I am looking to have solar power at my cabin used over the weekends and is approximately 750SF. The kicker is I bought a 24k btu mini split system before I thought of this. What are my options to achieve off grid power with generator backup? Will send some ideas a little later this evening.
Off Grid Cabin-Weekender-Air Condition
Collapse
X
-
-
You can run lights cheap enough, couple hundred bucks, a small panel, 1 battery, charge controller.
To run the 24K BTU, you are going to have to step that up a couple notches and likely be in for over $5KPowerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister -
Comment
-
Being a Split System means good efficiency. Not sure what the SEER is but assuming SEER = 16 draws 1.5 Kw. What that means is say at 24 volt battery requires a minimum 450 to 500 AH battery. That is just to handle the load the Ductless AC puts on the battery and has nothing to do with run time. FWIW a 24 volt 500 AH battery could only run it for 4 hours to discharge to 50% at which point you would need to recharge. Just to charge you are looking at 2000 watts of panels with a 80 amp CC.
It means a lo tof generator run time and fuel and $5K is just a down payment bare bones minimum just to turn it on and run a few hours each day. on battery.Last edited by Sunking; 06-18-2018, 08:29 PM.MSEE, PEComment
-
I was looking at this battery set up to run the AC/Heat for 6-8 hours a day. Would this be realistic and work?
Comment
-
To translate that means 40 amps @ 48 volts is 2000 watt solar, and 100 amp is 5000 watts. For a genny is a 7 Kva genny and a 48 volt 100 AMP charger.Last edited by Sunking; 06-18-2018, 08:36 PM.MSEE, PEComment
-
Comment
-
Is this what you would reccomend? Any options that should be adjusted up or could save money? How long could a system like this run the AC for continuously?
Renogy provides solar panels, charge controllers, inverters, lithium batteries, portable solar generators and other equipments for off grid solar power systems
link to mini split
Comment
-
Is this what you would reccomend? Any options that should be adjusted up or could save money? How long could a system like this run the AC for continuously?
Renogy provides solar panels, charge controllers, inverters, lithium batteries, portable solar generators and other equipments for off grid solar power systems
link to mini split
https://www.homedepot.com/p/MRCOOL-D...230A/207085061
For weekend use, I'd really suggest using a generator for a couple weekends, use a Kill-a-watt meter to see what your daily load is, and then you can engineer a system
The issue is :
1) plan too small, and you kill batteries and are unhappy
2) overbuild enough to "Be Sure" and you spend a lot of excess money.
Because AC is such a "heavy load" you have to size it just right. Rent a honda eu 3000 and a remote fuel tank, run it 24/7 and measure your loads. If you let the system shut down, the killl-a-watt looses it's memory and resets.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
As many have said here, it's not trivial to power an A/C unit like this from solar.
I considered the same for an RV and although I can do it, in reality the battery capacity is too costly for 24/7 operation.
I found the most reliable way was with a quiet Honda generator, gas and generators are cheap, portable and work on cloudy days..
Comment
-
gas and generators are cheap,
Clearly you're not in California.
2.2kw Suntech mono, Classic 200, NEW Trace SW4024Comment
-
As many have said here, it's not trivial to power an A/C unit like this from solar.
I considered the same for an RV and although I can do it, in reality the battery capacity is too costly for 24/7 operation.
I found the most reliable way was with a quiet Honda generator, gas and generators are cheap, portable and work on cloudy days..Comment
-
Sell that 24,000btu and buy a 12,000 , even the hot spot unit that works on DC 48v as it is the most efficientComment
-
12,000 BTU is too small, and 24,000 BTU is too large for 750/ft2. 18,000 BTU hits the sweat spot. Couple that with as high as an efficiency (SEER) as you can afford gets demand as low as possible. Example a 18K BTU with SEER = 16 demands 1120 watts. At SEER = 20 is 900 watts. In terms of energy makes a significant difference with 12 hours run time in a 24 hour period. At SEER 16 consumes 13.44 Kwh and at SEER 20 is 10.8 Kwh. In terms of battery cost would require a 40 Kwh battery at 16 SEER ($5000) and at 20 SEER requires a 32.4 Kwh $4000 battery. That hurts buying new batteries ever few years.MSEE, PEComment
-