X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • wire size to inverter

    I have a 85W panel with MC-4 connectors.

    What size wire do I need to connect it to the solar converter I have.

    It's a 300W solar inverter.

    tia

  • #2
    depends on how long the wires are.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment


    • #3
      10' tops.

      Comment


      • #4
        Originally posted by ant58 View Post
        10' tops.
        Let's make sure of the details. What is the panel voltage? How many panels - just one? If more than one - are they arranged in a string, or all paralleled?

        Finally, what is the Isc Short Circuit Current rating of your panel? That sets the wire size.
        Lawrence Lile, PE

        Comment


        • #5
          Originally posted by lile001 View Post
          Let's make sure of the details. What is the panel voltage? How many panels - just one? If more than one - are they arranged in a string, or all paralleled?

          Finally, what is the Isc Short Circuit Current rating of your panel? That sets the wire size.
          Using 12 now.

          1 panel, 12V

          Comment


          • #6
            Originally posted by ant58 View Post
            Using 12 now.

            1 panel, 12V
            Well the Isc will be a little more than this, but it'll be close enough. 85 watts / 12 volts = 7 amps. The smallest NEC wire size commonly used is #12 which is good for 20 amps. So a # 12 will handle your panel nicely. #10 is the next size up, and will also work. The wire should be RHW-2/RHH (type USE-2) sunlight resistant wire. If you have an MC4 connector on the panel, just get a set of cables already made up with MC4 connectors from any good solar supplier. If your inverter has terminal inputs, get a cable twice as long as you need, with male and female connectors on either end, and cut it in half.
            Lawrence Lile, PE

            Comment

            Working...