the Top Balance mindset. But you can programm Top Balance to OFF and reprogram anyway I want. I do not use it. I use a PL8.Last edited by Sunking; 06-20-2016, 04:55 PM.Leave a comment:
-
Just watched you Bottom Balance video. Your Cell pro does not require you to discharge into another battery. It can do regenative charging, but that is not how you should be using it. Look at the Specs
Output battery discharge current: Internal discharge 10mA to 10A, 100W max Regenerative discharge 10mA to 40A, 1344W max**
The way to Bottom Balance with the unit is real simple.
1. Do the initial discharge like you did to get the cells near 2.5 volts. You got that part right.
2. Then connect all the cells in Parallel.
3. Then set your PL8 to discharge at 10 amps to 2.5 volts, connect it and walk away. You keep doing this until the cell voltage rest at 2.5 volts with NO LOAD aka OCV. Very important to get this right.
Additional If you have time you could have tested each cell capacity. The PL8 has a Cycle test. It can cycle 2 to 5 times fully charging each cell, and fully discharging each cell howevery many times you tell it to do that. Charge it at 40 amps, discharge it at 10 amps, or you can do it from a battery and regenerate. at 40 amps charge and discharge.
I followed this guy's procedure: https://youtu.be/J2WvQre8sAQ
I think it's probably fine, but I really should create a 4S balance connector for the PLCP8 so I can charge/discharge on the bench.Leave a comment:
-
I had to chuckle out loud at that. I think everyone else had good feedback too, for the record, but I do tend to find your explanations a little easier to parse. In everyone else's defense, I found myself referring to the battery as "full" a lot in that video, when I damn well know it's not really full unless I charge it to 14.4v. I understand why everyone describes it that way at 13.8 or 13.6 volts when the battery stops accepting amps.Well I hate to say it; But I told you so. You stated inconsistent answers being all over the place on Solar Panel Talk right? Who was right? It was Sunking. Now you know who to ignore. I watched your video and knew exactly what you were going to observe before you observed it.Been down that road years before you.
I think I was starting to come around to that realization. The voltage didn't seem very accurate and the SOC percentage seemed out of sync with the AH display.You do have a couple of wrong assumptions. No big deal, but you need to know.
1. Your Victron SOC meter is pretty much meaningless using voltage to determine SOC. Your Victron is made for Pb batteries. Secondly the discharge curve is so flat on LFP, there is no resolution. Only way you can really tell is with Coulomb Counting or counting AMP Hours in and out. However there is even inaccuracy counting AH and requires constant re-calibration. So use your Victron Coulomb Counter as your fuel gauge as an ball park indicator
I remember asking you what happens if I pull the battery past a certain (I don't remember exact voltage, but it was intended to be battery EMPTY voltage, so... low) voltage under high amp load. You gave me a slingshot analogy and told me once I let it go I could never get it back.2. This one is your most glaring error in your assumptions. You said if you draw more power like 1000 watts, to raise the LVD Set Point for higher drains. Wrong Sir, you lower it, not raise it. Your own observations should be telling you that.
All batteries have Internal Resistance. If you know Ohm's Law then you know Voltage = Current X Resistance. So when you draw more power means you draw more current right? Of course it does. If you draw more current through a resistance then you develop more voltage drop. You seen this with your very own eyes and noticed it because you talked about it. You said what the voltage was before you started your discharge test, and noticed the voltage sagged as soon as you turned on the Inverter. You also noticed the battery voltage rises as soon as you turned off the Load.
You can take your battery, fully charge it, set your LVD to 12 volts, and if you draw say 1C (100 amps), or even C/2 (50 amps) your LVD would operate immediately despite the battery being 100% charged up. Why the Internal Resistance of the battery and your wiring/connector resistance accumulated voltage loss. The GBS batteries have the highest Internal resistance of all the Chi-Coms. 100 AH cells are roughly .004 Ohms per cell. So 4 in series is roughly .012 Ohms. Add in wiring and connection resistance, and you are up close to .015 to .020 Ohms. So do some simple math. If you are running 50 amps with an Open Circuit Voltage of 13.6 volts - [50 amps x .02 Ohms] = 12.6 volts. At 100 amps drops to 11.6 volts.
You do not want to take your batteries below 2.5 volts per cell open circuit voltage. If using a LVD you would set it lower than 2.5. A good quality BMS like an Orion has some smarts. Its LVD defaults to 2.5 vpc for more than 30 seconds under load. That allows an EV to accelerate at some 5 to 10C or 500 to 1000 amps. The cell voltages will all drop well below 2.5 volts, but once up to speed the current backs way off and the voltagg egoes way back up above 2.5 volts up to around 3+ volts.
The Victron BP-220 LVD has a 90 second delay at a given set point voltage. I stated I would raise my set point because I'm not sure what 90 seconds at high amp draw will do to the battery's resting voltage. I figure I'll start high and work my way down until I'm as low as I can get while still being sure it won't damage the battery.
Well, yes and no. The BP-220 can accept an external signal to disconnect the battery. I was thinking I might try using the Victron BMV-700's AH trigger alarm relay output to send this signal. But yeah, if I use the BP-220 purely in voltage set point mode, it's going to operate off of the voltage sag, not the resting voltage. I understand that.So let's go back to what I told you originally Float your batteries at 13.6 to 14.2 volts, and set your LVD to 12 volts. 12 volts works great on a Solar system because you are not drawing high current. You need to understand the difference between Open Circuit Voltage and Loaded voltage. Your LVD is passive, it does not know the difference between OCV or Loaded voltagge. All it knows is disconnect at 12 volts.
I have no idea how to calibrate my coulomb counter or view that info on the victron bmv-700. I'll make it a point to acquire this knowledge. Thanks!At 12 volts leaves you lots of room becaus danger is at 10 volts and less. Only thing you need to check periodically is the voltage of the cells when discharged. and look for a low cell voltage. When you Bottom Balance the voltage should be equal at the bottom, not the top. So you need to look out for a cell dropping to low because it is possible, although extremely remote chance, you could have a cell go bad and never detect it from pack voltage. Example one cell at 2.5 volts and the other 3 cells at 3.2-volts you would read a pack voltage of 12.1 volts. I ran my first EV with the same cells you did for 6-months and never had any drift. I now use Nissan Leaf cells going on 8-months and no drift. I know other EV guys going on 4 years and no drift.
So going forward:- Keep an eye open and check cell voltages at the Top and Bottom and measure OCV, don't get hung up on Loaded or Charging voltages because that does not tell you much of anything.
- Set your LVD to 12 volts.
- Calibrate your Coulomb Counter ever 10 cycles or so because it will drift due to charge efficiency. More goes in than comes out and over a few cycles induce inaccuracy.
- Set you Midnite Solar Bulk = Absorb = Float = 13.6 to 13.8 volts
- Relax
Leave a comment:
-
Just watched you Bottom Balance video. Your Cell pro does not require you to discharge into another battery. It can do regenative charging, but that is not how you should be using it. Look at the Specs
Output battery discharge current: Internal discharge 10mA to 10A, 100W max Regenerative discharge 10mA to 40A, 1344W max**
The way to Bottom Balance with the unit is real simple.
1. Do the initial discharge like you did to get the cells near 2.5 volts. You got that part right.
2. Then connect all the cells in Parallel.
3. Then set your PL8 to discharge at 10 amps to 2.5 volts, connect it and walk away. You keep doing this until the cell voltage rest at 2.5 volts with NO LOAD aka OCV. Very important to get this right.
Additional If you have time you could have tested each cell capacity. The PL8 has a Cycle test. It can cycle 2 to 5 times fully charging each cell, and fully discharging each cell howevery many times you tell it to do that. Charge it at 40 amps, discharge it at 10 amps, or you can do it from a battery and regenerate. at 40 amps charge and discharge.
Leave a comment:
-
Well I hate to say it; But I told you so. You stated inconsistent answers being all over the place on Solar Panel Talk right? Who was right? It was Sunking. Now you know who to ignore. I watched your video and knew exactly what you were going to observe before you observed it.Been down that road years before you.
You do have a couple of wrong assumptions. No big deal, but you need to know.
1. Your Victron SOC meter is pretty much meaningless using voltage to determine SOC. Your Victron is made for Pb batteries. Secondly the discharge curve is so flat on LFP, there is no resolution. Only way you can really tell is with Coulomb Counting or counting AMP Hours in and out. However there is even inaccuracy counting AH and requires constant re-calibration. So use your Victron Coulomb Counter as your fuel gauge as an ball park indicator
2. This one is your most glaring error in your assumptions. You said if you draw more power like 1000 watts, to raise the LVD Set Point for higher current drains. Wrong Sir, you lower it, not raise it. Your own observations should be telling you that.
All batteries have Internal Resistance. If you know Ohm's Law then you know Voltage = Current X Resistance. So when you draw more power means you draw more current right? Of course it does. If you draw more current through a resistance then you develop more voltage drop. You seen this with your very own eyes and noticed it because you talked about it. You said what the voltage was before you started your discharge test, and noticed the voltage sagged as soon as you turned on the Inverter. You also noticed the battery voltage rises as soon as you turned off the Load.
You can take your battery, fully charge it, set your LVD to 12 volts, and if you draw say 1C (100 amps), or even C/2 (50 amps) your LVD would operate immediately despite the battery being 100% charged up. Why the Internal Resistance of the battery and your wiring/connector resistance accumulated voltage loss. The GBS batteries have the highest Internal resistance of all the Chi-Coms. 100 AH cells are roughly .004 Ohms per cell. So 4 in series is roughly .016 Ohms. Add in wiring and connection resistance, and you are up close to .020 Ohms. So do some simple math. If you are running 50 amps with an Open Circuit Voltage of 13.6 volts - [50 amps x .02 Ohms] = 12.6 volts. At 100 amps drops to 11.6 volts on a fully charged cells
You do not want to take your batteries below 2.5 volts per cell open circuit voltage. If using a LVD you would set it lower than 2.5 for high loads. A good quality BMS like an Orion has some smarts. Its LVD defaults to 2.5 vpc for more than 30 seconds under load. That allows an EV to accelerate at some 5 to 10C or 500 to 1000 amps. The cell voltages will all drop well below 2.5 volts under heavy load of accelerating , but once up to speed, the current backs way off and the voltage recovers back up above 2.5 volts up to around 3+ volts. That is just the nature of the beast and physics. If you were to set a EV to 3.0 vpc as you do with a solar system, you would never get it out of the garage.
So let's go back to what I told you originally Float your batteries at 13.6 to 14.0 volts, and set your LVD to 12 volts. 12 volts works great on a Solar system because you are not drawing high current. You need to understand the difference between Open Circuit Voltage and Loaded voltage. Your LVD is passive, it does not know the difference between OCV or Loaded voltagge. All it knows is disconnect at 12 volts.
At 12 volts leaves you lots of room becaus danger is at 10 volts and less. Only thing you need to check periodically is the voltage of the cells when discharged. and look for a low cell voltage. When you Bottom Balance the voltage should be equal at the bottom, not the top. So you need to look out for a cell dropping to low because it is possible, although extremely remote chance, you could have a cell go bad and never detect it from pack voltage. Example one cell at 2.5 volts and the other 3 cells at 3.2-volts you would read a pack voltage of 12.1 volts. I ran my first EV with the same cells you did for 6-months and never had any drift. I now use Nissan Leaf cells going on 8-months and no drift. I know other EV guys going on 4 years and no drift.
So going forward:- Keep an eye open and check cell voltages at the Top and Bottom and measure OCV, don't get hung up on Loaded or Charging voltages because that does not tell you much of anything.
- Set your LVD to 12 volts. You can even go lower if you want, but I would not go below 11 volts. 10 volts is pushing it.
