Check my system

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Bearclaw
    Junior Member
    • Sep 2015
    • 9

    #16
    Check my system

    Originally posted by inetdog
    This is typical of any electronics with a well filtered power supply. Some of the older devices that used a lot more total power, including tube filaments, would use a series thermistor (with negative temperature coefficient of resistance) to limit the initial surge to a reasonable value. It also increased the life of the tube filaments, like soft starting an incandescent light bulb.
    Modern devices with far lower total power consumption apparently do not feel the need to mitigate the surge.
    When my psw inverter and the kill-a-watt are delivered I will send a complete list of watt usage, I've noticed changes in my cable box (which stopped working), and my stereo records speed was slowing down, so I stopped using the system until my new equipment arrives.

    Comment

    • PNjunction
      Solar Fanatic
      • Jul 2012
      • 2179

      #17
      Yep - that happens with msw inverters. Battery chargers if they don't fail outright may *seem* to work, but their algorithm timing is totally thrown off, and you end up killing the little tool battery you are attempting to charge.

      That being said, about the only thing I'm running from an MSW inverter without any seeming problems is modern LED bulb lighting (like GE, Sylvania, etc...)

      Comment

      • Bearclaw
        Junior Member
        • Sep 2015
        • 9

        #18
        Check my system

        Originally posted by PNjunction
        Yep - that happens with msw inverters. Battery chargers if they don't fail outright may *seem* to work, but their algorithm timing is totally thrown off, and you end up killing the little tool battery you are attempting to charge.

        That being said, about the only thing I'm running from an MSW inverter without any seeming problems is modern LED bulb lighting (like GE, Sylvania, etc...)
        I finally got figures.
        AMPS. WATTS
        T.V. .58. 67
        CABLE BOX. .67. 42
        CD. .04. 2.5
        ALL UNITS ON. 1.38. 150
        Then I lowered the lighting on the T.V. AS SUGGESTED.
        FINAL READINGS. 1.19. 142

        I WILL GET THE FIRE PLACE FIGURES WHEN IT GETS COOLER, I THANK YOU GUYS FOR ALL THE HELP...

        Comment

        • Bearclaw
          Junior Member
          • Sep 2015
          • 9

          #19
          Check my system

          Originally posted by Bearclaw
          I finally got figures.
          AMPS. WATTS
          T.V. .58. 67
          CABLE BOX. .67. 42
          CD. .04. 2.5
          ALL UNITS ON. 1.38. 150
          Then I lowered the lighting on the T.V. AS SUGGESTED.
          FINAL READINGS. 1.19. 142

          I WILL GET THE FIRE PLACE FIGURES WHEN IT GETS COOLER, I THANK YOU GUYS FOR ALL THE HELP...
          My fireplace start-up is .01amps and 8watts
          Blower.--high--.65 amps.--45watts
          Blower--med--.49 amps--30.3watts
          Blower--low---.44 amps--25.6watts
          The fire place will run alone.

          Comment

          • SunEagle
            Super Moderator
            • Oct 2012
            • 15125

            #20
            Originally posted by Bearclaw
            My fireplace start-up is .01amps and 8watts
            Blower.--high--.65 amps.--45watts
            Blower--med--.49 amps--30.3watts
            Blower--low---.44 amps--25.6watts
            The fire place will run alone.
            I am a little confused how you are calculating the wattage for that blower.

            W = Amps x Voltage. or W / Amp = Volt

            45w / .65amp = 69v
            30.3w / .49amp = 62v
            25.6w / .44amp = 58v

            So what is the voltage rating of that blower?

            Comment

            • Bearclaw
              Junior Member
              • Sep 2015
              • 9

              #21
              Check my system

              Originally posted by SunEagle
              I am a little confused how you are calculating the wattage for that blower.

              W = Amps x Voltage. or W / Amp = Volt

              45w / .65amp = 69v
              30.3w / .49amp = 62v
              25.6w / .44amp = 58v

              So what is the voltage rating of that blower?
              All amps and watt figures were taken with a kill-a-watt meter.

              Comment

              • SunEagle
                Super Moderator
                • Oct 2012
                • 15125

                #22
                Originally posted by Bearclaw
                All amps and watt figures were taken with a kill-a-watt meter.
                Ok. What is the voltage reading when you got the amp and watt measurement?

                Also are the "Watts" really watt hours over a period of time. Otherwise the W = V x A calculation doesn't work.

                Comment

                Working...