I'm trying to find information on any 12V battery charger(for flooded lead acid) that will work with modified sine output from a generator. Want to purchase one but every charger these days have some sort of printed circuitry that may not work with a generator. Anybody have any knowledge / experience with this. Would appreciate any advice on name brands or models that would work.
Announcement
Collapse
No announcement yet.
What 12V chargers that will work with a generator?
Collapse
X
-
Originally posted by mykidsbutler View PostI'm trying to find information on any 12V battery charger(for flooded lead acid) that will work with modified sine output from a generator.MSEE, PE -
Originally posted by Sunking View PostHuh? There is no such thing as a modified sine wave generator. All of them are pure sinewave.Comment
-
Well the throne thing you need to work that out on your own
Now running off a generator keep in mind that frequency is constantly changing with variations of load. This is worse on smaller generators than very large ones but frequency will change.NABCEP certified Technical Sales Professional
[URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]
[URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)
[URL="http://www.gaisma.com"]www.gaisma.com[/URL]Comment
-
A power generator is a combined unit of a engine and alternator.
A inverter produces AC power from DC & batteries.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Originally posted by Mike90250 View PostA power generator is a combined unit of a engine and alternator.
A inverter produces AC power from DC & batteries.Comment
-
Originally posted by mykidsbutler View PostI'm trying to find information on any 12V battery charger(for flooded lead acid) that will work with modified sine output from a generator. Want to purchase one but every charger these days have some sort of printed circuitry that may not work with a generator.....Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Originally posted by mykidsbutler View Post.... We are just wondering why smoke emanates from my appliances when run via generator and work fine using our pure sine inverter.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Originally posted by Mike90250 View Postthen the generator is bad or mis-wired. Pure Sine wave is what should be coming out of any genset. If it's smoking your gear, something is wrong with it.Comment
-
Sorry, I'm going to step aside on this thread, there is something I'm just not getting. Old eyes or brain fart going on.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
How about we start with make and model of the generator that is burning up the appliances.NABCEP certified Technical Sales Professional
[URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]
[URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)
[URL="http://www.gaisma.com"]www.gaisma.com[/URL]Comment
-
Originally posted by Sunking View PostHuh? There is no such thing as a modified sine wave generator. All of them are pure sinewave.
read: http://www.screenlightandgrip.com/ht...ators_ext.html
--mapmaker
Edit: The link appears to be broken now. Thanks to Mike90250 for finding the new link which he posted here:
https://www.solarpaneltalk.com/forum...-support/page3
(the 93rd post in that thread)
Last edited by mapmaker; 05-26-2016, 05:40 AM.ob 3524, FM60, ePanel, 4 L16, 4 x 235 watt panelsComment
-
Originally posted by mapmaker View PostIn one sense you are correct, but there are generators that are billed as modified sine wave output.
read: http://www.screenlightandgrip.com/ht...ators_ext.html
To summarize what I take from it for this application:
1. Modified Sine Wave generators: Mostly if not exclusively older inverter type generators. If the OP has one of those, it could cause problems with electronic loads.
2. And if he has a generator which has a limited current output and poorly designed regulation, the peak output voltage may be stabilized, but the waveform can change in a way that increases the RMS voltage. That could overload heating appliances like a toaster very badly.
If the OP uses a meter which just measures the peak AC voltage and multiplies by a constant to read RMS, he would not see that the generator output was actually going too high.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
Have you checked the voltage on the generator?
Forget the exact problem, but an old one I had was putting out too high a voltage I think - and that lead to things catching light etc.
It was then stolen after I'd left it out (normally quiet street) - hopefully they used it first and burnt some of their stuff out .Comment