Does This seem right?
Collapse
X
-
-
Comment
-
I don't know what meter he is using, but the diagram just shows AC voltage - doesn't list neutral anywhere. If he has the volt meter connected to both hots to read the ~240V and the CT where it is currently connected, he should get the correct power reading.Comment
-
I'm talking about the voltage sense, not the CT. He is measuring voltage so I don't think the meter is assuming anything. He just has the voltage sense connected to hot and neutral instead of hot to hot, so his power reading is half what it should be.Comment
-
So with 1 CT I will have to say the meter is looking for the "hot to neutral" measurement for the reference voltage of what the load is using.
A meter that will measure what a home is using from their 240 volt "single phase" main panel includes 2 CT's not 1.Comment
-
Comment
-
You might be correct but I thought those panels were connected to micro inverters which use both hot legs to produce their power.Comment
-
Yes, they use both hot legs, and the neutral is only used for voltage verification of each split phase. The current on each leg will be the same, so only one CT is needed - but the voltage needs to be measured across both hot legs to get the correct power reading.Comment
-
Here is an update with a meter on each 120VAC leg. This at about 11 AM in full sun.
I noticed that it took a few minutes for the meters to show any Amp reading.
I have reset the KWH to zero.
07-05-18--11am.jpgComment
-
Here is an update with a meter on each 120VAC leg. This at about 11 AM in full sun.
I noticed that it took a few minutes for the meters to show any Amp reading.
I have reset the KWH to zero.
07-05-18--11am.jpgComment
-
If you're going to run two meters then you will need to sum the power and energy readings to get the total. So in your picture you are producing 728W, which sounds reasonable for your panels. If you looked at the amp reading shortly after turning the power on, remember that there is a minimum 5 minute delay before the micros will generate power.
I am going to take readings at noon and 1 PM.Comment
-
Comment
-
Or the OP can use 2 of those meters (like he did) and sum the total wattage and amps to get close to the total production.Comment
-
Comment
-
Here is an update.
Readings-08-06-18.jpg
It has been a month now and here are the readings.
It appears that for the last 30 or 31 days, the panels have produced about 120KWH.
I would say that it has been about 25% more sunny than average this summer for the time period.
In Winter, there are many more cloudy days and some days the panels are covered with snow.
Since the panels are connected directly to my home power panel and I do not have
a meter that pays me for the generation of the power, I wonder if I am getting the full benefit.