    Originally posted by jflorey2
    At 1380ah you will want at least C/13, or 106 amps, charging current. That's about 1500 watts of panels. However I would avoid the smaller 100 watt panels and use the cheaper 200-300 watt panels. Your charge controller will be able to handle the higher voltages of the larger panels.
    I look at this slightly differently: all that extra capacity is for 5 days autonomy, he'd need to charge batteries once even if it would take few days and then he'd need PV to compensate for his 3.3kWh daily consumption + some inefficiencies.

    If his consumption stays flat through the winter as well he would need 3.3kWh / 0.9 efficiency / 2.5hr in winter = 1.5kw array. 1.5kW array at 12V would produce 125A charging current. Close enough to your estimate .

    OP, if you want to increase your battery size you can do it by connecting new ones in series- like if you connect 2 more banks like you have now in series you'd get 36V system which in turn would drop currents by factor of 3: 1.5kW / 36V = 42A so SK won't be laughing that much
    Last edited by max2k; 09-15-2017, 03:32 PM.

    Comment

    • max2k
      Junior Member
      • May 2015
      • 819

      #17
      Originally posted by Sunking
      Make sure your life, medical, health, and home owners insurance policies are paid up. You going to need them to bury the dead and rebuild your home from the pile of ashes.
      come on, you can make short runs of 400A conductors out of multiple big cable shielding pieces to remain flexible and have some multiple contact lugs on each to spread the current / reduce contact resistance- that's why I asked to look at the pics of the setup, he must have come up with some ingenious solution for that. Short of that and this whole thing is out of window. OP is also down to 2kW inverter now.
      Last edited by max2k; 09-15-2017, 03:34 PM.

      Comment

      • Sunking
        Solar Fanatic
        • Feb 2010
        • 23301

        #18
        Originally posted by max2k
        OP is also down to 2kW inverter now.
        Still 4 times to large for 12 volts. 2000 watts is 48 volt battery territory with a minimum 400 AH.Not to mention a waste of money when al that is required is 6 AWG wire.
        Last edited by Sunking; 09-15-2017, 03:42 PM.
        MSEE, PE

        Comment

        • Mike90250
          Moderator
          • May 2009
          • 16020

          #19
          Since Sunking didn't say it, I will:
          Ya gotta get yer head out of the 12V box. 125A charging current should be your 2nd tip-off something is wrong, That's 2, $600 charge controllers. And the fat chunks of copper wire with a $5 lug on each end for the interconnects...

          This is a 48V battery bank application. Same amount of lead, but you use voltage to your advantage, like the big boys do.
          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

          solar: http://tinyurl.com/LMR-Solar
          gen: http://tinyurl.com/LMR-Lister

          Comment

          • max2k
            Junior Member
            • May 2015
            • 819

            #20
            Originally posted by Sunking
            Still 4 times to large for 12 volts. 2000 watts is 48 volt battery territory with a minimum 400 AH.Not to mention a waste of money when al that is required is 6 AWG wire.
            who knows- he could lay them out as some super computer with batteries located vertically, charge controller on one side and inverter on the other with huge copper/silver buss bars going vertically as well. With required cross section those buss bars could actually serve as construction elements as they could probably provide necessary mechanical support. At 12V isolation would be trivial. I'm dying for pics now .

            Comment

            • jjrr007
              Junior Member
              • Sep 2017
              • 8

              #21
              I have contacted a solar tech guy.

              I told him about my situation. He recommended the following:

              1.Increasing my battery by 4 more batteries to 24 volts with 460ah

              2. total of 1,000 watt panels. My existing panels don't appear to be providing the proper amperage. so he suggested to test the amperage by connecting each one in parallel one at a time to see if the amperage goes up, what the problem is or if another brand of panels is needed.

              3. keeping the existing charge controller. The charge controller can handle 1,800 watts with a 24 volt battery

              4. Change my inverter to a 24 volt model.

              Is there any work around to doing number 4? Maybe a device I can put in the middle?

              Comment

              • jflorey2
                Solar Fanatic
                • Aug 2015
                • 2331

                #22
                Originally posted by jjrr007
                ]Is there any work around to doing number 4? Maybe a device I can put in the middle?
                Sure, you could get a boost converter. Five QSB40024S28 boost converters would do it and get you 12 to 24V at 2000 watts. They run around $260 ea for a total of $1300.

                Comment

                • jjrr007
                  Junior Member
                  • Sep 2017
                  • 8

                  #23
                  Do you guys/gals think that my plan in my previous post seems OK for a 100 kilowatt per month usage system (1 small window ac unit or sump cooler, flood lights that use 60 watts total, 1 camera system, couple of laptops)?

                  If I should post the plan on another thread, feel free to let me know.

                  Thanks again!

                  Comment

                  • bcroe
                    Solar Fanatic
                    • Jan 2012
                    • 5198

                    #24
                    Originally posted by jjrr007
                    100 kilowatt per month
                    Do you mean "100 kilowatt HOURS per month", because that made no sense? BRUCE ROE

                    Comment

                    • KMac
                      Member
                      • Apr 2016
                      • 66

                      #25
                      Yes, I think your solar pro seems about right, depending on the size of window air, and if it is a place you will live, versus a weekend cabin.

                      I have a 24v system, 1000w of panels 4x250w), 60 amp controller, 315 amp hour 6v Trojan batteries (20 hour rate), and a 2000 w inverter, and it runs my 5,000 BTU A/C by GE from Walmart, and keeps my 200 square foot well insulated cabin nice and cool. I am in the Midwest and get about 5 hours sun in summer, best case, and have panels tilted to summer angle. Will get about 750-850 watts from them max on a clear day, but over 4-5 hours it is sufficient. Lights (LED), computer, phone charger and the like are relatively insignificant. Water pumping and AC are the big draws. I keep the morning cool air and start AC early on "Eco" mode, so it seldom runs full speed (which is about 450 watts. I also run a 1/2 hp water pump on my well an hour or so throughout the day to water plants (220v grundfos that draws 850 w, and has little to no surge draw).

                      Ultimately, you need to learn your system capabilities in terms of production, and cost of loads you run. Then adjust accordingly., I don't live there so usually it's just a couple or three days in a row I am there, and only the water pump runs daily regardless. If you need to live there and have 3-5 days capability with no sun, then plan a bigger system.

                      Get into float almost every day with good weather.

                      Would not do it at 12v for a host of reasons.

                      Good luck.

                      ​​​​