    Want help in making 48v system

    Hello,

    Please help me in making 48v off grid system.

    I have...

    Solar panels 12v-150w * 12pcs

    Controller PWM 48v-60A * 2pcs

    Inverter 48v-5000w * 1pc

    Battery 12v-200Ah * 6pcs

    Please tell me how to make connection.

    Thank you
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    386536_224900547583406_120212794718849_544630_1918166571_n.jpg

    Here is a sample to get you started.

    Without knowing the specs on your PV panels, I can't advise any further, except that with that large of a system, you
    would benefit and save money on copper wire, by using a MPPT controller.

    Also, 6, 12V batteries - you can only use 4 batteries in a 48V system. Sell the 2 batteries and the PWM controller and get a good, name brand MPPT controller
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • djhassoonew
      Junior Member
      • Apr 2015
      • 29

      #3
      Originally posted by Mike90250
      [ATTACH=CONFIG]6755[/ATTACH]

      Here is a sample to get you started.

      Without knowing the specs on your PV panels, I can't advise any further, except that with that large of a system, you
      would benefit and save money on copper wire, by using a MPPT controller.

      Also, 6, 12V batteries - you can only use 4 batteries in a 48V system. Sell the 2 batteries and the PWM controller and get a good, name brand MPPT controller
      Panel specification is:

      Pm:150w
      Vmp:17.56v
      Imp:8.54A
      Voc:21.96v
      ISC:10.25A

      There is no way that 6 batteries can b connected to 48v system?

      Comment

      • Sunking
        Solar Fanatic
        • Feb 2010
        • 23301

        #4
        Originally posted by djhassoonew
        There is no way that 6 batteries can b connected to 48v system?
        Sure if they were 8 volt batteries wired in series. But you have 12 volt batteries which means groups of 4 wired in series. Loose two batteries and the PWM controller. Replace the controller with a 40 amp MPPT controller.

        FWIW 1800 watts on 200 amp hour batteries is going to cook the batteries. Make sure you have plenty of distilled water on hand.
        MSEE, PE

        Comment

        • djhassoonew
          Junior Member
          • Apr 2015
          • 29

          #5
          How about 12v solarpanels 12pcs into 48v?

          Is it ok if I use 1 pc of 48v-60A controller? If PWM is only option

          Comment

          • SunEagle
            Super Moderator
            • Oct 2012
            • 15123

            #6
            Originally posted by djhassoonew
            How about 12v solarpanels 12pcs into 48v?

            Is it ok if I use 1 pc of 48v-60A controller? If PWM is only option
            You are missing the point.

            First off you can't build a 48volt battery system using 6 x 12volt batteries. You can build a 24volt system with 3 sets of 2 batteries. Which gets you a 24volt 600Ah system.

            Next the charging amps for your battery system needs to fall between C/8 and C/12 where C = total Ah of system. So for that 600Ah system you need between 50 and 75amps of charging or say 60amps.

            You might be able to connect 12 150watt panels to that PWM charge controller but without knowing what it is I am only guessing. Based on what the max VDC input rating of that CC will determine how many of those panels you can wire in and if that will add up to around 60 amps.