Unfortunately with your CC having a maximum DC input voltage of 145V and your panels having a Voc = 30.4v you would be limited to 4 of them wired in series. So with 14 panels that is going to allow you to use 12 of them (3 sets of 4).
The only way to use more panels would be to find a different CC that allows a higher DC input voltage or more total wattage.
I would say only 3 panels in series, because I have no idea how cold it gets (makes Voc go higher and fries electronics early morning at dawn)
The low voltage requires you to use expensive, heavy copper cables instead of 15 panels in a string with #10 cable. But your electronics can't handle the standard high voltage.
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
I would say only 3 panels in series, because I have no idea how cold it gets (makes Voc go higher and fries electronics early morning at dawn)
The low voltage requires you to use expensive, heavy copper cables instead of 15 panels in a string with #10 cable. But your electronics can't handle the standard high voltage.
Good point. Low temperatures will make a panel Voc go higher and have the potential of exceeding the CC DC voltage input.