Problem installing PV system with battery and common generator

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #16
    Originally posted by PNW_Steve

    What is it that is different from the power generated from a "prime power" generator that keeps it from appearing the same as utility power?....
    Impedance. A generator has much higher impedance than a Grid. Some of the grid qualification testing involves frequency stability and some involves Grid Impedance. It's testing for 5 minutes, and only needs one fault to reset the clock. And if it does somehow pass, and your loads drop off, how does your generator deal with 5 or 10kw of power being pumped into it ? Will the inverter shut down first, or will the generator fry ?

    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Ben25
      Solar Fanatic
      • Jul 2014
      • 135

      #17
      I forgot about impedance... Inverters that are AC coupled are able to simulate this as well.

      Comment

      • ButchDeal
        Solar Fanatic
        • Apr 2014
        • 3802

        #18
        Originally posted by Ben25
        I forgot about impedance... Inverters that are AC coupled are able to simulate this as well.
        No need to simulate it. A bimodal inverter has batteries thus giving it all it needs to simulate a valid grid for the inverter that is AC coupled.

        OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

        Comment

        • Average Joe
          Junior Member
          • Feb 2019
          • 1

          #19
          It seems like a manual tranfer switch Would work fine. Power goes out then gen kicks in Maybe a yellow light comes in saying thst your on gen power. The gen dies. U go to a closet and flip a switch to easy. Maybe remove the gen wirei g completly hook it to a battery charge system And run off your system letting the gen assist the chargeing. Especially at night when there no solar and minimal use.

          Comment

          • Ampster
            Solar Fanatic
            • Jun 2017
            • 3649

            #20
            Originally posted by Average Joe
            It seems like a manual tranfer switch Would work fine. .......
            A manual transfer switch is what Mike 90704 suggested a month ago and we haven't heard from the OP since then.

            I suspect this is like a mini grid where the generator is connected at the HOA entrance and it has an auto transfer switch. If that is the case there is only one feed to the individual units. That feed is from the grid or the generator depending on the state of the auto transfer switch at the HOA entrance.
            Last edited by Ampster; 02-26-2019, 07:56 PM.
            9 kW solar, 42kWh LFP storage. EV owner since 2012

            Comment

            • solarhappy
              Junior Member
              • Feb 2015
              • 3

              #21
              Is water jetting under the driveway for a comm cable an option in lieu of digging it up?

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #22
                Originally posted by solarhappy
                Is water jetting under the driveway for a comm cable an option in lieu of digging it up?
                yes, but I'd put the cable inside conduit before connecting it to the transfer switch. That's the topic on this thread, Transfer Switch.
                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister