    With the PoCo maintaining line voltage at or above the legal limit, operating net metering can be
    a problem. Power from the panel inverter will tend to push the voltage higher, and voltage drop
    in the local wiring just adds to the problem. It is not very hard to see voltage that will trip out the
    standard inverter line monitors, just when lots of energy can be stored.

    Solutions to this problem include
    1. Get the PoCo to lower their voltage
    2. Reduce on site AC copper voltage drop (bigger wires)
    3. Use inverters programmed for higher voltage
    4. Use an auto transformer to shave a few volts off the line voltage that inverters see

    Most of these have been tried here. Now the last one will be tested on another local
    system (much smaller than mine). This 600VA transformer will be used to reduce 260VAC
    line to about 230VAC to the inverters, shaving off about 30V at 14A.

    Bruce Roe

    HiLineAutoX.JPG
  • SunEagle
    Super Moderator
    • Oct 2012
    • 15125

    #2
    Hey. Where did you find my boat anchor?

    Comment

    • bcroe
      Solar Fanatic
      • Jan 2012
      • 5198

      #3
      Originally posted by SunEagle
      Hey. Where did you find my boat anchor?
      That 23 lb transformer started as a reject from an industrial battery charger co in the 60s, spent
      some time in a 600W DC power supply, moved to 5 different ILL locations, and now takes up a
      new mission as I clean house. Standby power is 10W, 23VA. Bruce