Guys, trying to understand how to implement 690.47(C)(3) with SMA SunnyBoy TL-US-22 String inverter on my permit.
690.47(C)(3) - Combined Direct-Current Grounding-Electrode Conductor and Alternating- Current Equipment Grounding Conductor. An unspliced, or irreversibly spliced, combined grounding conductor shall be run from the marked dc grounding electrode conductor connection point along with the ac circuit conductors to the grounding busbar in the associated ac equipment. This combined grounding conductor shall be the larger of the size specified by 250.122 or 250.166 and shall be installed in accordance with 250.64(E).
The way I interpret the 690.47(C)(3) on SMA SunnyBoy TL-US-22:
1) Connect PV EGC to SunnyBoy grounding terminal in the DC Disconnect
2) Connect L1, L2 and N (White) to the SMA AC terminals and run them to AC Disconnect followed to Solar Breaker on Bus bar. N(White) goes to Neutral bus bar.
3) Connect #8 AWG Green CU on the Ground Connection of SMA inverter (not in DC disconnect) and run it to the to the service panel Ground busbar. This is continuous combined AC EGC and DC GEC per 690.47(C)(3).
4) Irreversibly Splice from combined AC EGC and DC GEC cable (above) a #8 AWG Green CU and run it to the AC disconnect.
Is the above correct? Can I run separate #8 AWG Green CU from AC disconnect to the service panel ground busbar so that I avoid splicing in step #4?
If I do the above steps, then I do not need a separate Grounding Electrode for DC side, correct?
Thanks,
Tomas
690.47(C)(3) - Combined Direct-Current Grounding-Electrode Conductor and Alternating- Current Equipment Grounding Conductor. An unspliced, or irreversibly spliced, combined grounding conductor shall be run from the marked dc grounding electrode conductor connection point along with the ac circuit conductors to the grounding busbar in the associated ac equipment. This combined grounding conductor shall be the larger of the size specified by 250.122 or 250.166 and shall be installed in accordance with 250.64(E).
The way I interpret the 690.47(C)(3) on SMA SunnyBoy TL-US-22:
1) Connect PV EGC to SunnyBoy grounding terminal in the DC Disconnect
2) Connect L1, L2 and N (White) to the SMA AC terminals and run them to AC Disconnect followed to Solar Breaker on Bus bar. N(White) goes to Neutral bus bar.
3) Connect #8 AWG Green CU on the Ground Connection of SMA inverter (not in DC disconnect) and run it to the to the service panel Ground busbar. This is continuous combined AC EGC and DC GEC per 690.47(C)(3).
4) Irreversibly Splice from combined AC EGC and DC GEC cable (above) a #8 AWG Green CU and run it to the AC disconnect.
Is the above correct? Can I run separate #8 AWG Green CU from AC disconnect to the service panel ground busbar so that I avoid splicing in step #4?
If I do the above steps, then I do not need a separate Grounding Electrode for DC side, correct?
Thanks,
Tomas