    How to add more PV? 200 Amp Mains panel with 4.6KW PV on circuit breaker

    I want to add 6.6KW of additional panels to a grid tie set up that already has 4.6KW connected through the Main panel (200amp) via a 40amp circuit breaker. One installer proposed connecting on the Load side or line side, which he explained would not be in the panel box or have a circuit breaker? Is this safe? What are the down sides? how do I learn more about this type of set up.
  • solar pete
    Administrator
    • May 2014
    • 1816

    #2
    Originally posted by Bill SEPA
    I want to add 6.6KW of additional panels to a grid tie set up that already has 4.6KW connected through the Main panel (200amp) via a 40amp circuit breaker. One installer proposed connecting on the Load side or line side, which he explained would not be in the panel box or have a circuit breaker? Is this safe? What are the down sides? how do I learn more about this type of set up.
    Hello Bill and welcome to Solar Panel Talk.

    What you are saying doesnt sound right, (but I am in Australia and rules and regs are different) at the very least I would ask your local POCO, as I think unless you got approval for the larger system at the start, I think there will be additional paperwork and processes to go through. Someone should pop in that knows a bit more at some stage. I think we will need more info from you like where are you and maybe more specs of the system. We have had some technical issues so it may be a bit longer than usual, cheers

    Comment

    • bcroe
      Solar Fanatic
      • Jan 2012
      • 5198

      #3
      Originally posted by Bill SEPA
      I want to add 6.6KW of additional panels to a grid tie set up that already has 4.6KW connected through the Main panel (200amp) via a 40amp circuit breaker. One installer proposed connecting on the Load side or line side, which he explained would not be in the panel box or have a circuit breaker? Is this safe? What are the down sides? how do I learn more about this type of set up.
      What inverters might you use for 6.6 + 4.6KW? String or micros? Does your PoCo contract
      cover the situation?

      There is a belt & suspenders rule that the inverter feed in breaker can't be more than 20%
      of the main breaker, so the total current can't overheat a section of busbars by ADDING
      TOGETHER with a heavy load applied. AND that the inverter feed in breaker must be at the
      opposite end of the bus bars from the main breaker, so that the 2 sources CAN'T ADD
      TOGETHER feeding heavy loads. Bruce Roe

      Comment

      • solarix
        Super Moderator
        • Apr 2015
        • 1415

        #4
        To do a standard load-side tap, the backfeed rule in the NEC says your solar backfeed cannot be more than 20% of the busbar size plus whatever difference there may be between the busbar size and the main breaker. For a 200A service (usually the size of the main breaker and the busbar), this means your backfeed breaker is a maximum of 40A and the inverter max output current is 40 x 80% = 32A (or 7.7kW). To go more than this you have four options:
        1) Upgrade the panel to 400A (which is really two 200A busbars - one of which you would dedicate to solar).
        2) Do a line-side tap before the main breaker. (which very few service panels are listed for and requires a separate permit to get the utility out to interrupt the service)
        3) Install a new meter socket product that backfeeds the solar power through it. (very new, and I'm not sure its available yet)
        4) Derate the panel by putting in a smaller main breaker. (many panels don't have main breakers in say a 175A size, you need to prove to your AHJ that it can handle your loads by doing a code approved load analysis and it requires a separate permit to shut your power down while it is installed). A 175A main gives you 25A more backfeed. 25A + 40A = 65A x 80% = 52A x 240Vac = 12.5kW of inverters.

        You need a competent installer to not muck this up.
        BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installed

        Comment

        • peakbagger
          Solar Fanatic
          • Jun 2010
          • 1561

          #5
          The local utility in my area got burned by solar installers making line sized taps inside the meter enclosure. They insist that the line size tap be installed in a completely separate enclosure downstream of the meter.

          A competent electrician apparently should know better but shortcuts get taken.

          Comment

          • Naptown
            Solar Fanatic
            • Feb 2011
            • 6880

            #6
            A line side tsp is very common.
            Also as others have said defeating the main breaker also works.
            NABCEP certified Technical Sales Professional

            [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

            [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

            [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

            Comment

            • skipro3
              Solar Fanatic
              • Jul 2015
              • 172

              #7
              Just derate the panel from 200 watt to 150 watt by replacing the main breaker with a 150 amp breaker. It will pass code inspection and most important, it is safe.

              Comment

              • foo1bar
                Solar Fanatic
                • Aug 2014
                • 1833

                #8
                Originally posted by Naptown
                Also as others have said defeating the main breaker also works.
                derating the main breaker is what Naptown meant.
                I'm sure it was a typo/autocorrect.

                (Hopefully no one read that and thought it really should be "defeating" - because defeating a main breaker is obviously just a bad idea.)

                Comment

                • bcroe
                  Solar Fanatic
                  • Jan 2012
                  • 5198

                  #9
                  Originally posted by foo1bar
                  derating the main breaker is what Naptown meant.
                  I'm sure it was a typo/autocorrect.

                  (Hopefully no one read that and thought it really should be "defeating" - because defeating a main breaker is obviously just a bad idea.)
                  I would certainly like to know how to DEFEAT this thing that keeps changing what I type
                  without my permission. Bruce Roe

                  Comment

                  • Bill SEPA
                    Junior Member
                    • Jul 2015
                    • 12

                    #10
                    WOW. Thanks for the information everybody.

                    To answer the question about the inverters. The 4.6KW system uses an SMA Sunny Boy 5000 and has been working great for 5 years so far. The proposed 6.6 system will use an SMA Sunny Boy 7000.

                    The more I read here the more I learn. I just don't want to burn down the house by overloading what I already have. I will talk to the installer again to be sure there is an understanding about that.

                    SO, the question becomes......Would you upgrade to a 400 amp panel or do a line side connection? I will start a new thread with that question to comply with standard forum protocal.

                    Thanks again everybody.

                    Comment

                    • Naptown
                      Solar Fanatic
                      • Feb 2011
                      • 6880

                      #11
                      Originally posted by Naptown
                      A line side tsp is very common.
                      Also as others have said defeating the main breaker also works.
                      Yes I meant de rate
                      Dam autocorrect