    2 panels 1 controller

    Hi after some advice, i have a 125w panel on the jayco roof and a 300w portable foldable panel can i run these 2 panels through a single 40amp controller?
    125w specs:
    max power voltage 18.4v
    open circuit voltage 21.9v
    300w specs:
    max power voltage 18v
    open circuit voltage 21.24v
    thanks Daniel
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    It looks like it's OK, as long as you are under 40A, the panel voltages match really well for wiring in parallel
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • DanQ
      Junior Member
      • Mar 2018
      • 2

      #3
      My main issue is I've heard i possibly need to install blocking diodes in both panels, as in if 1 panel is in the shade and the other in full sun?

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        No blocking diodes ever needed with panels made after 1968.

        Delete the word diode from your solar vocabulary, until you are educated enough to be able to break the seal on a panel,and replace a Bypass Diode, and reseal the panel.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • bcroe
          Solar Fanatic
          • Jan 2012
          • 5198

          #5
          Originally posted by DanQ
          My main issue is I've heard i possibly need to install blocking diodes in both
          panels, as in if 1 panel is in the shade and the other in full sun?
          Even a shaded panel will generate up to full open circuit voltage (but little current), so no blocking diode
          is needed to prevent reverse current flow from the unshaded panel. Bruce Roe