Just make sure the dip switch settings are within range of your battery specs. If not, the TS-MPPT can be set via a serial port or RS-232 for anything you want (within limits). That's what I did to charge my NiFe bank.
Having both TS-MPPT and Classic, I think the TS-MPPT has an edge in efficiency at less than full noon sun, and no fans. But the Classic has remote controlability.
(and the TS-MPPT does not come with the optional meter panel display. ~ $100)
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
10 Evergreen 205w on Powerfab top of pole PV mount | Midnight Classic 200 |
Iota charger
Collapse
X
-
Hold the buss, MPPT is far superior to PWM. At a minimum using a PWM controller you will loose 32% of your panel wattage turning your 100 watt panel into a 67 watt panel. A MPPT only looses 2 to 5%.
It takes a 300 watt PWM system to equal a 200 wat MPPT system. A 300 watt PWM system will cost you around $600 to $700. A 200 watt MPPT system will cost you around $400 to $500 for the exact same amount of power.Leave a comment:
-
This questions is for the professionals out there:
In your professional opinion, when running an AGM battery, I am throwing money away when buying a MPPT Solar Charge controller that does not allow me to specifically adjust my Float, Absorb, and Bulk voltages. What I mean is comparing a analog Morningstar to like a KID or Classic 150. It seems by the time I get all the gizmos, the morningstar and Midnight Classic runs about the same $$. For further clarification, I am not concerned about the cost, as I will pay more for "set it and forget it".
It takes a 300 watt PWM system to equal a 200 wat MPPT system. A 300 watt PWM system will cost you around $600 to $700. A 200 watt MPPT system will cost you around $400 to $500 for the exact same amount of power.Leave a comment:
-
This questions is for the professionals out there:
In your professional opinion, when running an AGM battery, I am throwing money away when buying a MPPT Solar Charge controller that does not allow me to specifically adjust my Float, Absorb, and Bulk voltages. What I mean is comparing a analog Morningstar to like a KID or Classic 150. It seems by the time I get all the gizmos, the morningstar and Midnight Classic runs about the same $$. For further clarification, I am not concerned about the cost, as I will pay more for "set it and forget it".Leave a comment:
-
For AGM batteries you don't really need any fancy charging algorithm, just a good single stage float charger with enough capacity for the battery to charge at at least C/10, can go as high as C/4. So with a solar system or daily cycle use, charge at maximum manufacture spec if you have temperature compensation, otherwise go to the middle ground like 14.4 on a range of 14.1 to 14.7. Now if you float use float voltage.
Hope that helps.Leave a comment:
-
My bad typo error of fat thumb. manual here. Go to page 14.Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
That leaves us cycle service, but what kind of charge source. Let's say the battery is used in a golf cart daily and recharged every night on a commercial charger. Trojan calls this Daily Charge charged from a hard source of the utility. If you look on page 14 that is between 13.8 to 14.4 volts. Charge is complete when current tapers to C/200 so on a AGM-31 that is .5 amps. This is the range for your Iota.
For RE applications things change. They raise the voltages because solar is a soft source. Range now becomes 14.1 to 14.7
So if I were you set your Iota on 14.4 volts on your new AGM and let it go until you see charge current falls just below 1 amp, then terminate charge, or lower voltage down to 13.5 Float Voltage. Then cycle the battery down to 50%, recharge, and repeat cycle a few times to form the plates as recommended by Trojan.
When on Solar set your controller for 14.7Leave a comment:
-
Its not, it is a CONSTANT VOLTAGE charger. They are just jacking the set point voltage to make it behave like a multi-stage charger.
Don't take that wrong, because there is nothing wrong with a Constant Voltage charger. In fact Float Chargers are the best to use, the just are not as fast, but very kind to the battery. Every utility out there with battery plants use Float Charger only.
What I would do if I were in your shoes is first look at the battery manufacture spec to see if they publish Absorb Voltage. Should say something like 2.35 to 2.45 volts per cell (2.4 is a good default) or say 14.1 to 14.7 volts (14.4 would be good in this example for a 12 volt battery.
OK assuming the battery is discharge if you were to set the Iota to 14.4 volts open circuit voltage, what you should observe is initially the battery will take full current of or near 30 amps, and if you look at the voltage will be less than 14.4 volts. Once the battery voltage reaches 14.4 volts, the current will taper off and continue to do so until the battery is saturated. WARNING, without intervention on your part can damage the battery if you let it go to long. An automatic system will terminate Absorb when the current tapers of to 3 to 5% of C where C = battery AH capacity. So if that is say a 300 AH battery you want to pull the plug when current tapers off to 9 to 15 amps, or lower the voltage to FLOAT VOLTAGE of around 13.2 to 13.6 depending on battery spec.
The battery I will be using is the Trojan 31AGM and my data sheet says Absorb should be 14.1-14.7 and float at 13.5. With the built in IQ4 my Dual Voltage jack (jumper) is disabled so my unit can not be adjusted manually. What it does say is: "Models with an internal IQ4 smart-charger (not sure how smart) give the user the benefit of automatic Bulk, Absorption, and Float stage charging. This increases the chargin capacity of the IOTA charger, decreases charge time and insures proper and safe battery charging without over-charging." It then just talks about what is happening when the LED blinks and where it is in the charge.
Would it be possible that the battery I was using, due to age and abuse, could not actually attain float status? I am going to assume that by the numbers, this is safe to hook up to my new battery - not in service?
In regards to this Trojan 31AGM, can I charge it at c/4 or should I be around C/8 when on PV Panels?Leave a comment:
-
Don't take that wrong, because there is nothing wrong with a Constant Voltage charger. In fact Float Chargers are the best to use, the just are not as fast, but very kind to the battery. Every utility out there with battery plants use Float Charger only.
What I would do if I were in your shoes is first look at the battery manufacture spec to see if they publish Absorb Voltage. Should say something like 2.35 to 2.45 volts per cell (2.4 is a good default) or say 14.1 to 14.7 volts (14.4 would be good in this example for a 12 volt battery.
OK assuming the battery is discharge if you were to set the Iota to 14.4 volts open circuit voltage, what you should observe is initially the battery will take full current of or near 30 amps, and if you look at the voltage will be less than 14.4 volts. Once the battery voltage reaches 14.4 volts, the current will taper off and continue to do so until the battery is saturated. WARNING, without intervention on your part can damage the battery if you let it go to long. An automatic system will terminate Absorb when the current tapers of to 3 to 5% of C where C = battery AH capacity. So if that is say a 300 AH battery you want to pull the plug when current tapers off to 9 to 15 amps, or lower the voltage to FLOAT VOLTAGE of around 13.2 to 13.6 depending on battery spec.Leave a comment:
-
OK something is wrong with this picture.
Bulk is a constant Current Mode, not Constant Voltage as you describe. There is no specified voltage during Bulk charge other than a Set Point to terminate the the Bulk stage at which point switches to Absorb. For example if Bulk is set to 14.1 volts on a 30 amp charger with a discharged battery what you would expect to see is the full 30 amps. Initially the voltage will be well below 14.1 volts, down in the 12 to 13 volt range with a steady 30 amps. As the battery charges, the voltage begins to rise but still 30 amps. Once the battery voltage reaches set point of say 14.1 volts, the charger switches to Absorb which is a Constant Voltage, current Taper.Leave a comment:
-
iotaiq4.jpg
--mapmakerLeave a comment:
-
Bulk is a constant Current Mode, not Constant Voltage as you describe. There is no specified voltage during Bulk charge other than a Set Point to terminate the the Bulk stage at which point switches to Absorb. For example if Bulk is set to 14.1 volts on a 30 amp charger with a discharged battery what you would expect to see is the full 30 amps. Initially the voltage will be well below 14.1 volts, down in the 12 to 13 volt range with a steady 30 amps. As the battery charges, the voltage begins to rise but still 30 amps. Once the battery voltage reaches set point of say 14.1 volts, the charger switches to Absorb which is a Constant Voltage, current Taper.Leave a comment:
-
Testing IOTA DLS-30
I did a little field-testing and research this weekend with the IOTA DLS-30 with IQ4 installed internally. This is a 12 v 30amp Power converter / battery charger (Taken from Iota’s instruction manual).
The battery I used was a car battery that was about 2 years old, who knows what condition it really is in, my guess it that it is on its last legs. I used this battery because it was a FLA and I did not want to start experimenting with my new Trojan -31 AGM battery.
I installed two Ammeter and voltmeters to measure input and draw and calibrated them with my multi meter. I hooked up a 45 watt 12v solar panel to the system with a cheap, and I mean cheap Solar Force PWM Charge controller that I had laying around. For running the IOTA I used my Honda EU2000I. For my draw, I ran my Dometic CF50 cooler that draws 3 amps at 12volt.
I charged the battery at home with a car style 12 amp charger and had it on the trickle charger for 2 days.
I ran the fridge all day Saturday hooked up to the solar panel as I had full sun. I moved the solar panel as the sun moved and was able to gain 3-3.5 amps from solar. The fridge ran all night with its on an offs (normal use). Sunday morning the battery was at 11.5 volts and the fridge was off due to the automatic battery protection.
I started the generator and warmed it up and switched it to Eco mode. I plugged in the IOTA and there was a quick draw but then the generator went back to a low RPM.
IOTA Charging at a constant 14.1 Volts
26 AMPs for 10 minutes - Bulk
15 AMPS for 15 minutes- Bulk
9 AMPS for 90 minutes - Bulk
6.1 AMPS for 1 hour before I turned off the generator – Absorption
I never hit float on the IOTA. When a load was turned off or on AMPS and Volts did not waiver.
If you have suggestions for better testing or question please post them up. I am no expert and would love to have feedback.Leave a comment: