I just got my two wattnodes mostly installed, still need to do the RS-485 connection to the inverter. One meter is an import/export meter, the other is a self-consumption meter.
Watching the LEDs on the import/export meter shows correct operation, or at least it seems to match-up with what my POCO's meter is showing, blinking green when I'm importing, red when I'm exporting.
However, the other meter that only measures what goes to the house is blinking nothing but red. I swapped the A CT, and the A phase blinked green. I have the white/black wires connected to the meter properly (check my pics). I turned off the inverters to see if maybe they were picking up noise from the feed to their panel, makes no difference.
Not sure if maybe this one is faulty, or what.
Watching the LEDs on the import/export meter shows correct operation, or at least it seems to match-up with what my POCO's meter is showing, blinking green when I'm importing, red when I'm exporting.
However, the other meter that only measures what goes to the house is blinking nothing but red. I swapped the A CT, and the A phase blinked green. I have the white/black wires connected to the meter properly (check my pics). I turned off the inverters to see if maybe they were picking up noise from the feed to their panel, makes no difference.
Not sure if maybe this one is faulty, or what.