It looks like this generator can handle 41 amps which isn't good because my wire can't. It's back feeding my panel through the dryer breaker which is a 30 amp but because the voltage is moving the opposite direction through the breaker I don't think I can trust it to trip.
Generator:
5000 watts
power factor 1
duty: continuous
voltage 120/240
amps 41.7/20.8
Try our solar cost and savings calculator
Golf Cart Batteries and Inverters
Collapse
X
-
It's generator power. 120/240v. It's THHN and will be laying on the ground and in the wall.
I asked about the wattage because when I did my load calculation it was in wattage so that I knew what generator I needed. I wasn't paying attention to the amps unfortunately.Last edited by BigRich; 09-09-2017, 09:12 AM.Leave a comment:
-
Most #10 awg wire is good for about 30 amps depending on the insulation type and how it is being run (open air, conduit, direct burial, etc.)
The problem is the voltage drop at 150feet. So what voltage are you using for that #10 wire.Leave a comment:
-
Not rated in watts. #10 wire is safe at no more than 30 amps. The lower your voltage, the more your losses will be.Leave a comment:
-
Does anyone know how many watts 150' of #10 wire is rated for?Leave a comment:
-
You can still run a smallish inverter for some lights and outlets. You will need a Transfer switch to connect gear to the generator, Fill your cars up, store some fuel (takes a lot of time to replace torn down power poles, and all the crews are in Tx) and hope flying debris does not do you in.Leave a comment:
-
I just Googled 3,000 watt 48 volt to 240 volt inverters. Holy cow they're expensive. $1,000. I don't see me buying one of those. It's too bad. I have all of these batteries and no other way of putting them to use.Leave a comment:
-
Thanks. The a/c's that I bought are for two rooms, the master and guest room. The larger unit draws 900 watts and the smaller unit draws 450 watts. Both units are sized for the room they'll be in. I need the a/c to sleep. Fans won't do it for us. If I have to I'll just run the generator all night.Leave a comment:
-
Whether it is Irma or not, now that you are thinking about it, seems a great time to get to know a Kill-A-Watt meter. Put it on the fridge and freezer for a week and get an accurate hourly average that will include the duty cycles, start-ups, etc. You can also measure your major hard-wired appliances by timing the digital (or mechanical) 'spinner' on most electrical service meters. I would bet you will be pleasantly surprised to find that your fridge and freezer are using a good deal less than their rated wattages.Last edited by AzRoute66; 09-05-2017, 02:25 PM.Leave a comment:
-
IMO I would think about using fans to keep cool at night then using A/C. Unless that A/C unit is very small it will eat up the batteries quickly.US Battery tech support says the batteries will last between 3 and 4 hours if I use 3,000 watts continuously. Of course the freezer and refrigerator won't run all the time and I would hope the a/c's will shut off after a couple of hours as well. So possibly that run time could double or even triple especially if i can cool the rooms down using the generator before I switch over to batteries. Which inverter would I need to be using?
I just tested my 2 generators and topping off my small battery system. I also live on the West coast of FL around the Clearwater area. My guess is that we could lose about 2 days of power if we get even a close call from Irma.Leave a comment:
-
US Battery tech support says the batteries will last between 3 and 4 hours if I use 3,000 watts continuously. Of course the freezer and refrigerator won't run all the time and I would hope the a/c's will shut off after a couple of hours as well. So possibly that run time could double or even triple especially if i can cool the rooms down using the generator before I switch over to batteries. Which inverter would I need to be using?Leave a comment:
-
Golf Cart Batteries and Inverters
Hi from Florida. I recently moved into a new house and with Irma headed this way have been forced to try to figure what to do if we lose power for a few days.
I have a 48 volt golf cart with (8) US 12V batteries. They are 77 minutes at 75 amps. I also have a 3,000 watt very loud generator that I don't want to run while we're trying to sleep.
I'd like to use the batteries if we lose electric to power my portable ac units, refrigerator, and freezer, while we're sleeping. Then during the day, I'd like to run the generator to charge them back up. The two ac's, fridge, and freezer use 2,755 watts.
Do you think this is a good idea or is there another way I should be approaching this? I'm trying to avoid dropping a few thousand on a Honda generator.Last edited by BigRich; 09-05-2017, 11:15 AM.