  • Sunking
    replied
    Originally posted by DanKegel
    Completely useless information.

    Answer this GURU DAN. It is not a trick question. First year 2nd day electrical student test question.

    What is the total PF of a Desktop consuming .120 Kva with a PF of .83, plus a space heater consuming 2 Kva at a PF = 1.

    Once you figure out the answer, you will then know the article is nonsense and useless. Give you a hint the PF = .9905 or 1 which is as good as it gets. Very Simple high school algebra 101. PF = True Power / Apparent Power, so 2100 watts / 2120 Kva = .9905 PF.

    Leave a comment:


  • DanKegel
    replied
    I recently bought a Kill-a-Watt meter to measure power consumption of my devices. This was just a fun project for me. I put this on my Mac-Mini to see power consumption during various usage states ...

    may be of interest. One snippet from that exchange:

    -- snip --
    Utilities do care about power factor to residential buildings, but hassling them about it is more trouble than it's worth due to the relatively light load compared to serious industrial customers.

    Instead, the utilities hassle your legislators. It is logistically easier and much more cost effective for them to get laws passed to require certain power factors from devices commonly used by residential customers than to try to enforce or charge for low power factors from those customers directly. In the EU, for example, any electronic device drawing more than some specified amount of power (used to be around 70 W if I remember right, but I think the threshold has been lowered recently) must have a power factor above some limit to get CE certification. More and more electronic devices start with switching power supplies that do active power factor control, partially as a result of such laws emerging worldwide.
    -- snip --

    Leave a comment:


  • Sunking
    replied
    Originally posted by posplayr
    It would seem that large inductive loads like motors and compressors with synchronous motors are going to look inductive and it is these thing that represent the largest loads and would dominate the trusses in my carpenter's square. IS the power company going to charge me more if I don't have a flat roof?
    Utilities do not charge residential customers for VARS. Only large commercial and industrial users have to pay more for VARS.

    Leave a comment:


  • bcroe
    replied
    Electronic Switcher PF

    When you have an inductive load such as a motor, the current waveforms will be pretty much a sine wave;
    since they lag the voltage sine, you have power factor of less than one. A cap load has a sine current leading
    the voltage, so in those cases a cap load bank may also be connected to cancel the out of phase inductive
    current and bring the PF to near 1. That works because the dynamic sum of sine waves (of the same frequency)
    is another sine wave.

    When non linear elements such as diodes or switched transistors are used, current waveforms are created
    which are more like abbreviated pulses than sine waves. Creating the inverse of these waveforms is not
    practical, so they cause a nasty power factor. Caps are only really effective against sines.

    Adding more filtering in load inputs helps smooth out input current, at some cost. In recent years there
    has been recognition of the electronic switcher PF issue. Some switchers now include input circuits that
    cause the input current waveform to approach an in phase sine. These add cost; how widely these are
    deployed at this time, industrial or consumer, I can't say, but try reading the spec labels. Bruce Roe

    Leave a comment:


  • inetdog
    replied
    Originally posted by Michieme
    Oh I understand now I was always confused with volts and watts
    Originally posted by Mike90250
    What's the difference ? Simplistically, Watts are for DC, and Volt-Ampres is it's AC equivalent. VA factors in the AC voltage & current when they are out of Phase, and is a more accurate standard of the energy being consumed.

    Schneider Electric's APC division has many white papers & podcasts (see http://www.apc.com/podcast/ )
    They are mostly trying to sell you a larger UPS, but the same factors are also present in off-grid housing, with CFL lights running off an inverter. Many CFL bulbs are.6 PF, which is really lame, when you have to have a lot of inverter overhead to run a little light.

    Watts and Volt-Amps: Powerful Confusion (#15)
    PDF: http://www.apcmedia.com/salestools/S...NQYF_R0_EN.pdf
    MP3: http://www.apcmedia.com/podcast/content/wp/15.mp3

    Enjoy.
    I think that you understand the issue quite well Mike, but what you are saying is exactly wrong.

    VoltAmps (VA) is just the simple product of the RMS voltage times the RMS current, with no allowance for phase angle. It is useful for both AC and DC.
    The Watts figure (W) takes into account the phase difference between voltage and current (zero for DC or for an AC resistive load). and is always less than or equal to the VA number.

