I look at this slightly differently: all that extra capacity is for 5 days autonomy, he'd need to charge batteries once even if it would take few days and then he'd need PV to compensate for his 3.3kWh daily consumption + some inefficiencies.
If his consumption stays flat through the winter as well he would need 3.3kWh / 0.9 efficiency / 2.5hr in winter = 1.5kw array. 1.5kW array at 12V would produce 125A charging current. Close enough to your estimate .
OP, if you want to increase your battery size you can do it by connecting new ones in series- like if you connect 2 more banks like you have now in series you'd get 36V system which in turn would drop currents by factor of 3: 1.5kW / 36V = 42A so SK won't be laughing that much
If his consumption stays flat through the winter as well he would need 3.3kWh / 0.9 efficiency / 2.5hr in winter = 1.5kw array. 1.5kW array at 12V would produce 125A charging current. Close enough to your estimate .
OP, if you want to increase your battery size you can do it by connecting new ones in series- like if you connect 2 more banks like you have now in series you'd get 36V system which in turn would drop currents by factor of 3: 1.5kW / 36V = 42A so SK won't be laughing that much