If I can get breakers into this combiner box I ordered I will, otherwise this is what I'm planning. There will be 5 of these rows.
Serial PV.png
Getting ready for panels
Collapse
This topic is closed.
X
X
-
I looked at a few of those but couldn't find one that was 1) small 2) practical outdoors. I think I spent more time trying to find an alternative to the combiner box. Why can't I just combine my strings together like I have my batteries, along a busbar?
Edit: For that matter is it really necessary to use branch connectors and MC4? Using butt splices I could decrease the size of the PVC boxes planned to house branch connectors. Not sure why that would be frowned upon.
I understand that adding the overcurrent protection is a PIA and can be costly but in the end you will be saving you from replacing all of the panels that can be damaged if you don't have oc protection.Leave a comment:
-
Last edited by Sunking; 02-23-2017, 11:41 PM.Leave a comment:
-
I looked at a few of those but couldn't find one that was 1) small 2) practical outdoors. I think I spent more time trying to find an alternative to the combiner box. Why can't I just combine my strings together like I have my batteries, along a busbar?
Edit: For that matter is it really necessary to use branch connectors and MC4? Using butt splices I could decrease the size of the PVC boxes planned to house branch connectors. Not sure why that would be frowned upon.Last edited by -TX-; 02-23-2017, 09:56 PM.Leave a comment:
-
Midnight has some pre-fab combiner boxes, and I like using DC, Switch Rated Breakers instead of fuses. Touch-Safe fuse holders are just that, touch safe. They will arc ferociously if used to open a circuit under load
20160821_132247cc.jpgLeave a comment:
-
While the electric code mentions that a pv system with more than 2 items (panels or strings) in parallel require fuse protection for each "string", it really smart to protect your good panels if you develop a short on one set it could back-feed into the others, so the fuses are there to protect them.
You can build a combiner box like the one I made. It was not cheap but IMO it cost less to build then to purchase.
Leave a comment:
-
Texas. longest run is 10 meters, shortest is 3 meters. I've already ordered that cable which is fine if it works or not. Easy enough to test the furthest string once installed, and if it's too low changing to higher gauge for it alone won't be difficult.Leave a comment:
-
Leave a comment:
-
Hi. I used an online calc and it indicated that I should use 5awg for the longest run, but I'm going 6awg so I can buy a bulk 100'. By 'fused' are you being literal? This would be a solar combiner box and it looks like there are screws to secure the solar runs.
I chose these: http://www.ebay.com/itm/271885508220 because of their width. Specs are there but I went over them first with Midnite Solar (Classic 150).
I'm gathering the setup is ok, which is great.
You can build a combiner box like the one I made. It was not cheap but IMO it cost less to build then to purchase.
You do not have permission to view this gallery.
This gallery has 1 photos.Leave a comment:
-
Ha, thanks. I thought 5-6 was overkill but that calc disagreed. Never heard of anyone wiring their panels with 5 AWG!
Edit: Much better product at 50% savings. I like it! http://www.ebay.com/itm/400246316396
I still say use 1/0 or even better 750 MCM.
Leave a comment:
-
Ha, thanks. I thought 5-6 was overkill but that calc disagreed. Never heard of anyone wiring their panels with 5 AWG!
Edit: Much better product at 50% savings. I like it! http://www.ebay.com/itm/400246316396Last edited by -TX-; 02-23-2017, 06:50 PM.Leave a comment:
-
You are going to like this. OK you are using 2S 12 volt 165 watt panels right? That puts your Vmp = 36 volts and Imp = 8.8 amps. I will use 9 amps for for room and 2% voltage drop at 33 feet only requires:
10 AWG @ 1.7% Voltage drop
12 AWG @ 2.9% Voltage drop
You are pissing away a lot of money using 6 AWG which gives you 0.8% drop. In reality you will never be pumping 8.8 amps. More like 7 amps. Save some coins, weight, and space using 10 or 12 AWG. The smaller wire is a lot easier to work with. 12 AWG is good to 20 amps so safety is of no concern.
6 AWG cost $1/foot
12 AWG cost 20-cents/foot.
How many feet total for all 6 runs. Gets expensive real fast.
Since I own copper stock, I say use 1/0 AWG.Last edited by Sunking; 02-23-2017, 06:19 PM.Leave a comment:
-
Hi. I used an online calc and it indicated that I should use 5awg for the longest run, but I'm going 6awg so I can buy a bulk 100'. By 'fused' are you being literal? This would be a solar combiner box and it looks like there are screws to secure the solar runs.
I chose these: http://www.ebay.com/itm/271885508220 because of their width. Specs are there but I went over them first with Midnite Solar (Classic 150).
I'm gathering the setup is ok, which is great.Leave a comment:
-
First off you need to make sure each parallel "string" is fused properly in the combiner box.
Next you really should perform a voltage drop calculation for the longest "round trip" run based on the Vmp & Imp of the 2 series wired panels of that string and make sure it is less than 2%.
So what is the spec for each 165 watt panel? Vmp, Voc, Imp, Isc.
If the Voc is 22.81v then my guess is that each panel has a Vmp ~ 18v and an Imp ~ 9amps so it is very possible that #6 wire should work on the 10 meter run for a pair of those panels.Leave a comment:
-
Getting ready for panels
and looking for confirmation here. Is the following design ok?
This is an RV install
10x 12v panels @ 22.81 voc, 2S5P
Overall, 10 lines to combiner box. Longest run will be 10 meters, but I'd like to stick with 6awg for all runs.
Is this the best or even an acceptable way to do this? are there better options?
solar.png
Thank you
Leave a comment: