  • morgandc
    Member
    • Feb 2015
    • 77

    Proposed system / Calculations

    I am in the final stages of moving to an off grid house in Sacramento, CA area and am starting my upgrade planning.

    Calculated winter daily loads are 15.5kwh
    Weekly loads that can be shifted 46kwh/wk and run with generator if needed
    Optional load for summers 12kwh (Hybrid car, gas and charge at work in the winter)

    Calculate for Winter 15.5kwh*2 days*1.5 losses= 46.5kWH
    Calculate for Winter 15.5kwh*3 days*1.5 losses= 70kWH

    46.5kwh/48v = 968AH needed for 2 days
    70kwh/48v = 1458AH needed for 3 days

    Trojan SIND 04 1685 has a 1293ah * 48v 20hr rate = 62,064 kWh
    Trojan SIND 02 2450 has a 1489ah * 48v 48hr rate = 71,472 kWh
    Trojan SIND 02 2450 has a 1594ah * 48v 72hr rate = 76,512 kWh

    2 days @ 20hr rate => 968ah/1293ah => 75% discharge => 25% charge
    2 days @ 48hr rate => 968ah/1489ah = 65% discharge => 35% charge
    Days of charge to 20% = 1594ah/484ah = 2.63 days

    Not ideal, but stays above 80% discharge in emergency, and a generator can be used to help as needed. To increase to 3 days or staying about 50% batteries requires doubling the inverters, panels, etc. to meet the min charge rates. This would translates to a 50% increase in an already expensive system, and 50% more in battery replacement costs forever.
    http://www.trojanbattery.com/pdf/dat...04_1685_DS.pdf

    So, assuming 1293ah batteries that puts me at a max discharge of c/8 = 161.6amps, and min. charge rate of 129 amps.
    Min. Generator size is 129amps*48v = 6.2kW @80% load = 7.7k round up to 8k generator
    min. solar array is 129amps * 48v = 6.2kWh
    Max draw is 161amps =>7.7kW

    Solar array is at 150 degree angle, due to shading and pvwatts says
    Month 6.9k DC array Output (kWh) per 30 days kWh
    Jan 488.0 16.3
    Feb 658.9 22.0
    Mar 871.4 29.0
    Apr 1017.0 33.9
    May 1085.9 36.2
    Jun 1054.5 35.1
    Jul 1117.8 37.3
    Aug 1146.7 38.2
    Sep 1077.5 35.9
    Oct 936.6 31.2
    Nov 603.9 20.1
    Dec 471.7 15.7

    Existing system
    Solar Array: 2.5kW panels
    Inverter/Charger: Magnum MS4448PAE
    Batteries: 48v 370ah and 7 years old.
    Generator: Champion DuelFuel 7k continuous

    Proposed System
    1x Schneider Electric Conext XW+ inverter rated at 6800watts
    2x Midnite Classic 150
    12x 4v Trojan 1685AH batteries
    1x top of pole mounts holding 15 60cell panels
    15x 295watt mono Solarworld panels (input needed)
    12x 205watt poly panels (existing panels)
    8k Diesel or LP liquid cooled low rpm generator
    1x residential fridge is in the daily load calc (The main fridge, not willing to compromise to propane)
    1x 48v Sunfrost RF18 is in the daily load calc (may not happen, but including in loads)

    Once I pin down the proposed system, I will then be trying to figure out the best order to do things. The generator brand doesn't instill confidence and the batteries are on their last legs. I don't dare get an expensive set of batteries without a large enough inverter/charger to maintain them. The existing Magnum invertor could charge them, but not avoid stratification.

    Proposed order of purchase / install
    1. Generator 8k
    2. Solar Panels -> upgrade existing system to 4.4kW with the new panels
    3. Forklift upgrade the Inverter and chargers / Upgrade to full 11.4kW
    ?? Batteries

    Batteries should be replaced soon, so possibly step 1.5 if I can survive 6-12 months with the existing charger and not kill them. Otherwise step 4 and I hope I can avoid buying a temp cheap set of batteries in the meantime. Possibly a lot of generator time, which is cheaper than a cheap set of batteries
    Last edited by morgandc; 01-08-2018, 11:55 PM.
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    15kwh daily ? That is some load. Any of that you can shed will be useful.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • morgandc
      Member
      • Feb 2015
      • 77

      #3
      It seems to add up fast with someone in the house all day... I am hoping that the numbers are estimated high, but they are gathered off the net, so we shall see. I can hopefully get some real numbers in a few weeks

      -Dwight
      Qty Watts Daily Hours Daily Total WH Weekly Hours Weekly Total Notes
      Car - Surplus KW / Generator / @work 1 12,195 Winter I will run on gas kicker engine or Generator
      Annette PC - Business style 2x monitors 1 400 9 3,600
      LP Heat (fans) 2 70 16 2,240
      Dwight PC, 2x monitors - Gaming style 1 700 3 2,100
      Refridge - LG Residential 1 1,959
      Refridge - Sunfrost RF19 1 1,019
      Air Filters 2 20 24 960
      LED Lights 2 20 17 680
      Cameras 2 12 25 600
      Security System 1 22.5 24 540
      TV 1 150 3 450
      Microwave 1 1200 0.3 360
      Keurig 1 1500 0.2 300
      Toaster 1 1200 0.2 240
      Clock Radio 1 7 24 168
      Vacuum 1 1000 0.1 100
      Blender 1 500 0.1 50
      Toothbrush 2 0.9 24 43
      ipads 1 2.5 12 30
      router 1 2.5 12 30
      electric razor 1 0.9 24 22
      phones 2 10.5 1 21
      apple tv 1 0.5 24 12
      smart watch 1 1 1 1
      Well Pump (150ft water level, 1.5HP) 1 2760 - 7 19,320 15gpm - Large Cistern with gravity feed - Gen or sunny days
      dryer 1 1800 - 7 12,600
      dishwasher 1 1500 - 2 3,000
      washer 1 800 - 7 5,600
      LP Oven 1 90 - 4 360
      Rice Maker 1 1000 - 1 1,000
      Pressure Cooker/Crock Pot 1 160 8 1,280
      Total with car 27,720 41,880
      Summer Daily with car 41,580 62,820 x1.5 for off grid inverter innefficiencies
      Winter Daily without car 17,887 x1.5 for off grid inverter innefficiencies
      Last edited by morgandc; 01-09-2018, 08:52 AM.

