While most capital projects I have worked on either met or slightly exceeded the NEC regulations there were times when "just meeting the code" could have been improved by spending a little more. What I found was that while the design was good and the project succeeded with everything working correctly, sometimes the required maintenance to keep it all working wasn't performed due to budget constraints. So hardware failed earlier than expected. -
I agree with you. It is not worth to over spend when getting a quality installation for less works.
The problem I have run into my 40 some odd years of being a project manager is that the funding for the electrical side seems to take a back seat to the rest of the project. It sometimes takes a project that failed due to penny pinching that helps support my side and allows me to get the funding I needed for my portion.Leave a comment:
-
I agree with you. It is not worth to over spend when getting a quality installation for less works.
The problem I have run into my 40 some odd years of being a project manager is that the funding for the electrical side seems to take a back seat to the rest of the project. It sometimes takes a project that failed due to penny pinching that helps support my side and allows me to get the funding I needed for my portion.Leave a comment:
-
The problem I have run into my 40 some odd years of being a project manager is that the funding for the electrical side seems to take a back seat to the rest of the project. It sometimes takes a project that failed due to penny pinching that helps support my side and allows me to get the funding I needed for my portion.Leave a comment:
-
The phrase penny wise and pound foolish comes to mind. Probably also applies to planning, design and quality as well. Still, overdesign (or what ignorance may think is overdesign) to cover ignorance is never a substitute for knowledge and experience in practice.Leave a comment:
-
Call up SMA and ask them what is the best voltage drop % for longevity. Schneider Electric will tell you the same thing, as many others. As far as the companies that fund projects go. They only know the costs and have no caring for a proper system design. They only care about how much money they are going to make on each project. In the San Diego area we have seen many contractors go out of business due to the fact that they could not handle fixing the crap that they sold. This is a huge black eye in this industry. In solar, you get what you pay for. A not so good design and crappy installation will be cheap and will fail. A well thought design and a proper installation will harvest more energy, last longer and with fewer problems. I have tons of data to prove this. Price per watt is not the most important thing. A well thought out system with proper installation will cost a few more dollars up front, but saves the customer a lot more in the long run.Leave a comment:
-
Call up SMA and ask them what is the best voltage drop % for longevity. Schneider Electric will tell you the same thing, as many others. As far as the companies that fund projects go. They only know the costs and have no caring for a proper system design. They only care about how much money they are going to make on each project. In the San Diego area we have seen many contractors go out of business due to the fact that they could not handle fixing the crap that they sold. This is a huge black eye in this industry. In solar, you get what you pay for. A not so good design and crappy installation will be cheap and will fail. A well thought design and a proper installation will harvest more energy, last longer and with fewer problems. I have tons of data to prove this. Price per watt is not the most important thing. A well thought out system with proper installation will cost a few more dollars up front, but saves the customer a lot more in the long run.Leave a comment:
-
But based on the manufacturer spec sheets that I am familiar with unless the system is considered "critical operation" a 3% VD is not unacceptable for most equipment.
To add most if not all companies that fund a project will not do more than what the NEC requires due to the higher cost and longer payback. Unfortunately that is the normal way most companies run their business.Leave a comment:
-
Again, you are using code book thinking. In the field it is a different reality. And what I said is exactly what I see and repair on a daily basis. It does not hurt the equipment, it kills it prematurely. You guys need to think beyond code when performing a system design. Code is just a basic minimum guideline and systems installed using only that type of limited thinking will fail before they should.Last edited by ncs55; 05-04-2016, 09:23 AM.Leave a comment:
-
Sunking, what you say about voltage drop is straight from the code book. However, in real life a 2-3% voltage drop in either the dc or AC side is not even acceptable by most inverter manufacturers standards. In the real world and when you design a system for longevity, the voltage drop should be less than 1% by manufacturer standards. Wire is a small percentage of cost for residential systems and going 1 or 2 sizes larger is not expensive. A 2-3% voltage drop will cause more heat inside of the inverter and is one of the biggest mistakes that cause premature inverter failure. It is more expensive to have to replace an inverter than to simply follow a 1% or less rule. As far as the physics of electron flow and wire nicks. Thank you for your insight, and the only important thing for me, is using the correct size and type for the application, and to strip the covering carefully as to not Nick or cut the strands. Thank all of you for the physics lesson.Leave a comment:
-
Sunking, what you say about voltage drop is straight from the code book. However, in real life a 2-3% voltage drop in either the dc or AC side is not even acceptable by most inverter manufacturers standards. In the real world and when you design a system for longevity, the voltage drop should be less than 1% by manufacturer standards. Wire is a small percentage of cost for residential systems and going 1 or 2 sizes larger is not expensive. A 2-3% voltage drop will cause more heat inside of the inverter and is one of the biggest mistakes that cause premature inverter failure. It is more expensive to have to replace an inverter than to simply follow a 1% or less rule. As far as the physics of electron flow and wire nicks. Thank you for your insight, and the only important thing for me, is using the correct size and type for the application, and to strip the covering carefully as to not Nick or cut the strands. Thank all of you for the physics lesson.Last edited by ncs55; 05-04-2016, 08:51 AM.Leave a comment:
-
Stranded is easier to work with and for DC applications there is really no difference between both types , what's important is the voltage drop over my 20' and that is why I am using 6/2 instead of 12/2 from the panel, I did follow Sunking's advice and went with marine 6/2 just to be safe.
Morro of the story is be careful with over sizing. You want to limit losses to 2-3%. If Codes dictate 12 AWG minimum, but voltage drop calcs determine 10 AWG is required, going to 6 AWG is not gaining you anything meaningful and doubles the cost needlessly. I not only care about your safety and proper operation, I also care about your wallet and keeping the green in it.
Leave a comment:
-
Particularly with solid wire a nick forms a stress concentration which makes it much more likely that the wire will break at that point under bending and vibration.
Leave a comment:
-
What is conflicting, are that there are two theories currently taught about electron flow and or current flow, which is what I was trying to explain was taught to me.
There is nothing conflicting about wire stripping or the potential thereof. That was just an example of what I have been told by electricians in the past, more often than not.
As for what part of a wire current uses is well known. DC currents uses all the cross-sectional area, and AC Currents use the SKIN EFFECT. The higher the frequency to more pronounced the effect is.
As stated both electricians, technicians, engineers, and scientist use great care skinning a wire as to not nick or cut a strand as it affects mechanical strength. If it results in cutting a strand reduces current capacity and mechanical strength. Look in any high frequency application or Lightning protection and signal paths tend to be wide with a lot of surface area due to SKIN EFFECT. Power Frequencies 300 Hz and less) have very little Skin Effect.
Now there are special circumstances in Motors and Controls where High Stand Count in wires is important. Most DC Motors, and variable speed AC motors use a form of PWM that operates at High Frequencies of several Khz between 10 and 20 Khz.
But for the most part stranded wire is used sparingly because it is much more expensive, and larger than its solid counter part. Therefore it is reserved for larger sizes because anything above 4 AWG is impossible to work with unless your knuckles drag the ground when walking upright, in tight spaces, Lot of bends and turns, and vibration/movement is encountered.
I can only suggest is if you perceive conflicting information is you have been misinformed by people who do not know what they are talking about. Do a simple search Stranded vs Solid Wire, and Skin Effect. There is no conflicting information or theory. It is physical facts .
Hope that helps Norman.Last edited by Sunking; 04-29-2016, 02:25 PM.Leave a comment: