Hello there all.
Before I start I shall give the details of my system.
4 x 240w Bosch panels
Outback FLEXmax60 MPPT Charge Controller
Outback VFX 3024 inverter
4 x Rolls s530 6v Batteries run is series at 24v
Panels receive full sun from 9am until 6pm in summer and 10am until 3.30 ish in winter
System was installed in mid July 2012
I have recently purchased a hydrometer to monitor specific gravity levels on my battery bank as after a long winter and a very wet spring the system had been somewhat under powered. The readings were around 1.22-1.23. I ran an eq cycle on the charge controller at 31.4v over a couple of sunny days and was able to get this up to 1.25-1.255 before I ran out of sun. The system seemed to be performing better until we had a small run of bad weather and the voltage ran low (23.0v). After this it seemed that the battery bank did not want to charge. A full day of sun with 850-940 watts consistent during peak hours and yet it would not rise above 26.2v.
I took a reading with the hydrometer and it was below the scale (the scale being 1.15-1.30) and not just by a bit but by a lot. The top of the glass tube was bobbing in the water. At this I panicked and ran out and bought gas for the generator ( a rather inefficient 6kva petroleum that pushes out 2000w charge and up to another 2000w for ac loads) and ran an eq cycle at 32.0 volts over the day until the readings were 1.26-1.265 across all cells. This is what rolls recommends.
The low battery cut off on the inverter is set at 24.0 volts and the full charge cycle has been completed several times since this (2 hour absorb at 29.4) and hydrometer reading were showing 1.23 in the morning with a voltage of 24.7 easily rising to 1.25 and above with the absorb cycle.
After another couple of cloudy days the system is down to about 24.0 volts last thing at night but has not gone so low as for the cut off to occur.
Yesterday I took a hydrometer reading while the the voltage was above 24 volts and the sun was not shining and my reading was 1.15-1.16 across all cells.
This has confused me as I thought the system was working better now and yet my SG reading indicate that my batteries are way below 50% SOC even though the voltage is above 24 volt. This SG has remained consistent throughout the day even though levels have gone up to 26volts despite the lack of sun. If it was not for the hydrometer I would not know that I have a problem.
What can I do? Should I run another eq and continue until all cells read 1.26-1.27 (I was only short by a hare's breath). Could I have a faulty cell or are my batteries shot after one winter?
I wish to expand the system in the near future doubling the bank and adding more panels to match. I am worried that if these batteries are now compromised I will not be able to see the full potential of any new batteries that I add.
Sorry to be so long winded but I wanted to answer the obvious questions before they are asked.
Thanks in advance.
V
Before I start I shall give the details of my system.
4 x 240w Bosch panels
Outback FLEXmax60 MPPT Charge Controller
Outback VFX 3024 inverter
4 x Rolls s530 6v Batteries run is series at 24v
Panels receive full sun from 9am until 6pm in summer and 10am until 3.30 ish in winter
System was installed in mid July 2012
I have recently purchased a hydrometer to monitor specific gravity levels on my battery bank as after a long winter and a very wet spring the system had been somewhat under powered. The readings were around 1.22-1.23. I ran an eq cycle on the charge controller at 31.4v over a couple of sunny days and was able to get this up to 1.25-1.255 before I ran out of sun. The system seemed to be performing better until we had a small run of bad weather and the voltage ran low (23.0v). After this it seemed that the battery bank did not want to charge. A full day of sun with 850-940 watts consistent during peak hours and yet it would not rise above 26.2v.
I took a reading with the hydrometer and it was below the scale (the scale being 1.15-1.30) and not just by a bit but by a lot. The top of the glass tube was bobbing in the water. At this I panicked and ran out and bought gas for the generator ( a rather inefficient 6kva petroleum that pushes out 2000w charge and up to another 2000w for ac loads) and ran an eq cycle at 32.0 volts over the day until the readings were 1.26-1.265 across all cells. This is what rolls recommends.
The low battery cut off on the inverter is set at 24.0 volts and the full charge cycle has been completed several times since this (2 hour absorb at 29.4) and hydrometer reading were showing 1.23 in the morning with a voltage of 24.7 easily rising to 1.25 and above with the absorb cycle.
After another couple of cloudy days the system is down to about 24.0 volts last thing at night but has not gone so low as for the cut off to occur.
Yesterday I took a hydrometer reading while the the voltage was above 24 volts and the sun was not shining and my reading was 1.15-1.16 across all cells.
This has confused me as I thought the system was working better now and yet my SG reading indicate that my batteries are way below 50% SOC even though the voltage is above 24 volt. This SG has remained consistent throughout the day even though levels have gone up to 26volts despite the lack of sun. If it was not for the hydrometer I would not know that I have a problem.
What can I do? Should I run another eq and continue until all cells read 1.26-1.27 (I was only short by a hare's breath). Could I have a faulty cell or are my batteries shot after one winter?
I wish to expand the system in the near future doubling the bank and adding more panels to match. I am worried that if these batteries are now compromised I will not be able to see the full potential of any new batteries that I add.
Sorry to be so long winded but I wanted to answer the obvious questions before they are asked.
Thanks in advance.
V