Trouble equalizing batteries
  • extrafu
    • Apr 2016
    • 185
    Hello,
    I've tried to equalize my batteries again and it looks like I failed once again. I have 8 rolls S-550 (428Ah) wired in series. This morning, I started the generator until current started to taper down. Them, I let solar do its job for a few hours (about 5 hours) until I reached float. When I reached float, I tried to start the equalization process.
    There was (and still is) plenty of sun right now and I'm starting the equalization process from the two Conext MPPT 80-600 CCs to equalize using the PV.
    When I switched to equalization, the batteries started to climb to 59.5, 60.5 and 61V for a few minutes (about 10-15 minutes) then voltage dropped rapidly to 56V, slowing going down. One of the two CC switched back from equalize to bulk and the other one kept on equalization. But voltage was still at 56V. Few minutes later, both were out of the equalization stage, back into absorb for a few minutes and then, back to float.
    Why is that? Help me understand as I have tried two times with them results.
    Thanks,
  • Bala
    • Dec 2010
    • 716
    I have two charge controllers, but different type and brand.
    When I equalise I need to disconnect the communication cables that connect them together, otherwise I have the same trouble as you are having.
    • citabria
      • Oct 2016
      • 90
      Are you running a Schneider Conext System Control Panel along with the 2 Conext CCs? It may be needed for coordinating absorb/float/EQ stages. A good sales representative can give you advice. I have a similar issue while running 2 different brands of charge controllers (an older Apollo T80 and a newer FlexMax80), since they sort of fight each other once Bulk stage is complete. I believe the my only fix is to replace the Apollo T80 with another FlexMax80 and connect those 2 CCs to a Hub Mate.
      • extrafu
        • Apr 2016
        • 185
        I indeed do use two Conext MPPT 600-80 CCs with the SCP. I'll try tomorrow to only switch ONE CC to equalize and leave the other at float.
          First you have to do a full charge. Then you must use a generator or commercial AC power to EQ batteries as it takes up to 24 hours. You cannot EQ or properly charge batteries with solar as you are just now learning.
          • extrafu
            • Apr 2016
            • 185
            Sunking Right now the batteries are about 1.25 SG which from Rolls' documentation, is nearby 100% SOC (http://support.rollsbattery.com/supp...ecific-gravity). I know I can EQ using my generator before my inverter can do it, but why I am observing this behaviour? There was plenty of sun and tons of PV available so lack of power has to be ruled out. It's either a Conext fart because I set both CCs to EQ like others said, or something else.
              Try starting the EQ after absorb is finished, and forget about FLOAT.
              Solar can do it, if both charge controllers are properly configured, but in your case, one or both are not configured correctly.
              • extrafu
                • Apr 2016
                • 185
                Mike90250 I pretty much did that, as I started EQ immediately when the CCs reported going into float. I'll try today to only switch one CC to EQ and leave the other one to float. I've also emailed Schneider, we'll see what they think about this. I'll report back what they say. Thanks!
                  Extrafu Absorb and EQ are not timed events. EQ can take up to 24 hours. This time a year you are doing good to get 3 hours per day on solar. Be aware of what time of year it is. We are in the shortest days of the year. Connect the dots. This time of year solar cannot fully charge batteries. Also make sure you are compensating for the electrolyte temperature.
                  • extrafu
                    • Apr 2016
                    • 185
                    So I tried again today and it worked using the two CCs. It looks like one has to be a bit patient when switching the Conext MPPT 600-80 to EQ as they need a few minutes in absorb before they kick in the EQ. Even with 2 CCs it worked. I ran EQ for about 45 mins before the PV wasn't generating enough power. I've tried then using the generator and the inverter and I got an error (W95 - EQ abort). I'll see what Schneider thinks about this one...
                    • Cult of Dionysus
                      • 53
                      Keen to hear how this goes for you. My dad just got some S550s (8 in one string), and I need to EQ them as well. But everything is through Outback (FlexPower Two, Hub10, Mate3 and a FM80). So should make the job a little easier.