    Combiner Box Question

    Hi all, I am about to install solar for my shop at my house. Here are the specs on what I'm installing:

    6 each Topoit 245 watt Mono panels
    Watts (STC) 245W
    Watts (PTC), No
    Maximum Power (Vmp) 49.51V
    Maximum Current (Imp) 4.95A
    Open Circuit Voltage (Voc) 59.45V
    Short Circuit Current (Isc) 5.54A
    Power Tolerance ±5%
    Module Efficientcy No

    My equipment is:
    Outback GVFX3648 Inverter/Charger, 3600W, 48VDC, 120VAC, 45A charger
    Outback FLEXmax FM80 Charger Controller
    Outback MATE3 Control Module and Display
    Outback HUB-10 Communications Manager
    Outback RTS Remote Temperature Sensor
    Prewired AC and DC boxes with 120VAC Bypass and Type B Outlet
    FLEXnet DC
    surge protector for 120V 60Hz applications
    80 amp charge controller breaker
    175ADC breaker
    GFDI
    1 x PSX-240 Auto transformer

    Now my question is, how can I tie them all together in parallel? How many string before I need a combiner box? Can I use branch connectors and bring one run down to a fused DC disconnect? My intentions are to add more panels at a later date and time. Thanks in advance for any help.
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    Your panels are 45V, batteries 48V, so there must some panels in series.

    I would wire 2 panels in series, then parallel the three series strings with 3 combiners. Do the panels have a series fuse spec on the label ? Otherwise I'd use 10A fuses or DC breakers.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Krazy1
      Member
      • Nov 2014
      • 32

      #3
      Originally posted by Mike90250
      Your panels are 45V, batteries 48V, so there must some panels in series.

      I would wire 2 panels in series, then parallel the three series strings with 3 combiners. Do the panels have a series fuse spec on the label ? Otherwise I'd use 10A fuses or DC breakers.
      Thanks for the input Mike. I was not quite sure if my panels would charge my 48volt bank without configuring one in series. Is there a rule of thumb for us beginners when sizing the panels for charging 12, 24, and 48 banks? I was aware that I would need to output much more than the 48v.

      Comment

      • Krazy1
        Member
        • Nov 2014
        • 32

        #4
        Here is the complete spec on the panels:

        Electrical Characteristics
        Watts (STC) 245W
        Watts (PTC), No
        Maximum Power (Vmp) 49.51V
        Maximum Current (Imp) 4.95A
        Open Circuit Voltage (Voc) 59.45V
        Short Circuit Current (Isc) 5.54A
        Power Tolerance ±5%
        Module Efficiency No
        Mechanical Characteristics
        Cell Technology Monocrystalline
        Cell Size Others
        Cells Per Module 96
        Dimension 1575*1082*50mm
        Weight 21.5000
        Frame Material Anodized Aluminum
        Module Color Silver Frame
        Moduel Connector MC4 or Compatible
        Junction Box IP65
        Output Cable No
        Operating Conditions
        Maximum System Voltage 1000VDC
        Operating Temperature -40℃--85℃
        Maximum Series Fuse 10A
        Max Snow Load 5400Pa ( 112 lb/ft2)

        Comment

        • Mike90250
          Moderator
          • May 2009
          • 16020

          #5
          Originally posted by Krazy1
          Here is the complete spec on the panels:...
          Maximum Series Fuse 10A......
          10A fuse or circuit breaker. in each of the parallel strings
          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

          solar: http://tinyurl.com/LMR-Solar
          gen: http://tinyurl.com/LMR-Lister

          Comment

          • Amy@altE
            Solar Fanatic
            • Nov 2014
            • 1023

            #6
            You have 96 cell modules, which are "nominal 32V". A 12V panel is 36 cells. Each cell (the individual block of silicon) is about .33V nominal. So .33V x 96 cells = 32V nominal. You have a nominal 48V battery bank. Nominal voltage is a term used to be able to see at a glance what equipment works together, a nominal 12V solar panel works with a nominal 12V battery bank, even though neither are actually 12V. So since you have a nominal 32V panel, you need to wire 2 in series to get a higher nominal voltage than your battery bank, that charge controller can adjust down, but not up. You can only do 2 in series, because the charge controller can only handle up to 150Voc, including temperature deration (voltage goes up when it's cold). 59.45 x 2 in series x 1.2 for cold (guessing where you are) = 142V.

            Then get a Midnite MNPV6 (for room for expanding) combiner box with 3 10A fuses and 4 2-hole strain reliefs for the wire to enter (including one for grounding wire). That will combine the panels into 3 parallel strings of 2.

            Amy
            Solar Queen
            altE Store

            Comment

            • Krazy1
              Member
              • Nov 2014
              • 32

              #7
              Wow, I'm so glad I posted on here. Thanks for all this good information. This forum is fa nominal!!

