Greetings,
I am upgrading an off-grid system and I would sincerely appreciate some input.
(4) FLA Trojan SPRE 12 225 = 48 V
DC Disconnect /Load Enclosure: Midnite MNDC
Inverter: COTEK SD2500-148 2500 Watt 48 Volt Pure Sine Wave Hardwire Inverter
I would like to get some help figuring out inverter breaker, cable and inline fuse size.
The Cotek manual recommends a 90 amp inline fuse and 4 AWG cable < 6ft. Bigger cable can be used for longer distance to avoid reducing inverter performance. I didn't want to post a link to the manual to avoid making the moderator's job harder.
What would be the best breaker choice between the following Midnite panel breakers: MNEDC90, MNEDC100 or MNDC125? Midnite breakers are reported to be rated for 100% continuous duty.
The breaker opening in my MNDC enclosure is 1.5 " wide, but I can always create an adapter to make either one of those breakers fit since they are smaller.
The wiring (under 6ft) from battery to inverter will be as follow:
Pos battery post - inline fuse near battery - breaker - inverter
Neg battery post - 500A, 50 MV DC Shunt - inverter
I would prefer to use a cable bigger than 4 AWG, if possible.What is the maximum size cable (THW) and corresponding inline fuse I could safely use based on that configuration?
Bonus - There will be no code or inspector to worry about, however being safe is a priority.
Thanks for reading, and possibly commenting.
Harry
I am upgrading an off-grid system and I would sincerely appreciate some input.
(4) FLA Trojan SPRE 12 225 = 48 V
DC Disconnect /Load Enclosure: Midnite MNDC
Inverter: COTEK SD2500-148 2500 Watt 48 Volt Pure Sine Wave Hardwire Inverter
I would like to get some help figuring out inverter breaker, cable and inline fuse size.
The Cotek manual recommends a 90 amp inline fuse and 4 AWG cable < 6ft. Bigger cable can be used for longer distance to avoid reducing inverter performance. I didn't want to post a link to the manual to avoid making the moderator's job harder.
What would be the best breaker choice between the following Midnite panel breakers: MNEDC90, MNEDC100 or MNDC125? Midnite breakers are reported to be rated for 100% continuous duty.
The breaker opening in my MNDC enclosure is 1.5 " wide, but I can always create an adapter to make either one of those breakers fit since they are smaller.
The wiring (under 6ft) from battery to inverter will be as follow:
Pos battery post - inline fuse near battery - breaker - inverter
Neg battery post - 500A, 50 MV DC Shunt - inverter
I would prefer to use a cable bigger than 4 AWG, if possible.What is the maximum size cable (THW) and corresponding inline fuse I could safely use based on that configuration?
Bonus - There will be no code or inspector to worry about, however being safe is a priority.
Thanks for reading, and possibly commenting.
Harry