Hi all, new here, but have been lurking for over a year!!!
I am new to the Solar Power System world but I have a remote Swamp Camp and I had some money saved so I thought I would buy a System because parts of the year no AC is needed. I got this system http://www.solarpenny.com/Magnum-Ene...assic-(4p).htm in the 4024 Version. I have 4, 6 volt Trojan L16 RE-B for my storage.
Now I have 2 Generators at my Camp. A Westerbeke 4.5 KW and an Onan DJE 6.0 KW. I like redundancy Both of these Gensets run fine and produce at 60 HZ, and 122-124 volts
I know Generators very well, and I am no novice when it comes to electrical connections.
Now the Crazy part. When I have the Westerbeke connected with out the AC Input Breakers on I read the voltage in the panel at AC In and it is 122-124 volts. I flip the breakers on the panel it bogs down the Genset, and the voltage rises up to 160 volts or so and the breaker trips.
Now when I have the Onan connected it does the exact opposite. A good 122-124 volts at the AC In, flip the breakers on the panel it does not bog down the Genset and it drops to 8-5-9.6 volts.
I set the AC input Amps in the Inverter Controller to 15. The Westerbeke puts out 19 each leg and the Onan 25 so I thought that would be a good start for that setting.
Not sure if anyone has ever saw this type thing, or have any ideas, but they are all appreciated
Thom
South of New Orleans
Thom