Upgrading from 4 to 12 panels, best configuration?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • mlsadler
    Junior Member
    • Feb 2019
    • 10

    Upgrading from 4 to 12 panels, best configuration?

    Hello Members am new on this forum but i need assistance, i had a solar system set up with four(4) 280W solarworld panels but am upgrading and have bought new eight(8) 290W solarworld panels and my panel total number is now 12 panels but of different wattages with a victron MPPT 150V 85A, am wondering what is the best panel array that will give me the lowest voltage drop working with a 48V battery bank system.
    Thanks
  • Yet another Yeti
    Banned
    • Feb 2019
    • 51

    #2
    There are newer and older versions available of this Victron string inverter .

    How many DC-inputs are available ?

    The one , that seems newer has 3 inputs .

    The guess is , that formerly there were 2 panels in a string and these 2 strings attached to different inputs .

    The victon does only accept 145/150 Volts-DC according to it s datasheed ,
    and therefore in a voltage range of 25-45 Volts of each PVpanel ,
    only up to three modules on a string would fit .

    The input voltage to start charging an attached battery needs to be 5 Volts over the battery s voltage .
    If the battery has 48 V , the panels need to deliver 53 V , and this is achieved by already two panels
    running in Standard Test Conditions and Normal Operating Conditions between 30 and 36 Volts .


    The best combination for the version with 3 inputs would be 2 similar modules in a row and then two of these rows
    in parallel , which would be perfect in colder climates , since the temperatures do not reach
    values , that pull down the Voltages of the PVs to lesser than battery voltage values .

    Input 1 : 2*2 280 W , 2*10 A
    Input 2 : 2*2 290 W , 2*10 A
    Input 3 : 2*2 290 W , 2*10 A

    As I understand the datasheet correctly , there are 30 Amps allowed each input , and 3*20 Amps is 60 Amps .


    One could also join all three 2*2 strings and attach these to one input .


    Asynchronic Setup for Voltages in the 25-45 V range in hotter climates :
    Input 1 : 1*3 280 W, 10 A
    Input 2 : 1*1 280 W + 2*290 W , 10 A
    Input 3 : 2*3 290 W , 20 A


    For the Amps and Voltages see the datasheets for your pvpanels ,
    which should be downloadable as .PDF s .

    Comment

    • mlsadler
      Junior Member
      • Feb 2019
      • 10

      #3
      There is only one dc input for PV and its + and -

      Comment

      • mlsadler
        Junior Member
        • Feb 2019
        • 10

        #4
        Here are the panel ratings

        280W Voc = 39.0V , Vmpp = 31.8V, Isc = 9.45A, Impp = 8.93A

        289W Voc = 39.6V , Vmpp = 31.9V, Isc = 9.75A, Impp = 9.20A

        Hope that can help

        Comment

        • Mike90250
          Moderator
          • May 2009
          • 16020

          #5
          Originally posted by Yet another Yeti
          1.) Two panels in series and 6 series joined to one cable make a parallel to attach to the inverter .

          2.) Three panels in series and 4 series joined to one cable make a parallel to attach to the inverter .
          ......
          BAD ADVICE. You can only safely parallel 2 panels. You are speaking from a place of ignorance.

          3 or more panels (or parallel strings) need to be paralleled with a Solar Combiner Box with fuses or circuit breakers that can isolate a bad string and prevent a fire.

          Mr Jr Member Yeti. Listen closely. Bad or Dangerous advice will not be tolerated on this forum. Our suggestion is to refrain from blurting out "good ideas" when
          you really have no idea. I really don't care about your ego. I do care about some neophyte that may follow your bad advice and die in a fire caused by your bad advice,



          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

          solar: http://tinyurl.com/LMR-Solar
          gen: http://tinyurl.com/LMR-Lister

          Comment

          • mlsadler
            Junior Member
            • Feb 2019
            • 10

            #6
            Hello Mike90250

            Thanks for the advise so would you advise me to do 2 panels in series and 6 parallel connections for the 12 panels?

            Regards

            Comment

            • Yet another Yeti
              Banned
              • Feb 2019
              • 51

              #7
              Originally posted by Mike90250

              BAD ADVICE. You can only safely parallel 2 panels. You are speaking from a place of ignorance.

              3 or more panels (or parallel strings) need to be paralleled with a Solar Combiner Box with fuses or circuit breakers that can isolate a bad string and prevent a fire.

              Mr Jr Member Yeti. Listen closely. Bad or Dangerous advice will not be tolerated on this forum. Our suggestion is to refrain from blurting out "good ideas" when
              you really have no idea. I really don't care about your ego. I do care about some neophyte that may follow your bad advice and die in a fire caused by your bad advice,


              Since when ? At the time of the release of this apparent old charge inverter , solar combiner boxes were apparently not invented , yet .

              MODERATOR: He/She has been warned previously about running amok at the keyboard without any clue as to the accuracy of the output.

              All postings by Yeti are suspect as to safety and accuracy.


              It appears , that this current over-protections were introduced somewhere around year 2010 .

              SO, if you have an old car without seatbelts, you should not use belts ever ? more bad information from yeti

              Do you think, that the installation of a "simple" battery charging inverter somewhere will result in unrecoverable losses ?
              Usual purposes for such kind of installations are small sheds and barns for chickens , or colony gardens ,
              but since gipsy-like living-conditions become more and more common , also for trailer dwellers .

              Inverters are waste parts , that unfortunately die after a while ; usual living-time for an inverter is considered 10 years .

              So , the TStarter should probably take into consideration to shift the inverter .


              Nevertheless , calculating 4*280w panels as rounded 1kW , and assuming 100Ah batteries in series
              Last edited by Mike90250; 03-20-2019, 07:49 PM.

              Comment

              • Yet another Yeti
                Banned
                • Feb 2019
                • 51

                #8
                a 12 Volts would make a battery of 4,8 kWh .

                1 kW solar would supply at 2/3rd STC and 1/5th charging losses around 550 Watts into the battery ,
                and at sunny days should fill it in around 8 hours having been deep cycled emptied .

                That there is the apparent need to add so much more Wattpower , indicates , that there is something
                not right with the sunshine conditions .

                When adding so much more solar Watts , the TS should probably add a second 4*12 V battery in parallel .

                Comment

                • littleharbor
                  Solar Fanatic
                  • Jan 2016
                  • 1998

                  #9
                  Looks like Mr.Yeti didn't comprehend the warning. Whatever he's talking about here sounds like gibberish.

                  Time for a time out?
                  2.2kw Suntech mono, Classic 200, NEW Trace SW4024

                  Comment

                  • SunEagle
                    Super Moderator
                    • Oct 2012
                    • 15125

                    #10
                    Originally posted by Yet another Yeti

                    Since when ? At the time of the release of this apparent old charge inverter , solar combiner boxes were apparently not invented , yet .

                    It appears , that this current over-protections were introduced somewhere around year 2010 .

                    ......


                    Nevertheless , calculating 4*280w panels as rounded 1kW , and assuming 100Ah batteries in series
                    It doesn't matter what the rules were before 2010. You now have to follow the latest regulations for your area even if you do not agree with them. So please stop posting stuff that can be considered dangerous or does not follow the electric code.

                    Comment

                    • Mike90250
                      Moderator
                      • May 2009
                      • 16020

                      #11
                      If the panel numbers are right:

                      Here are the panel ratings
                      280W Voc = 39.0V , Vmpp = 31.8V, Isc = 9.45A, Impp = 8.93A
                      289W Voc = 39.6V , Vmpp = 31.9V, Isc = 9.75A, Impp = 9.20A
                      I would run 3 panels in series if you are concerned about copper wire cost. That will save a bit on cable expenses

                      If you are in a area with hot days, I would run 3 in series. Panel voltage drops with increase in heat. Vmpp of 63V cannot be relied upon to allow a MPPT controller to fully charge a battery,
                      fully charging and EQ a 48V battery needs up to 65 volts.

                      And you need a Solar PV combiner with breakers or fuses, That's going to be a bit more money, but if you use breakers, you now have an easy diagnostic way to measure each string of panels for troubleshooting if needed

                      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                      solar: http://tinyurl.com/LMR-Solar
                      gen: http://tinyurl.com/LMR-Lister

                      Comment

                      • mlsadler
                        Junior Member
                        • Feb 2019
                        • 10

                        #12
                        Hello Mike

                        Thank you so much for that advise

                        regards