  • #31
    Originally posted by organic farmer View Post
    ... Unfortunately with my woodstove it was not possible for me to design it for thermal-syphoning. I must use a circulator-pump. ......
    You sir, have built yourself a bomb. You are just one power or pump failure away. Or some mineral deposit clogging. If you have a fire stoked up in your stove, and loose circulation, it goes boom in 2-30 minutes, depending. You just said in the nuke subs, they naturally circulate slowly, or else they would go boom too.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment


    • #32
      Originally posted by Mike90250 View Post
      You sir, have built yourself a bomb. You are just one power or pump failure away....
      No, not really. I have pressure-relief valves in the loops.
      4400w, Midnite Classic 150 charge-controller.

      Comment


      • #33
        Alright I think I've figured it out.... Normal hot water tank, thermo siphon supply into the top of the tank with the return from my floor Y'ed Into it. Return going back to the stove exiting from the drain at the bottom of the hw heater with the suppy to the floor T'ed off somewhere in this area along with the circ pump. If it was designed correct I think it would work well and the suction from the circ would encourage the flow of natural convection. Thoughts?

        Comment


        • #34
          Originally posted by Grahamsurette View Post
          Alright I think I've figured it out.... Normal hot water tank, thermo siphon supply into the top of the tank with the return from my floor Y'ed Into it. Return going back to the stove exiting from the drain at the bottom of the hw heater with the suppy to the floor T'ed off somewhere in this area along with the circ pump. If it was designed correct I think it would work well and the suction from the circ would encourage the flow of natural convection. Thoughts?
          Toss in a few check-valves to ensure the flow is always in the direction that you intend it to be.

          When you have multiple loops with Y-connections, there is a possibility of water flowing in the opposite direction, without any check-valves.

          4400w, Midnite Classic 150 charge-controller.

          Comment


          • #35
            Originally posted by organic farmer View Post
            Toss in a few check-valves to ensure the flow is always in the direction that you intend it to be.

            When you have multiple loops with Y-connections, there is a possibility of water flowing in the opposite direction, without any check-valves.

            I will do that. This is the second winter I've had my garage and I've been itching to see my infloor in action. Thanks for your input. If anyone has anything else to add I'm open for options

            Comment


            • #36
              Originally posted by organic farmer View Post
              No, not really. I have pressure-relief valves in the loops.
              Make sure that the relief valves are in a position where steam and hot water coming out will not cause risk to people or damage to the surroundings.
              SunnyBoy 3000 US, 18 BP Solar 175B panels.

              Comment


              • #37
                Originally posted by inetdog View Post
                Make sure that the relief valves are in a position where steam and hot water coming out will not cause risk to people or damage to the surroundings.
                Thanks for that. No one want hot steam in their face

                Comment


                • #38
                  Originally posted by inetdog View Post
                  Make sure that the relief valves are in a position where steam and hot water coming out will not cause risk to people or damage to the surroundings.
                  My system has been in operation for a few years. The pressure reliefs lift a few times every year. No problem so far.
                  4400w, Midnite Classic 150 charge-controller.

                  Comment


                  • #39
                    I'm thinking of venting the top of the hw heater that way it would be a little safer I think.

                    Comment


                    • #40
                      Originally posted by organic farmer View Post
                      My system has been in operation for a few years. The pressure reliefs lift a few times every year. No problem so far.
                      It only counts if they function perfectly year after year - maybe they will and maybe they won't.

                      If it is a low pressure system and you can use a vent pipe it would be great.
                      [SIGPIC][/SIGPIC]

                      Comment


                      • #41
                        The original link that mountain shared does not work for me. Is it still available?

                        Comment


                        • #42
                          Originally posted by gmanInPA View Post
                          The original link that mountain shared does not work for me. Is it still available?
                          That post made by mountain is over 5 years old so the link is probably long gone by now.

                          Comment


                          • #43
                            When I was a kid we made and placed a copper coil inside the fire box of our wood stove, it pumped water through the coil and into pex tubing in our concrete floor. Even in the teens weather we could burn for four hours in the evening and sleep warm all night. home was earthen berm, super insulated.
                            4X Suniva 250 watt, 8X t-105, OB Fx80, dc4812vrf

                            Comment


                            • #44
                              A copper coil in a wood stove is a time bomb, copper will work harden in the heat, and will fracture easily. Stainless Steel is the preferred material for a heat loop in a stove or heater.
                              http://www.woodheat.org/heating-wate...ood-stove.html
                              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                              || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                              || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                              solar: http://tinyurl.com/LMR-Solar
                              gen: http://tinyurl.com/LMR-Lister

                              Comment


                              • #45
                                i can't open link

                                Comment

                                Working...
                                X