Need Help Calculating Breaker Sizes For an Off-Grid System

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • SunnyIAV
    Junior Member
    • Apr 2019
    • 4

    Need Help Calculating Breaker Sizes For an Off-Grid System

    Greetings,

    I am upgrading an off-grid system and I would sincerely appreciate some input.

    (4) FLA Trojan SPRE 12 225 = 48 V

    DC Disconnect /Load Enclosure: Midnite MNDC

    Inverter: COTEK SD2500-148 2500 Watt 48 Volt Pure Sine Wave Hardwire Inverter

    I would like to get some help figuring out inverter breaker, cable and inline fuse size.

    The Cotek manual recommends a 90 amp inline fuse and 4 AWG cable < 6ft. Bigger cable can be used for longer distance to avoid reducing inverter performance. I didn't want to post a link to the manual to avoid making the moderator's job harder.

    What would be the best breaker choice between the following Midnite panel breakers: MNEDC90, MNEDC100 or MNDC125? Midnite breakers are reported to be rated for 100% continuous duty.

    The breaker opening in my MNDC enclosure is 1.5 " wide, but I can always create an adapter to make either one of those breakers fit since they are smaller.

    The wiring (under 6ft) from battery to inverter will be as follow:

    Pos battery post - inline fuse near battery - breaker - inverter

    Neg battery post - 500A, 50 MV DC Shunt - inverter

    I would prefer to use a cable bigger than 4 AWG, if possible.What is the maximum size cable (THW) and corresponding inline fuse I could safely use based on that configuration?

    Bonus - There will be no code or inspector to worry about, however being safe is a priority.

    Thanks for reading, and possibly commenting.

    Harry
    Last edited by SunnyIAV; 04-02-2019, 11:22 PM. Reason: Edited because post keeps getting truncated
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    Wire size determines the maximum breaker size
    4ga wire is good for 70A
    if you need 90A, you need #2 wire, to do it safely

    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • SunnyIAV
      Junior Member
      • Apr 2019
      • 4

      #3
      Thank you for replying Mike. By looking at the NEC table in the link, 4 ga corresponds to 85 A and # 2 = 115 A. I looked at the column for THW wire. Did the wire sizes you provided include derating?

      I am not exactly sure what I need, I would like to know the safest size wire I could use with matching fuses and breakers. The manual provides information based on 1 inline fuse between battery and inverter, but it doesn't take consideration of the additional breaker I will have in the DC enclosure. I have attached some of the specs , if that would help.

      Thank you

      Cotek_SD500_48V.jpg


      Attached Files
      Last edited by SunnyIAV; 04-03-2019, 07:52 AM.

      Comment

      • NewBostonConst
        Solar Fanatic
        • Nov 2018
        • 113

        #4
        You will also have to worry about going to big and the wire not fitting in where the connection is made.

        Comment

        • SunnyIAV
          Junior Member
          • Apr 2019
          • 4

          #5
          Thank you for replying. The inverter post can take a 2/0 lug without a problem. Strangely enough two 2/0 compression lugs were included inside the inverter box

          Comment

          • SunEagle
            Super Moderator
            • Oct 2012
            • 15125

            #6
            Originally posted by Mike90250
            Wire size determines the maximum breaker size
            4ga wire is good for 70A
            if you need 90A, you need #2 wire, to do it safely

            https://lugsdirect.com/WireCurrentAm...ble-301-16.htm
            Just for clarification that chart is for wires inside a raceway or direct burial. If they are being run in open air they can handle more amps then what the chart shows. There is another NEC chart for open air wire runs but for some reason I can't find it now but the #2 wire is definitely safer then the #4.