New 2 panel solar array questions...
Collapse
X
-
Ok so i got my MPPT Tristar CC (mppt45), i hooked it up to my 2 batteries (2x145aH AGM in parallel) and to my 2x lg panels (520W output power). I have installed a 50A breaker right before the positive terminal on the battery, am i also supposed to install one on the positive out of the solar array right before the CC, if so what size do i need to install? -
Hi abbas - Welcome to Solar Panel Talk!
RussLeave a comment:
-
my introduction
Hi,
I am abbas and new on the forum and have little or no information on solar panels, but i want to learn more. Hope you can help meLeave a comment:
-
Just curious, when you guys said "The batteries can not handle a 45 amp charge. They are too small for that and will get hurt. Use only one of those 260 watt panels not both." How do you calculate this?
Also i wont be doing this but am curious. If i wanted to tie these two panels into the electrical for my house is it as simple as just getting a grid ties inverter and plugging it into an outlet that can handle the amperage or is that incorrect?
Source for the above question:https://www.youtube.com/watch?v=YZKaZfEZHro
As inetdog states; those cheap grid tie inverters that plug in are illegal in the US and unsafe. Please do not even consider using them.
A grid tie system needs to meet your Utilities requirements and the local electric code. You can't do that by just putting in a couple of panels and an inverter.Leave a comment:
-
I am very glad that you will not be doing that.
The "plug and pray" grid tie inverters, in low wattages and intended to be plugged into a normal household receptacle, usually on an existing circuit, are totally illegal for use in the US and most other industrialized countries. They are a fire hazard and their efficiency is far lower than claimed.
The National Electrical Code does not allow for any method of connection for a PV GTI system other than hard wiring by an electrician.Leave a comment:
-
The "plug and pray" grid tie inverters, in low wattages and intended to be plugged into a normal household receptacle, usually on an existing circuit, are totally illegal for use in the US and most other industrialized countries. They are a fire hazard and their efficiency is far lower than claimed.
The National Electrical Code does not allow for any method of connection for a PV GTI system other than hard wiring by an electrician.Leave a comment:
-
Makes sense, thanks for clarifying. How about getting a grid tie inverter and connecting that directly to an outlet in my house? and if i were to get a grid tie inverter i would need to get something w/ at least 65v and 600w right? Just trying to wrap my head around that. Im still going to do the battery setup but i would like to learnLeave a comment:
-
Now with your 520 watts you can get up to 43 amps of charge capacity. So that 140Ah battery system would see a ratio of 140Ah/43amp = 3.25hr which is way too fast for FLA.
If you only use one 260 watt panel you can get 21.5 amps of charge. So now that 140Ah battery would see a 140Ah/21.5amp = 6.5h which is fast for a FLA battery but ok for an AGM type.
Battery Ah size needs to be "matched" to the solar panel wattage and charge controller. Too big or little on one side will either run your batteries down quickly or over charge them.
With a 245Ah battery and 520 watts of panel & MPPT charger you can get charge rate of 245Ah/43amp = 5.7h which while again fast for FLA should be ok for AGM.
Someone check my math because I am doing this without any coffee.Leave a comment:
-
Just curious, when you guys said "The batteries can not handle a 45 amp charge. They are too small for that and will get hurt. Use only one of those 260 watt panels not both." How do you calculate this?
Also i wont be doing this but am curious. If i wanted to tie these two panels into the electrical for my house is it as simple as just getting a grid ties inverter and plugging it into an outlet that can handle the amperage or is that incorrect?
Source for the above question:https://www.youtube.com/watch?v=YZKaZfEZHroLeave a comment:
-
Leave a comment:
-
I agree. I was thinking of you when I thought of that battery.
He didn't mention if any 6volt batteries were available so the single 12volt 245Ah (while very heavy) is sure better than two 12volt 125Ah in parallel. Even then that 520 watts of panels may be too much for that 245Ah on a really sunny day. But the OP got the panels first and now is trying to make them work.Leave a comment:
-
I agree. I was thinking of you when I thought of that battery.
He didn't mention if any 6volt batteries were available so the single 12volt 245Ah (while very heavy) is sure better than two 12volt 125Ah in parallel. Even then that 520 watts of panels may be too much for that 245Ah on a really sunny day. But the OP got the panels first and now is trying to make them work.
PS: My wife and i go to gym so carrying that heavy battery shouldnt be so badLeave a comment:
-
He didn't mention if any 6volt batteries were available so the single 12volt 245Ah (while very heavy) is sure better than two 12volt 125Ah in parallel. Even then that 520 watts of panels may be too much for that 245Ah on a really sunny day. But the OP got the panels first and now is trying to make them work.Leave a comment:
-
Leave a comment:
-
Yep the 245ah is an AGM battery. I may just get two of them and connect them in parallel if i can get some sort of discount on them if i get two, if not ill just get one. Thank you so much for all the input, i learned a lot todayLeave a comment: