    We have a Park Model manufactured home that we will be living in while we build our off grid home. Is there a way to connect the cable from the main breaker panel(Square D 150 amp) to an inverter?
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    It depends if the main panel is designed for split phase 240VAC or single phase 120VAC. If you open the panel cover, does it have a single bus that all breakers plug into, or 2 bus, with alternate breakers contacting alternate bus ? (that would be 240 split phase, and not advisable).
    Also, mod sine inverters can't feed a grounded (per code) panel. You need a pure sine inverter.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||