    One MPPT 3 strings mixed panels

    Hi all,

    My question is as follows.

    Inverter 30 kWp

    2 x MPPT
    6 x DC connections for Strings 3 per MPPT

    At the moment the situation is as follows:

    MPPT 1 3 strings of 20 pieces of 265 Wp Panels Total 15,900 Watt

    MPPT 2 1 string of 20 pieces of 265 Wp Panels Total 5,300 Watt

    The connected panels above are all same brand same type
    I want to connect to the remaining 2 DC String connections

    2 Strings of 16 panels each. Each panel 260 Watt

    So one MPPT will operate with different strings. But each string exist out of the same panels.

    Is that smart to do?

    Curious to your answers

    Kind regards














  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    All the strings connected to a single MPPT input ( one or 3 connections, does not matter). If the strings are not matched equally, the MPPT will track the average of the lowest string,

    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • SupraLance
      Junior Member
      • Feb 2018
      • 27

      #3
      What's the Vmp, Imp, Voc, Isc of the panels?
      The way you propose to do it, the voltage of your single string of 265w pv will be pulled down to the Vmp of your 260w pv, lowering the output of that string.
      What is the rated capacity of MPPT1? Any chance of moving your other 20 265w panels to it so each MPPT has only the 1 size of pv?
      If not, what you propose is probably within the 5% tolerance, and depending how many watts you are losing, may be the most cost effective option.

      Comment

      • Bendesa1962
        Solar Fanatic
        • Nov 2016
        • 103

        #4
        Ok thanks for the answer Mike. I'm a bit confused. What exactly does that mean in this example? does it mean the MPPT will track on the lowest string in this case the 16 x 260 Watt. And it will loose the power of the extra watts in the string of 20 x 265 Watt? By the way I also asked GoodWe support about this question and they said it would not give any problems .....

        Comment

        • Bendesa1962
          Solar Fanatic
          • Nov 2016
          • 103

          #5
          Ok one more time the question with some more aditional info



          They also have a GoodWe GW25K-DT installed with only 21,200 Watt connected

          The GW25K-DT has 2 MPPT each MPPT can be connected to 3 strings

          At the moment the GW25K-DT is connected to

          4 strings of 20 panels each.

          3 strings connected to MPPT 1
          1 String connected to MPPT 2

          Each panel is 265 Watt same brand

          Voc 37,7V
          Isc 9,29A
          Vmp 30,7V
          Imp 8,64A

          MPPT 2 still has two DC string connections available.

          Can I connect two extra strings to MPPT 2 with the following specs all same panels same brand

          String 1 16 panels of 260 Watt each
          String 2 16 panels of 260 Watt each

          Voc 37,98V
          Isc 9,04A
          Vmp 30,63V
          Imp 8,49A

          All panels will be facing the same orientation and also have the same tilt.

          Comment

          • littleharbor
            Solar Fanatic
            • Jan 2016
            • 1998

            #6
            I would take the total of 52 panels subtract one, and create 3 strings of 17 panels. You will lose a small amount of potential output due to the small panel mismatch but your voltage between strings will be much closer.
            2.2kw Suntech mono, Classic 200, NEW Trace SW4024

            Comment

            • Mike90250
              Moderator
              • May 2009
              • 16020

              #7
              The string with the lowest voltage, limits the entire group on a single MPPT channel.
              It won't cause a problem for the inverter, it don't care.
              It will reduce your harvest by the amount of the mismatch. Your task is to shuffle things around to minimize the mismatch
              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||