panels, inverters and generators

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • farmerdoug
    Junior Member
    • Jan 2011
    • 15

    panels, inverters and generators

    My solar panels will be hooked to the grid using an inverter. When the grid goes down, I would like to use a generator as back up and to run the inverter as well. It seems to me I should be able to do it. Any suggestions how?
  • russ
    Solar Fanatic
    • Jul 2009
    • 10360

    #2
    Hi Farmerdoug - Welcome to Solar Panel Talk!

    I see no benefit in using the inverter when running the gen set?

    What are you trying to gain?

    Russ
    [SIGPIC][/SIGPIC]

    Comment

    • Sunking
      Solar Fanatic
      • Feb 2010
      • 23301

      #3
      Well you you can certainly use a generator as emergency power, but yu will not be able to use your GTI when commercial power is off as they are not designed to work with a generator or high impedance source.
      MSEE, PE

      Comment

      • farmerdoug
        Junior Member
        • Jan 2011
        • 15

        #4
        GTI?

        It's been a while since I took an electronics course isn't a transformer used to match impedances?

        Comment

        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #5
          Originally posted by farmerdoug
          GTI?

          It's been a while since I took an electronics course isn't a transformer used to match impedances?
          GTI = Grid Tied Inverter.. No power transformers are used to convert AC voltages either up or down within their impedance limits. You might be thinking of impedence matching transformer like they used in tube amplifier days to match the high impedance of the tube amplifiers to low impedance speakers.

          GTI's are current sources, not voltage sources like a generator or battery. They are made to operate into the extremely low impedance and frequency precision of the grid. An emergency generator like those used at a residence or commercial application are very low power (high impedance) and have horrible frequency regulation compared to the national grid. Well unless your home generator happens to be a few Terra Watts.(That means 1 Trillion Watts or more, enough to run a small country)
          MSEE, PE

          Comment

          • farmerdoug
            Junior Member
            • Jan 2011
            • 15

            #6
            So I need something more sophisticated. I need to take some power from the generator to run the inverter ( or one of new design); and when the generator is in use, I need somewhere to dump the extra power that would normally go back to the grid. In fact, since the generator is not meant to replace the grid, there may never be any extra pump. I could insure that by what I ask the generator to power in the house.

            Comment

            • Sunking
              Solar Fanatic
              • Feb 2010
              • 23301

              #7
              Originally posted by farmerdoug
              So I need something more sophisticated. I need to take some power from the generator to run the inverter ( or one of new design); and when the generator is in use, I need somewhere to dump the extra power that would normally go back to the grid.
              No when power is lost and you have an emergency generator, you have what is called a Transfer Switch that isolates you home from the grid and the GTI. Once the generator is running the GTI is completely shut down, turned off, isolated, and disconnected completely from your homes electrical system. In other words it is not doing squat.
              MSEE, PE

              Comment

              • farmerdoug
                Junior Member
                • Jan 2011
                • 15

                #8
                Ok. Forget the grid for a moment. I could build a circuit that allows me to use solar panels and a generator. Right?

                Comment

                • Sunking
                  Solar Fanatic
                  • Feb 2010
                  • 23301

                  #9
                  Originally posted by farmerdoug
                  Ok. Forget the grid for a moment. I could build a circuit that allows me to use solar panels and a generator. Right?
                  Not that I know of unless you have a degree in electrical and mechanical engineering.

                  With that said there are what is called Hybrid GTI's. They use batteries to take over when the grid fails for a short period of time until the generator starts up and takes over. But they have very limited power output, still require two transfer switches one to isolate you from the grid, and another to limit what has power in your home like cutting off your air conditioner, electric hot water heater, stove, oven, etc.. IMO they are not worth the expense, time or trouble.

                  Best option with a grid tied system if you want emergency power is a generator. It is th eleat expensive option and you do not have to suffer with power limitations if sized correctly.
                  MSEE, PE

                  Comment

                  • farmerdoug
                    Junior Member
                    • Jan 2011
                    • 15

                    #10
                    So let me rephrase that: One could hook up a generator and solar panels.
                    Regarding your other comment: What happens when the grid goes down for days or weeks?

                    Comment

                    • russ
                      Solar Fanatic
                      • Jul 2009
                      • 10360

                      #11
                      If the grid is down for a couple of weeks you run the generator a lot.

                      The preferred method here is to have a grid tie PV system with a generator for emergency power. It is by far the cheapest option available for most folks.
                      [SIGPIC][/SIGPIC]

                      Comment

                      • farmerdoug
                        Junior Member
                        • Jan 2011
                        • 15

                        #12
                        If I have a propane generator, the price of propane may stay reasonable for a while but if I use diesel then the price will get very high. If the grid goes down for a week or two, it would be silly to let the panels go used. No?

                        Comment

                        • Sunking
                          Solar Fanatic
                          • Feb 2010
                          • 23301

                          #13
                          Originally posted by farmerdoug
                          If I have a propane generator, the price of propane may stay reasonable for a while but if I use diesel then the price will get very high.
                          Depends on what country you live in, but in the USA diesel is the least expensive generator fuel because of its energy content and efficiency

                          Originally posted by farmerdoug
                          If the grid goes down for a week or two, it would be silly to let the panels go used. No?
                          I understand what you are trying to say and think, but it just does not work that way with grid tied inverters. Like i said you can buy a hybrid gti inverter with batteries, plus the generator if you are dead set if using solar panels for emergency standby power. However if you think the gen fuel is expensive wait until you pay for the batteries and replacing them every 5 years or so on top of the generator and fuel.
                          MSEE, PE

                          Comment

                          • farmerdoug
                            Junior Member
                            • Jan 2011
                            • 15

                            #14
                            That's why I am investigating the use of solar panels and generators.

                            Comment

                            • Sunking
                              Solar Fanatic
                              • Feb 2010
                              • 23301

                              #15
                              Originally posted by farmerdoug
                              That's why I am investigating the use of solar panels and generators.
                              Good luck as it has already been developed. You can have it as long as money is no object.
                              MSEE, PE

                              Comment

                              Working...