    Minimum panel size

    260 specs.jpg
    Morning,
    Can I charge a 24v battery with this panel?
    Sorry sent before realizing was not rotated.
    Cheers Mike
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    On a cold day - yes. But you may have trouble trying to Equalize the battery with it. A 24V FLA battery needs 30 - 32V for EQ. That's very close to the max the panel can produce.

    That panel would work for sure with a cheap PWM controller and give you about 8 amps

    With a really good MPPT controller, that will work down to 30V, you may get 9 amps output. (to do their power shifting, MPPT controllers need about 1.5 x peak battery voltage to work)
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Aussiemike
      Solar Fanatic
      • Mar 2017
      • 137

      #3
      Excellent. Just using some older battery's from another system and only need to run a few garden lights.
      Thanks Mike

      Comment

      • Aussiemike
        Solar Fanatic
        • Mar 2017
        • 137

        #4
        Just out of curiosity can I run a small 600w inverter with 4 x 20w out of the load terminals?

        Comment

        • chrisski
          Solar Fanatic
          • May 2020
          • 547

          #5
          Originally posted by Aussiemike
          Just out of curiosity can I run a small 600w inverter with 4 x 20w out of the load terminals?
          Not sure what you mean by this?

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #6
            Sure you can run a 600w inverter, but remember, you have to be able to recharge in 48 hours, what the inverter consumed. That may mean more panels. And the inverter will consume a not-insignificant amount of power
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • chrisski
              Solar Fanatic
              • May 2020
              • 547

              #7
              OK I understand now. To use 1800 watts AC on my inverter, I need to pull 2100 watts from the battery at a little over 10% loss. So that would be DC loads plus 10 to 15% loss, plus a certain amount of amps per hour to run my inverter. On the 2000 watt inverter I mentioned, it pulls 12 watts per hour or 288 watts a day just to be turned on.

              So may fix your flickering problem, but now you’d need a bigger battery and more panels than before.