I am in the midst of an install and I am questioning the sizing of the AC disconnect for the inverter.
Inverter is an SMA SB20000TL, 277/480V, 3-phase. AC disconnect is 30A.
Inverter output is rated at 24A
Inverter Maximum permissible fusing is at 50A.
Our utili connection is 277V.
If we calc the short circuit current for the inverter at 277V, I get 90.25A
If we calc the short circuit current for the inverter at 480V, I get 52.08A
Both values are above the permissible fusing of 50A.
Note that the inverter has a listed output of 24A, which applied to the 1.25 s.f., gives us 30A, which I am sure is why the 30A disconnect was chosen and installed.
Please advise.
Inverter is an SMA SB20000TL, 277/480V, 3-phase. AC disconnect is 30A.
Inverter output is rated at 24A
Inverter Maximum permissible fusing is at 50A.
Our utili connection is 277V.
If we calc the short circuit current for the inverter at 277V, I get 90.25A
If we calc the short circuit current for the inverter at 480V, I get 52.08A
Both values are above the permissible fusing of 50A.
Note that the inverter has a listed output of 24A, which applied to the 1.25 s.f., gives us 30A, which I am sure is why the 30A disconnect was chosen and installed.
Please advise.