Thanks to you both..I knew this, but wanted to hear it from someone knows more than I do. Self doubt is a terrible affliction 😁 Thx.
Try our solar cost and savings calculator
Battery jumpers and lenghts.
Collapse
X
-
Ditto, what he said.
Leave a comment:
-
No, because the currents in all batteries in series configuration will be the same. The extra resistance of the longer cable will have the same (negligible) effect whether it's at the positive end of the string, the negative end, or somewhere in the middle.
Leave a comment:
-
If we can get back on topic of this thread.
The issue of different cable/jumper length in series banks plagues me. Sunking is it ok to have one or two battery jumpers longer in a AGM or Flooded bank in order to work around a difficult space that does not allow even rows.
will batteries in that bank be equal in charge and discharge? Will the longer piece not create a touch more resistance to that battery and the batteries thereafter?
N.B wire is sized correctly for load. i.e 35mm in this case on a 4kw inverter.
I know in parallel (which you should actually never do in a daily cycling system) dead even cables and correct termination are non neg..!Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
It's back. Whatever was done to remedy , Thanks.
Leave a comment:
-
Leave a comment:
-
I know where the caps lock key is. Will definitely use it next time.Leave a comment:
-
Leave a comment:
-
Flagging a spam post is best, but if you're not able to do that, one thing that's helped me is when someone responds with "SPAM!!!". Sometimes when looking through the new posts I'll miss the telltale wording of a spam post, but I never miss that all-caps proclamation. It's the next best thing if you can't "flag" a post for some reason.Leave a comment:
-
For some strange reason I don't have the flag tab . I'm going to try restarting my computer and see if it reappears.
Restarted , no difference....Strange.
Last edited by littleharbor; 08-13-2018, 10:59 AM.Leave a comment:
-
Leave a comment:
-
The spammers seen to have figured out how to get through, once again. Where's the flag tab?Leave a comment:
-
This was my understanding as well, but recently someone argued the point of voltage losses, and that battery 5 onwards would be slightly less, I then became unsure.
So to confirm, there is NO need to adjust cable size in a series bank for longer runs as I described before?
Sunking, your point re max amps are known and noted, inverter is 5kw, fuse is 120amp.
While we are on the subject of wire size (or AWG) and their max amp ratings, is there a table or post on the forum that shows these? And voltage losses at certain lenghts.Leave a comment:
Copyright © 2014 SolarReviews All rights reserved.