How to use load function on solar charge controller?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • ewarnerusa
    Solar Fanatic
    • Apr 2016
    • 142

    How to use load function on solar charge controller?

    Hello,
    I have never quite understood how the load function works on many solar charge controllers. For example, I'm looking at a 60A rated MPPT controller that offers a load function up to 20 amps. I know what a diversion load or dump load is to divert unused current into a heating element. But I don't think that is what these typical load functions on solar charge controllers do. Can someone explain it for me? Thanks!
    I'm an RV camper with 470 watts of solar
  • SunEagle
    Super Moderator
    • Oct 2012
    • 15143

    #2
    Usually the "load" output on a charge controller is for some low wattage lighting. Turning on the output is different for each controller.

    Comment

    • Bala
      Solar Fanatic
      • Dec 2010
      • 734

      #3
      I have a controller in my off grid system just for the load function. With this controller i can set low v cut out and a cut in v. Essentially i use it to switch off the non critical loads if there is not enough sun.

      Using relays and contactors i run a 240v pump on a timer, a 24v to 12v reducer, a 24 night light and v meter.

      Comment

      • littleharbor2
        Solar Fanatic
        • Jan 2016
        • 220

        #4
        Originally posted by Bala
        I have a controller in my off grid system just for the load function. With this controller i can set low v cut out and a cut in v. Essentially i use it to switch off the non critical loads if there is not enough sun.

        Using relays and contactors i run a 240v pump on a timer, a 24v to 12v reducer, a 24 night light and v meter.
        Sounds like a Trace/Xantrex C series controller in "Load Control" mode.

        For the loadout function on small charge controllers are meant for small, many times, timer controlled loads. Don't ever connect a big load like an inverter to this output, go straight to the battery.
        2 Kw PV Classic 200, Trace SW 4024 460ah,

        Comment

        • Bala
          Solar Fanatic
          • Dec 2010
          • 734

          #5
          Originally posted by littleharbor2

          Sounds like a Trace/Xantrex C series controller in "Load Control" mode.

          For the loadout function on small charge controllers are meant for small, many times, timer controlled loads. Don't ever connect a big load like an inverter to this output, go straight to the battery.
          No, its a Plasmatronics PL40. The load function is controlling coils on relays, so only milliamps of load on the circuit.

          Comment

          • ewarnerusa
            Solar Fanatic
            • Apr 2016
            • 142

            #6
            Originally posted by Bala
            I have a controller in my off grid system just for the load function. With this controller i can set low v cut out and a cut in v. Essentially i use it to switch off the non critical loads if there is not enough sun.

            Using relays and contactors i run a 240v pump on a timer, a 24v to 12v reducer, a 24 night light and v meter.
            What is the trigger for when load function comes on/off?
            I'm an RV camper with 470 watts of solar

            Comment

            • Bala
              Solar Fanatic
              • Dec 2010
              • 734

              #7
              Originally posted by ewarnerusa

              What is the trigger for when load function comes on/off?
              I have it set to turn off at 24v

              It will not turn back on until 28.2v

              It also had a 10 minute time delay, so a spike to low or high setting will not trigger.