    Just come back from a site where the sunny boy 2000hf is not generating there is dc coming in and the 240 is good but it looks as though it's not
    Registering the dc ,could this be the varistors? The site is 100 mile round trip so will take some with me if it's a possibility. Anything else I should be looking for ?
    Many thanks bob

  • #2
    I doubt the varistors are in a DC circuit. or that they are replaceable. There is a 5 minute qualification period where the inverter tests the grid for stability and only then (if it passes the FQ, Voltage and Impedance testing) will it start up and backfeed the grid.
    Any glitches on the grid would prevent the inverter from starting up.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||