    I have a friend (yes I have ONE FRIEND ) that is putting together a "small cottage" solar system.
    He seems to be doing all the right things, but he asked me what the difference is between a DC fuse and a AC fuse? He said his "instructions" (I think he's reading a book on PV systems) call for a DC fused disconnect between the solar panels and Charge controller and a DC fused disconnect between the Charge controller and the batteries. Now I agree that there needs to be disconnects between devices, but do they need to be fused?
    I answered "I don't have a clue, but it seems to me an Amp is a Amp, and it doesn't care which way the electrons are going"
    He's pretty insistent that that there is some difference?
    so I ask? Is there such a thing as a DC fuse? Why would it be different than a regular AC slow blow fuse?
    I don't get drunk~~~~I get awesome
    Feb 2011
    Annapolis Md
    6,631
    Yes there is a difference
    Because of the nature of DC current it will arc when a fuse blows. The amount of separation between the ends on a DC fuse are longer and many times there are other things within the fuse to prevent arcing.
    Use only fuses that are DC rated for the voltage intended. And yes the disconnects should be fused. The need and configuration of the fuses and disconnects depend on the system design. There should be a fuse on the battery to the inverter also.
    Rich
    WWW.solarsaves.net
    www.gaisma.com
    Aug 2010
    New York, ya it sux
    67
    No kidding? I did not know that, Thanx for the response.
    so I take it these fuses directional? or polarity sensitive?
    Is there a website I can go to, to see the construction of a DC fuse.
    should you fuse both legs from the device(s) or just the positive leg?
    Feb 2011
    Annapolis Md
    6,631
    fuses are not polarized they work in either direction.
    On a floating system both poles should be fused but that is a design question we don't have enough info on for your particular case.
    Rich
    WWW.solarsaves.net
    www.gaisma.com
    16,294
    Quote Originally Posted by Jmac00 View Post
    In general no they are not directional. DC can sustain an arc over significant distances at low voltages, and almost impossible to extinguish at high voltages. AC on the other hand crosses has zero sequence voltage 60 times a second, so it does not sustain an arc as easily at least until the air or gas is ionized.
    Dpends if the system is grounded or not and the system voltages. Low voltage non grounded system must have both polarities fused. grounded systems do not.
    Aug 2010
    New York, ya it sux
    67
    Is there a chart for sizing DC fuses. I know that a 10ga wire requires a 30amp fuse, 12ga needs a 20 amp and 14ga needs a 15 amp, and so on.
    16,294
    There is no chart for DC fuses as they are treated no different than AC.
    You are also stating things incorrectly. 30 amps is the largest over current device that can used on a #10 AWG wire under normal circumstances. You can use a 1-amp fuse on a 10 AWG wire, you just cannot use larger than 30.