Hi i am newby to solar energy...hi i bought 4 pieces of them here 240 wats panels, and will make a 24-volt system with 4 units 12 volt 100 amp batteries ... can help me with conections chart (conect all 4 pannels to 4 batery ant use them on 220 volt inverter)...thanks
Announcement
Collapse
No announcement yet.
New solar with batery--12v or 24v???
Collapse
X
-
24 V is better for the battery, but those are 20 V panels. You'll need an MPPT charge controller to make this work efficiently. With a PWM, you'll be stuck with putting all the panels and batteries in parallel and operating as a 12 V system, turning those panels into the equivalent of 100 W each. What charge controller do you have?CS6P-260P/SE3000 - http://tiny.cc/ed5ozx -
i have this controller http://www.ebay.co.uk/itm/LCD-30A-MP...0AAOSwY45UPNMC
this is only 30 A and 760 wats on 24 volt...max input from solar panels is 48 volt...Comment
-
ok do I need a second controller... I can connect four panels in series and having four batteries in series on 24 or 48 volts ... can you recommend another controllerComment
-
I have used that charge controller. One thing I very much like about it is that you can change the LVD setting thereby greatly increasing battery life. It may be a Cheap Chinese knock off, but it's a good one IMO4X Suniva 250 watt, 8X t-105, OB Fx80, dc4812vrfComment
-
Oh yea, I forgot it only has a 40 volt input, would waste half of your panels.
4X Suniva 250 watt, 8X t-105, OB Fx80, dc4812vrfComment
-
I have another one that I have yet to test. about 30 bucks on fleabay. says it can take 100v in, but as I said I can not recommend since I have not taken the time to try it out.
http://www.ebay.com/itm/351238675473...%3AMEBIDX%3AIT4X Suniva 250 watt, 8X t-105, OB Fx80, dc4812vrfComment
-
Note: the LVD on this unit is pre-set at 10.5 volts, you should use a separate LVD to prevent discharging your battery bank below 11.9 or 23.8 volts4X Suniva 250 watt, 8X t-105, OB Fx80, dc4812vrfComment