Personally I hope you go with the 50 amp Victron since I'm hoping to hear how that works out.
And I personally wouldn't worry too much about the "3 day battery reserve", that's another case of applying off grid house thinking to an rv. But of course it doesn't hurt.
Also the link for your inverter isn't working for me. Is it a true sine wave inverter?Leave a comment:
-
The decision for an additional power source, like a generator, falls to every person. In most cases you can go for a couple of days without sunlight and not kill your batteries. But sometimes it could be many days without any significant recharging from solar due to the weather.
AKA. Since Saturday (5 days) we have had little to no sunshine here is West Central Fl. The forecast is calling for a couple more days of rain and clouds. My guess is that by the time this weather event ends I will have seen very very little sun for more than 9 days.
So if anyone was banking on the sun to recharge their batteries and live close to where I live, will be in for a big surprise unless they can find another source to charge them back up.
This is my strongest argument concerning solar when I try to convince people that there is always a chance of an extended loss of sunlight. If you put all of your chips on using solar to run your electrical devices you will one day end up in the dark.
So I say, yes you can use solar energy, but please at least prepare for the chance of not getting enough sunlight for extended times if you really need power for medical or critical loads and can't rely on the grid.Leave a comment:
-
Here is your calculation:
Do you see the difference?
If you can get comfortable with the idea of using a battery less than 400 Ah, you can stick with a (much less expensive) 40 A charge controller. As Sunking has pointed out, you don't need to plan for so much autonomy because you have another power source available (the alternator) to pick up the slack when solar is not available. As Wrybread and I have pointed out, with the pair of 320 W panels you have purchased, with decent exposure, you'll have enough power from the panels to minimize the amount of time you need to fall back on running the engine or tapping shore power, no matter what charge controller you choose.Leave a comment:
-
I'm going to take a look around at the Victron Mppt 100/50 charge controller and see what reviews and pricing I can get on it as well as some other MPPT in the 50a range or male 60a, just to see what's out there and pricing.
I see the diagrams they will be handy for wiring my system in and very easy to follow, I'm sure I will just have to make sure to size the wire and fuses according to my system.
I'm going to be mounting a small fuse board that will take the bigger blade fuses to put outside lights, inside lights and such. Would this be wired straight from the battery?
I like the idea of those fuses mounting right to the battery post cause its clean, easy to mount to the battery and if there is a problem I won't loose the wiring before the fuse. I Was thinking of putting a main power master switch off the positive battery to shut all power off to the system, or is that not needed?
Off that estimate of Battery Bank of 479 amp hours is that in total without 50% battery or after?
What do you think of this inverter? http://www.canadiantire.ca/en/pdp/mo...1866p.html#srp
I saw it come on sale, I've had many C tire inverters in the past for car trips and always worked great. Looking through reviews it looks like it does a great job for powering a little fridge and other things of my needs.
Leave a comment:
-
So how do you size the batteries. Simple you must know your daily watt hour usage and how many days of autonomy is. Guess what? You have not answered that question. Until you know that, you cannot build a system. At least not one you know will work and not cost a penny more than necessary. So when you figure out how many watt hours you need, the rest is simple.
5741 watt hours = Battery Bank of 479 amp hours, 390 watt in panels needed, running 2x 320 watt panels = 54 amp controller....
Leave a comment:
-
Sunking, it's one thing to disagree with people's equipment recommendations and approaches, but you're simply lying when you say this:
Your and wyebread way is to sit in the dark and wished you had done things differently
And by the way, I have a battery isolator in my RV, I've just never used it when I'm parked for weeks at a time, since I simply don't need to. I've never once needed to start the engine to charge up the batteries. What part of that do you not understand???
You can disagree with my equipment choices and all that, but please keep the discussion honest, so we can all learn from each other. Otherwise you're just subjecting people to your prejudices.
320 watts wasted and never seen or used
200 watts wasted and never seen or used.
if you size the batteries properly, you have no need for solar to begin with.
In the real world, solar is infinitely easier than plugging in and charging before a trip, especially if the trailer or camper isn't stored near shore power. And besides it gives the flexibility to stay on the road longer and for plans to change. Furthermore it's much safer for the batteries since you're far less likely to run them low. You really should stop acting like you have a clue about the real world factors involved in owning an RV.
It would be one thing if solar were really hard to build or really expensive, but it's dead simple and dirt cheap.
minus a whole bunch of cash you wasted on panels you do not need or doing you any good.
I think you should stick to Ohm's Law. When you go off script you simply have no idea what you're talking about, and are actively spreading misinformation.Last edited by Wrybread; 06-07-2017, 08:20 AM.Leave a comment:
-
No sir that is where wyebread lives. That is why he never needs a genny or alternate source of power like a $50 Isolator to save your butt when those cloudy days roll in and your batteries go dead.
You should try to think outside the box and know you are throwing tons of money away that gains you very little. Throwing 720 watts of panels into a 30-amp controller designed for 360 watts is a huge waste of money. There becomes a point you are wasting money and valuable space. Like I said I can see over powering up to a point say 400 and 500 is a stretch. You are recommending a full 100% over the line and that is just plain horrible advice, and well outside any standard practice.
Listing a minimum and maximum does not imply a recommendation. Despite the carelessness with which you typically recommend array sizes, I strongly encourage folks to look at where they are likely to put their panels before recommending a size (within that min-max range). Are the panels facing east and west? Mounted flat or mostly standing up? Lots of cloudy weather? Very hot or cold daytime temps? There are conditions which should push a recommendation toward the maximum, and others which push a recommendation towards the minimum.
The only responsible way I see to deal with all those variables is to present the range, and try to give guidance on how to select within that range. Cost effectiveness is one of those variables. Find a pair of 320 W panels on sale for $0.50 / W or less, delivered? Go for it. It might even cost less than the 400 W of panels you'd prefer.Last edited by sensij; 06-06-2017, 04:55 PM.Leave a comment:
-
The OP stated 2 to 4 days out just like wyebead says he does. Well guess what Sensij, if you size the batteries properly, you have no need for solar to begin with. My approach is sensible and gives the user the most bang for there buck and redundancy that completely escapes you. . Example with your 30 amp model.
400 watts Panel
30 amp controller
250 AH battery
600 watt Inverter
50 amp Isolator.
A heck of a lot less expensive, and if those cloudy days roll in you got backup power to recharge. Your and wyebread way is to sit in the dark and wished you had done things differently minus a whole bunch of cash you wasted on panels you do not need or doing you any good. My way is a much wiser and sound design with redundancy. I thought you were smarter than that. I can only guess your position being in the biz to sell more stuff and line your pockets with customer cash.
The OP wants the most bang for their dollar, meets their expectations, functional, and I am giving that to them. That is what I have always done, and its SAFE. You are pissing away money right and left. and no back up.Last edited by Sunking; 06-06-2017, 04:39 PM.Leave a comment:
-
You should try to get out of the STC box and look at real data from real PV systems sometime.Last edited by sensij; 06-06-2017, 03:46 PM.Leave a comment:
-
Some battery / charge controller / inverter combinations /PV power combinations to consider, depending on where you decide you want capacity to be, and the prices of equipment local to you. 12 V systems should pretty much collapse down to these options for most normal circumstances, I think.
30 A CC - Tracer 3210A
2 x Trojan T-105RE or 2 x Rolls S-290 = 225-230 Ah
2 x Rolls S-330 = 250 Ah
Max inverter = 600 W
Min PV power = 360 W
Max PV power = 720 W (depends on orientation)
320 watts wasted and never seen or used
40 A CC - Tracer 4210A
2 x Trojan L16RE-A = 325 Ah
2 x Trojan L16RE-B or 2 x Rolls S-480 = 370-375 Ah
Max inverter = 800 W
Min PV power = 480 W
Max PV power = 960 W (depends on orientation)
200 watts wasted and never seen or used.
