Following specs come from the operation manual I found here (under documents tab): https://www.altestore.com/store/deep...ck-48v-p11941/
1) Each S-line stack can take 17A current. Do you consider that slow? The internal resistance will reduce the efficiency compared to lead acid, for example. But, as you mention, the capacity can be increased, and the higher internal resistance helps here as up to 12 stacks can be connected in parallel, which allows higher total current. For example, if you have a CC that can put out 80A, then 5 stacks in parallel can take max output (80/17=4.7). That of course requires a higher total battery capacity for the system, which won't be appropriate for all situations, but for systems that need higher energy capacity this may make sense.
2) This might have been true for the first generation of AHI, but the current generation has all of it's specifications made with respect to standard 48V inverters. The voltage range for AHI is 40-57.6 V, which meets most (all?) the inverter and CC specs I'm familiar with. And why isn't energy below 46V available? The recommended settings in the manual show that the battery LVCO can be set as low as 36V (outback FX and Radian inverter settings).
I don't know whether Aquion is going bankrupt or not. Do you have a source for that?
Having said all that, I agree that AHI is a new technology that doesn't have enough field data to verify the manufacturer claims. The battery might perform better than expected or it might be an expensive paper weight. And the warranty will of course be useless if Aquion goes bankrupt.
1) Each S-line stack can take 17A current. Do you consider that slow? The internal resistance will reduce the efficiency compared to lead acid, for example. But, as you mention, the capacity can be increased, and the higher internal resistance helps here as up to 12 stacks can be connected in parallel, which allows higher total current. For example, if you have a CC that can put out 80A, then 5 stacks in parallel can take max output (80/17=4.7). That of course requires a higher total battery capacity for the system, which won't be appropriate for all situations, but for systems that need higher energy capacity this may make sense.
2) This might have been true for the first generation of AHI, but the current generation has all of it's specifications made with respect to standard 48V inverters. The voltage range for AHI is 40-57.6 V, which meets most (all?) the inverter and CC specs I'm familiar with. And why isn't energy below 46V available? The recommended settings in the manual show that the battery LVCO can be set as low as 36V (outback FX and Radian inverter settings).
I don't know whether Aquion is going bankrupt or not. Do you have a source for that?
Having said all that, I agree that AHI is a new technology that doesn't have enough field data to verify the manufacturer claims. The battery might perform better than expected or it might be an expensive paper weight. And the warranty will of course be useless if Aquion goes bankrupt.