    One reason that VA is needed for AC work is that it tells you exactly how much current the conductors must be able to carry, even when the actual net power going over the same wires is close to zero.

    PF by definition (for sine waves anyway) is just Watts/VA, and so is a number less than or equal to 1.

    (That same information came right after Mike's original post back in 2012, but since the original was quoted here I am also repeating the correction.)
    Last edited by inetdog; 07-12-2015, 03:00 AM.

    Leave a comment:


  • Mike90250
    replied
    In the USA, residential power is not metered by PF, so there is no real point in correcting for it.

    Leave a comment:


  • posplayr
    replied
    Originally posted by Sunking
    Not possible to answer other than generically of .7

    My recollection is that equipment manufactures are supposed to keep Pf close to 1.
    False. PF keeps going lower and lower with Switch Mode DC Power Supplies now used in all electronic equipment. Your laptop or PC is runing near .5 PF

    Nope capacitor banks are useless. Complete Snake Oil.
    OK lets start over.

    It would seem that large inductive loads like motors and compressors with synchronous motors are going to look inductive and it is these thing that represent the largest loads and would dominate the trusses in my carpenter's square. IS the power company going to charge me more if I don't have a flat roof?

    I might have a few small switch mode DC devices, but I don't think that is going to change the pitch on my roof much is it?

    Leave a comment:


  • Sunking
    replied
    Originally posted by posplayr
    What is the typical power factor of a residential load.
    Not possible to answer other than generically of .7

    My recollection is that equipment manufactures are supposed to keep Pf close to 1.[/QUOTE]
    False. PF keeps going lower and lower with Switch Mode DC Power Supplies now used in all electronic equipment. Your laptop or PC is runing near .5 PF

    Originally posted by posplayr
    Finally I would gather if pF is off it is inductive so some capacitive trimming might be warranted in off grid. What works here?
    Nope capacitor banks are useless. Complete Snake Oil.

    Leave a comment:


  • posplayr
    replied
    I've read about as much of this thread as I can possibly handle about carpenter's rules; two questions:
    Does your power meter read true watts or VA?
    What is the typical power factor of a residential load. My recollection is that equipment manufactures are supposed to keep Pf close to 1.

    Finally I would gather if pF is off it is inductive so some capacitive trimming might be warranted in off grid. What works here?

    Leave a comment:


  • Michieme
    replied
    I get it now

    Originally posted by Mike90250
    What's the difference ? Simplistically, Watts are for DC, and Volt-Ampres is it's AC equivalent. VA factors in the AC voltage & current when they are out of Phase, and is a more accurate standard of the energy being consumed.

    Schneider Electric's APC division has many white papers & podcasts (see http://www.apc.com/podcast/ )
    They are mostly trying to sell you a larger UPS, but the same factors are also present in off-grid housing, with CFL lights running off an inverter. Many CFL bulbs are.6 PF, which is really lame, when you have to have a lot of inverter overhead to run a little light.

    Watts and Volt-Amps: Powerful Confusion (#15)
    PDF: http://www.apcmedia.com/salestools/S...NQYF_R0_EN.pdf
    MP3: http://www.apcmedia.com/podcast/content/wp/15.mp3

    Enjoy.
    Oh I understand now I was always confused with volts and watts

    Leave a comment:


  • SunEagle
    replied
    Originally posted by Sunking
    No PF =< 1, and VA=>W.

    VA = W/Pf
    W = VA x PF
    PF = W/VA
    Thanks Sunking. Formulas are so much easier to understand than writing them with words like I did.

    Leave a comment:


  • Sunking
    replied
    Originally posted by Naptown
    Since power factor is a loss wouldn't you divide by that?
    No PF =< 1, and VA=>W.

    VA = W/Pf
    W = VA x PF
    PF = W/VA

    Leave a comment:


  • SunEagle
    replied
    Originally posted by Naptown
    Since power factor is a loss wouldn't you divide by that?
    The power factor is the amount of watts divided by the volt amps. So watts = volt amps x the pf.

    Leave a comment: