    Need help with wiring and fuses

    So still learning a lot about solar. I'm now reaching into uncharted waters with 4 panels. I'm hoping to hook up in parallel yeah? Can someone help me understand the connections I would need and fuses, how big and where?

    System:
    4 245w 37.3V 30.7Vmp 7.98Imp panels
    60a controller
    4 6v 210ah batteries wired for 24v
    800w 24v inverter

    I could run a mc4 branch from 2 panels at 30a 10awg
    and wire those 2 sets with mc4 branch 40a 8awg to controller right?
    and then fuse each panel, the controller, bank, and inverter?

    Or am I off a bit?
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    So, you are into the wattage range where you should be using a 40A MPPT controller. Wiring 4 panels in series to keep your wire gauge down, is going to set you too close to the 150V threshold for killing your controller, so you will need to run panels 2S2P (2 in series, 2 in parallel giving you 61V @ 16A )

    A PWM controller with all panels in parallel ( I hope you have not bought one ) will not have enough voltage, at 31v, to loose a couple volts to hot (being baked in the sun) and drop a couple volts in the controller, to be able to properly charge @ 30V and EQ 32V the batteries.

    If nobody else has a sketch, I'll make up one in the AM
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Alohasun
      Junior Member
      • Dec 2018
      • 6

      #3
      So basically the attached picture.
      20a fuse on each series pos line yeah?
      Match fuse size with controller on pos line yeah?
      Attached Files

      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15125

        #4
        Originally posted by Alohasun
        So basically the attached picture.
        20a fuse on each series pos line yeah?
        Match fuse size with controller on pos line yeah?
        OK. So if you used the 2s2p configuration with your 4 x 245 watt panels, your circuit would be 2 x the Vmp value of 30.7v or 61.4v and 7.89amps for each parallel string.

        The 61.4v is enough to charge a 24v battery system but with a PWM CC you can maybe 16 amps (2 x 7.89 = 15.78a) of charging or a C/13 charge rate which would be not enough for a 24V 210Ah battery system.

        If the CC was an MPPT then you could get 40 amps of charging (4 x 245w / 24v = 40.8a) or a C/5.25 charge rate which would be too high for FLA batteries and almost too high for AGM type batteries.

        With only 2 strings of panels you are not required to install any fusing between the panels and CC but if you wanted to install fuse you might be able to go with a 10amp for each string since the Imp = 7.89a
        Last edited by SunEagle; 12-30-2018, 07:17 PM. Reason: added last sentence

        Comment

        • Alohasun
          Junior Member
          • Dec 2018
          • 6

          #5
          Originally posted by SunEagle

          OK. So if you used the 2s2p configuration with your 4 x 245 watt panels, your circuit would be 2 x the Vmp value of 30.7v or 61.4v and 7.89amps for each parallel string.

          The 61.4v is enough to charge a 24v battery system but with a PWM CC you can maybe 16 amps (2 x 7.89 = 15.78a) of charging or a C/13 charge rate which would be not enough for a 24V 210Ah battery system.

          If the CC was an MPPT then you could get 40 amps of charging (4 x 245w / 24v = 40.8a) or a C/5.25 charge rate which would be too high for FLA batteries and almost too high for AGM type batteries.

          With only 2 strings of panels you are not required to install any fusing between the panels and CC but if you wanted to install fuse you might be able to go with a 10amp for each string since the Imp = 7.89a
          Yeah CC is MPPT. Thank you for reply.

          Comment

          • Sunking
            Solar Fanatic
            • Feb 2010
            • 23301

            #6
            No fuses are required or needed for panels in 2S2P configuration. Panels are current sources, not voltage sources. So with just 2 parallel strings, it is not possible to generate enough current to ever operate a fuse.
            Last edited by Sunking; 12-31-2018, 09:55 AM.
            MSEE, PE

            Comment

            • Alohasun
              Junior Member
              • Dec 2018
              • 6

              #7
              Originally posted by SunEagle
              If the CC was an MPPT then you could get 40 amps of charging (4 x 245w / 24v = 40.8a) or a C/5.25 charge rate which would be too high for FLA batteries and almost too high for AGM type batteries.
              What is the remedy to a better c rate for FLA batteries?
              less panel?

              Comment

              • Sunking
                Solar Fanatic
                • Feb 2010
                • 23301

                #8
                Originally posted by Alohasun

                What is the remedy to a better c rate for FLA batteries?
                less panel?
                C/10 to C/8 which is controlled by the right panel wattage paired with the right controller.

                With MPPT Controllers is pretty simple to get panel wattage in the ball park. A 200 AH battery requires 20 to 25 amps. Wattage = Battery Voltage x Charge Amps so a 48 volt battery is 50 volts x 20 amps = 1000 watts, up to 1250 watts. Unforrtunately you have a PWM controller, thus not enough panel wattage to get you to minimum requirements.

                MSEE, PE

                Comment

                • Mike90250
                  Moderator
                  • May 2009
                  • 16020

                  #9
                  Advanced MPPT controllers you can also set a max charge rate. So on a cloudy day, normally excess panels help your harvest
                  Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                  || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                  || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                  solar: http://tinyurl.com/LMR-Solar
                  gen: http://tinyurl.com/LMR-Lister

                  Comment

                  • Alohasun
                    Junior Member
                    • Dec 2018
                    • 6

                    #10
                    Originally posted by Sunking
                    C/10 to C/8 which is controlled by the right panel wattage paired with the right controller.

                    With MPPT Controllers is pretty simple to get panel wattage in the ball park. A 200 AH battery requires 20 to 25 amps. Wattage = Battery Voltage x Charge Amps so a 48 volt battery is 50 volts x 20 amps = 1000 watts, up to 1250 watts. Unforrtunately you have a PWM controller, thus not enough panel wattage to get you to minimum requirements.
                    CC is MPPT. Battery is 24v

                    Comment

                    • Sunking
                      Solar Fanatic
                      • Feb 2010
                      • 23301

                      #11
                      Originally posted by Alohasun
                      CC is MPPT. Battery is 24v
                      OK wire panels 2S2P. That wil get you roughly 40 amps of peak charge current at noon if the batteries are real low. A bit high, just keep an eye on water levels.

                      MSEE, PE

                      Comment

                      • Alohasun
                        Junior Member
                        • Dec 2018
                        • 6

                        #12
                        Originally posted by Sunking
                        OK wire panels 2S2P. That wil get you roughly 40 amps of peak charge current at noon if the batteries are real low. A bit high, just keep an eye on water levels.
                        Appreciate it.