      Comment

      • bcroe
        Solar Fanatic
        • Jan 2012
        • 5198

        #4
        Originally posted by morgandc
        I am in the final stages of moving to an off grid house in Sacramento, CA area

        Trojan SIND 04 1685 has a 1293ah * 48v 20hr rate = 62,064 kWh
        Trojan SIND 02 2450 has a 1489ah * 48v 48hr rate = 71,472 kWh
        Trojan SIND 02 2450 has a 1594ah * 48v 72hr rate = 76,512 kWh
        1293ah * 48v = 62,064 WATT HOURS, NOT KWH. Better check everything again. Bruce Roe

        Comment

        • SunEagle
          Super Moderator
          • Oct 2012
          • 15123

          #5
          Originally posted by bcroe

          1293ah * 48v = 62,064 WATT HOURS, NOT KWH. Better check everything again. Bruce Roe
          Damn that 3 place decimal point for "k" always getting in the way of good numbers.

          Comment

          • morgandc
            Member
            • Feb 2015
            • 77

            #6
            LOL, good thing that is from the word document and not the spreadsheet!

            Comment

            • morgandc
              Member
              • Feb 2015
              • 77

              #7
              One the reasons the battery capacity is not larger, is due the max charge rate on the WX+6848 being 140amps. Following the min. 10% charge rate rule of thumb, 1400ah @20hr is the max battery bank it can charge properly without sunshine to help out. How firm is this recommendation? Could I bump up the batteries to the next size up? Say the 2v 1547ah Trojan industrials? This would put be below 10% without solar to help. The solar plan can add up to more than 100 amps if I were to run the gen during the day. On the other hand, the battery size is already pushing based on the 6.9kW panel size alone. But that could be upped a little bit easily.

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #8
                Have you figured how much solar and charge controllers it's going to take, to get your 10-13% charge rate for a larger pack ? And figured it for only the high performance part of the day, you don't get noontime sun all day long
                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister

                Comment

                • morgandc
                  Member
                  • Feb 2015
                  • 77

                  #9
                  The 2x midnight solar controllers can handle up to 96amps each so that would be 192amps enough for any non parallel Trojan industrial line configurations at 10%. I have no problem bumping up the solar array a bit more to match the 10%, just really don't want to add another invertor for the additional generator charge rate. The length of that charge time is what I was hoping someone would chime in with. If I went to 1547ah, I would be at 9% on the gen charge capacity plus whatever solar I have. How long does the charge rate have to be above 10% to mix the electrolyte properly? Is mid day enough...

                  Comment

                  • Mike90250
                    Moderator
                    • May 2009
                    • 16020

                    #10
                    Are you sizing batteries for loads, or for expected long days of clouds ? To stir the electrolyte with bubbles, you have to get the battery charging voltage above the gassing point. That happens in the latter half of the Absorb stage. If you have drained batteries down low, you may not have enough solar to get the batteries recharged to the gassing point, forcing you to run generator.
                    The electrolyte only needs weekly stirring, it takes it a while to separate out to different layers, but you still need to recharge to prevent sulfation,
                    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                    solar: http://tinyurl.com/LMR-Solar
                    gen: http://tinyurl.com/LMR-Lister

                    Comment

                    • morgandc
                      Member
                      • Feb 2015
                      • 77

                      #11
                      The sizing is based on a balance of a couple days of min. winter load combined with staying below the threshold for moving to a 2nd inverter, 3rd charger and more panels to keep up with a larger battery bank.

                      If bubbling is caused by voltage/bubbling, why the need for a min c/10 charge rate? Couldn't you in theory get to the same point with a longer charge period?

                      Comment

                      • Mike90250
                        Moderator
                        • May 2009
                        • 16020

                        #12
                        Originally posted by morgandc
                        ......If bubbling is caused by voltage/bubbling, why the need for a min c/10 charge rate? Couldn't you in theory get to the same point with a longer charge period?
                        Because you need enough power to get the batteries to that voltage. With solar, you only have so many hours to work with. And these are "Guidelines", you can play outside the lines, but understand things may not work as expected.

                        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                        solar: http://tinyurl.com/LMR-Solar
                        gen: http://tinyurl.com/LMR-Lister

                        Comment

                        • morgandc
                          Member
                          • Feb 2015
                          • 77

                          #13
                          Thanks, it helps to understand it is voltage/charge related and not a certain period time of amperage.

                          Comment

                          • morgandc
                            Member
                            • Feb 2015
                            • 77

                            #14
                            Well, I have been living on the existing system now for 6 months. No car charging, no crock pots, no kuerig, no dishwasher (yet), no well usage (use gen). But otherwise during summer I can live on10KWh in a day no problem. I really wish I had decent monitoring of usage off the charger/inverter for better numbers instead of just looking at the solar charger numbers. Winter was another story... the generator was being run every day for a couple of hours.

                            Moral of the story, real life usage doesn't match up with the theoretical numbers all that well.