50 A CC - Victron MPPT 100/50
2 x Rolls S-550 = 428 Ah
2 x Rolls S-605 = 468 Ah
Max inverter = 1000 W
Min PV Power = 600 W
Max PV power = 1200 W (depends on orientation) [4 x Canadian Solar 280 MS, wired 2S2P, for example]
Acceptable utilization of assets
Any of these is compatible with 2 x 340 W panels in parallel (or series assuming the controller can do it) , although you may be starting to get thin on PV power for the biggest batteries.
Leave a comment:
-
Batteries are the source of power, not the panels. 1 or two parallel strings of panels require no fuses, 3 or more do require fuses. The battery fuses are installed directly on the Battery Term Post. Otherwise they are worthless as you will leave unprotected wire between the battery term post and the OCPD. Like I said the schematic wiring does not change, just the values.
Last edited by Sunking; 06-06-2017, 03:10 PM.Leave a comment:
-
Some battery / charge controller / inverter combinations /PV power combinations to consider, depending on where you decide you want capacity to be, and the prices of equipment local to you. 12 V systems should pretty much collapse down to these options for most normal circumstances, I think.
30 A CC - Tracer 3210A
2 x Trojan T-105RE or 2 x Rolls S-290 = 225-230 Ah
2 x Rolls S-330 = 250 Ah
Max inverter = 600 W
Min PV power = 360 W
Max PV power = 720 W (depends on orientation)
40 A CC - Tracer 4210A
2 x Trojan L16RE-A = 325 Ah
2 x Trojan L16RE-B or 2 x Rolls S-480 = 370-375 Ah
Max inverter = 800 W
Min PV power = 480 W
Max PV power = 960 W (depends on orientation)
50 A CC - Victron MPPT 100/50
2 x Rolls S-550 = 428 Ah
2 x Rolls S-605 = 468 Ah
Max inverter = 1000 W
Min PV Power = 600 W
Max PV power = 1200 W (depends on orientation) [4 x Canadian Solar 280 MS, wired 2S2P, for example]
Any of these is compatible with 2 x 340 W panels in parallel, although you may be starting to get thin on PV power for the biggest batteries.Last edited by sensij; 06-06-2017, 03:19 PM.Leave a comment:
-
What you are wyebread do not understand is all components have to match to work with each other. A pair of Rolls S-550 requires:
Panel Wattage min = 600 watts, max 1000 watts
Controller size 50 to 80 amps
Max inverter size = 1000 watts
Now you say maybe S-290 and that changes everything.
Panel Wattage min = 275, max = 450 watts
Controller size 25 to 40 amps
Max Inverter size = 600 watts
So how do you size the batteries. Simple you must know your daily watt hour usage and how many days of autonomy is. The acceptable range so everything works together is 3 to 5 days. Guess what? You have not answered that question. Until you know that, you cannot build a system. At least not one you know will work and not cost a penny more than necessary.
So when you figure out how many watt hours you need, the rest is simple. Say you decide the number is 1000 watt hours. For a part time system you can go with 3 day autonomy which gives you 2 usable cloudy days of power before you have to shut down and wait for 2 sunny days to recharge.
AH = [3 days x 1000 wh] / 12 volts = 250 AH.
Panel Wattage is easy in an RV, you want a charge rate of C/10 to C/8, preferable C/8, and C/8 = 250 AH / 8 H = 31.25 amps.
Panel Wattage required = 31.25 amps x 13 volts = 406 watts.
Then you go shop for a 30 amp controller and 400 watts of panels.
Leave a comment:
-
Good to know about the inline fuses when using just two parallel panels, thanks for the great info as usual Sensij.
And to the op here's a link to the battery terminal fuses that Sensij is talking about. Note that these don't come with the fuses, but they're at the link too:
https://www.amazon.com/dp/B002INJXO6..._FJQnzbVV6CW6DLast edited by Wrybread; 06-06-2017, 09:28 AM.Leave a comment: