  • Blowing fuses on commercial system

    Fair enough
    Last edited by rwest; 03-14-2018, 09:23 PM.

  • #2
    You are a pro on a DIY site asking questions how to troubleshoot? Bet your customer would like to know about this.

    You have a short on one of the strings. Disconnect all strings, then reconnect one string at a time until you find the bad string with a short. That is what a pro would do. It does not require any toys and should not take more than 30 minutes. .
    MSEE, PE