    battery bank disconnect

    I'm about to install a modest battery bank (48V/400amp hours) as part of my grid-tie with battery backup system, using the Outback Radian 8048A inverter. Do I need to install a disconnect switch between the battery bank and the inverter's load center, or will the circuit breakers in the load center suffice as a disconnect switch?

    The battery bank will be located roughly 6 feet from the load center. Should I install a fuse on the positive side of the circuit, right next to the battery bank, or will the circuit breaker in the load center take care of that as well?

    Thanks for your help.
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    If you protect the + & - cables well ( like each one inside it's own liquid tight flex conduit ) you could get by with just the breaker in the load center. Does your local electrical inspector need to inspect high power battery systems ? He may have a different opinion.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||