One source says a 1.25 factor in sizing charge controllers is to account for "peak irradiance conditions", and it is required by the NEC.
How do I properly use this factor, if this is true?
The Xantrex 80 600 (rated for 80A output) says connect to arrays of "up to" 4800W. 4800/48 = 100A, and if I multiply that by (1/1.25) or 0.8, I get 80A. Does this reflect the 1.25 factor mentioned, or is it just a coincidence? When they say "arrays up to 4800W" are they in essence saying the peak power coming in can be 4800W, but the nameplate PV would be lower? In other words, the maximum nameplate PV power would be .8 * 4800, or 3840W?
More to the point and put another way, let's say I plan for a 4400W array. Do I divide by the battery bank nominal and multiply by 1.25 to determine the charge controller output capacity required? This would make sense if the purpose is to allow for peak input power.
Edit I saw another example, using the 1.25 factor on the short circuit current of the solar panel array at the input to the controller, and making sure the result doesn't exceed the input current limit of the charge controller (which is 35A for this unit). This makes the same or more sense as checking the output side. Should the factor also be used against the output current, as described above?
It seems like the controller would limit its output, which brings up a whole different important question about these systems - if the array is loaded to operate at its peak output, what happens to the excess power that can't be delivered to the battery? Is not the battery current or voltage carefully controlled per desired profiles for absorb, float, etc? Can the array be putting out maximum power, and the power to the batteries be far lower if they are in float for example? What happens to the excess power (assuming there is no diversion of excess power, and no load on the inverter)? Would the controller move off the curve to a point where only the power required is being delivered by the array?
Thanks!
ps I posted a question a few days ago about a proposed system. I've discovered I skipped over or misunderstood several design details - this is just one. So I'm going back to learn how to walk, before running. Thanks for your patience.
Thanks!