              Comment

              • Krazy1
                Member
                • Nov 2014
                • 32

                #8
                Originally posted by Amy@altE
                You have 96 cell modules, which are "nominal 32V". A 12V panel is 36 cells. Each cell (the individual block of silicon) is about .33V nominal. So .33V x 96 cells = 32V nominal. You have a nominal 48V battery bank. Nominal voltage is a term used to be able to see at a glance what equipment works together, a nominal 12V solar panel works with a nominal 12V battery bank, even though neither are actually 12V. So since you have a nominal 32V panel, you need to wire 2 in series to get a higher nominal voltage than your battery bank, that charge controller can adjust down, but not up. You can only do 2 in series, because the charge controller can only handle up to 150Voc, including temperature deration (voltage goes up when it's cold). 59.45 x 2 in series x 1.2 for cold (guessing where you are) = 142V.

                Then get a Midnite MNPV6 (for room for expanding) combiner box with 3 10A fuses and 4 2-hole strain reliefs for the wire to enter (including one for grounding wire). That will combine the panels into 3 parallel strings of 2.

                Amy
                FYI, I'm in northwest Florida. Lots of sun, not much wind unless a hurricane is coming!

                Comment

                • SunEagle
                  Super Moderator
                  • Oct 2012
                  • 15125

                  #9
                  Originally posted by Krazy1
                  FYI, I'm in northwest Florida. Lots of sun, not much wind unless a hurricane is coming!
                  Out of curiosity what is the voltage and AH rating of the batteries are you using for 48volt system?

                  Comment

                  • Amy@altE
                    Solar Fanatic
                    • Nov 2014
                    • 1023

                    #10
                    slight correction

                    I said 10A fuses, I meant 10A breakers.

                    Even in FL, you can't do 3 in series. 59.45Voc x 3 = 178V = boom
                    Solar Queen
                    altE Store

                    Comment

                    • Krazy1
                      Member
                      • Nov 2014
                      • 32

                      #11
                      Originally posted by SunEagle
                      Out of curiosity what is the voltage and AH rating of the batteries are you using for 48volt system?
                      This is what I plan to use:

                      6 each,12 Volt 200 Ah Group 4D Deep Cycle Sealed AGM SCADA Systems Solar Backup Battery.But I'm open to any suggestions!

                      Comment

                      • Krazy1
                        Member
                        • Nov 2014
                        • 32

                        #12
                        Originally posted by Amy@altE
                        I said 10A fuses, I meant 10A breakers.

                        Even in FL, you can't do 3 in series. 59.45Voc x 3 = 178V = boom
                        Yes, I ordered my combiner box today with 10A breakers, not fuses. My plans were to test the system with all 6 panels in parallel first. Then if I need to, I had intentions of placing only 2 of the panels in series! Once my system and components arrive, I have an electrical engineer helping me wire it up. I'm still up in the air whether or not to place combiner on the roof or add the extra wires to put it inside near all the controls.

                        Comment

                        • SunEagle
                          Super Moderator
                          • Oct 2012
                          • 15125

                          #13
                          Originally posted by Krazy1
                          This is what I plan to use:

                          6 each,12 Volt 200 Ah Group 4D Deep Cycle Sealed AGM SCADA Systems Solar Backup Battery.But I'm open to any suggestions!
                          I am not sure how you can configure 6 x 12volt batteries into a 48volt system.

                          First off unless you are worried about fumes or spillage a Flooded Lead Acid (FLA) deep cycle battery is better then AGM type batteries.

                          Second you should build the system with batteries wired in series and not in parallel.

                          What is your daily watt hour need? If for example it is around 4000 watt hours then I would say 8 x 6 volt 420Ah Trojan L16P would give you a 48V system good for about 4kWh using about 20% of the battery capacity.

                          If your daily load is more than 4kWh then even in Florida your 1470 watt panel system may not be enough to put back what you used during the Winter.

                          A solar battery system requires all of the components to be balanced.

                          If you haven't read them yet go to the Off Grid Section of this forum and read the Sticky posts on sizing an off grid battery system. Below is the link to that post. There are others in the same area that will help you understand what you need and what to get.

                          Discuss remote solar applications for homes, cabins, RV and boats. If you have a question on equipment for an off grid system, such as charge controllers or inverters, then post your question in this forum.

                          Comment

                          • russ
                            Solar Fanatic
                            • Jul 2009
                            • 10360

                            #14
                            Originally posted by SunEagle
                            I am not sure how you can configure 6 x 12volt batteries into a 48volt system.
                            It is that new math I guess - you can get most any answer you want and it is OK - you still get a ribbon.
                            [SIGPIC][/SIGPIC]

                            Comment

                            • SunEagle
                              Super Moderator
                              • Oct 2012
                              • 15125

                              #15
                              Originally posted by russ
                              It is that new math I guess - you can get most any answer you want and it is OK - you still get a ribbon.
                              Either that or he typed in the wrong quantity.

                              I think he meant to say 8 x 12volt 200Ah batteries. Which would require some parallel wiring. So I suggested 8 x 6v 420Ah batteries wired in series. Cleaner installation as far as I'm concerned.

                              He needs to have a good battery system to meet his needs, especially since he purchased that Outback Hybrid inverter/charging system for around $4000.