- Calibrate your Coulomb Counter ever 10 cycles or so because it will drift due to charge efficiency. More goes in than comes out and over a few cycles induce inaccuracy.
- Set you Midnite Solar Bulk = Absorb = Float = 13.6 to 13.8 volts
- Relax
Last edited by Sunking; 06-20-2016, 11:39 AM.Leave a comment:
-
I doubt anyone who has participated in this thread so far really wants to watch this, but for posterity, if anyone stumbles upon this thread in the future, here's my LifePO4 battery capacity testing results: https://youtu.be/gMEbXG94vPc
And here are the preceding videos in the series:- Part 1 is about draining the battery to 12V: https://youtu.be/kFLFqpB-DAU
- Part 2 is about bottom balancing the cells: https://youtu.be/rZGLbAv2MCA
- Part 3 is about installing the battery: https://youtu.be/tLQ7TY5xeIs
- Part 4 is about charging via solar for the first time: https://youtu.be/dI36N79bnOE
Leave a comment:
-
PN I don't have any real issues with anything you have said except with this statement. There are a couple of ways to get to 100% on a LFP. Fastest way is to charge CCCV at .3 to 1C at 3.65 vpc or 14.6 volts on 4S. Even at the 1C rate is up to two hours on a fully discharged cell. At that fast of a rate you get to 14.6 volts in just under an hour, but you only get to around 60/70% when you hit 14.6 volts and takes a longer Absorb time till you taper down to 3% of C. Slow down to C/2 and you reach 80% at 14.6 volts, and spend less time in absorb. There is plenty of documentation that details that out and I can pass it along if you would like. If you use this method to get to 100% you have to terminate the charge and quit applying 14.6 volts. Great if you are charging an EV. Power Tools, Flashlights. etc. Not really a good way for Solar because you do not want to turn off th esolar and miss out on what remains in the day.
The other way to get to 100% or something less like say 80% to 90% is use Open Circuit Voltage set Point and use the same CCCV algorythim. That varies a bit depending on which manufacture you use. But for GBS 90% is around 3.4 vpc. You can float at that voltage and the SOC and voltage cannot possible go up when it saturates unless you have a Malfunction with your charger. You can charge as fast or slow as you want. For a Solar system if you follow reccomended practice of 3 day autonomy, you are going to be charging fairly quickly in excess of C/6 up to C/2. Using OCV Float charging works best for solar as it allows you to utilize all the power possible from the Sun in a day rather than cut-off solar at mid day.
Point to make here is a BMS is pretty much useless and not needed in this application. Not needed at all in 4, 8 and to some degree 16S systems. If you are only charging to OCV at 90% SOC, the dang BMS would never turn itself on. All you gotta do is an Initial Balance at whatever point you like, Top, Middle, or Bottom and forget about it.
If you have a cell go bad in a 4 or 8S system you are going to notice it right away. Either when charging when the voltage never reaches its normal high value, or immediately during any discharge with abnormally low operating voltages. 1 in 4 or 8 cells is going to catch your attention real quick especially when your Inverter trips off-line form under-voltage. Missing 3 volts on a 12 or 24 volt system is an attention getter. Guess what? If you have a bad cell guess what that means? Replace it.
A BMS does not stop that from happening, chit happens.
Edit Note:
As for further proof no BMS is required for solar 12, 24, and 48 volt solar systems look no further than Genasun Li MPPT controllers. They are Float CCCV controllers with only two ports. One for Panels and one for batteries. You could not interface a BMS if you tried. Well you could if you disconnect the panels or batteries. They use the same concept. they lower the output voltage. For LFP they float a little higher than I an comfortable with at 14.2 volts, but that is an easy fix, just order it to use a lower voltage if you want. The only protection they offer is HV shutdown in the event the controller fails. Other than that they stay on until the sunsets so you can utilize all the Sun Power as possible to conserve battery power. .Last edited by Sunking; 06-14-2016, 07:58 PM.Leave a comment: