Circuit to shut off inverter at low battery voltage set point = 50%

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • DSII
    Junior Member
    • Mar 2010
    • 7

    Circuit to shut off inverter at low battery voltage set point = 50%

    Charge controlers have an adjustable high voltage set point, so the batteries are not over charged. If you place a relay circuit that disconnects the batteries from the inverter so the voltage does not fall below the 12.06 50% level it would reduce damage to the batteries. The problem is that the circuit will need to not enguage the inverter until the voltage is some what higher like 12.30 volts. If needed the relay could open the 115 volt side and the inverter would only draw a small amount of current, until you checked the battery voltage level.

    Thanks for any help in this matter.
    Dale La Roy Smith II
    Cocoa, Florida
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    Some inverters have a "Low Battery Disconnect" in them, but they are set too low usually.
    I think you could use a 12V relay, and a trim pot in series with it, to control the 115V output, adjust the trimpot so the relay just drops out at your desired voltage, and have a "override" push button switch to short out the trimpot, to reset the relay.
    Has to be home brew, i've see nothing in stores.
    Last edited by Mike90250; 03-30-2010, 03:38 PM.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • DSII
      Junior Member
      • Mar 2010
      • 7

      #3
      Relay will bounce unless close voltage is set higher.

      Here is what happens:
      1. Voltage goes down to low set point = 12.06 ~ 50%
      2. Relay opens, no load on batteries, now voltage goes above 12.06
      3. Relay closes, which places load on batteries, now voltage goes below 12.06
      4. Go back to step 2. repeat process ( relay now is in circular cycle )

      Do you think the OUT BACK inverts have Low Battery Disconnect that is adjustable?

      Thanks for your help.

      Comment

      • Sunking
        Solar Fanatic
        • Feb 2010
        • 23301

        #4
        Here is the problem, State Of Charge Voltages is meaningless when the battery has a load on it or being charged. The only time SOC has any meaning is when the battery is disconnected from any load or charge currents and rested for several hours.

        The only true measure of the state of charge is by using a temperature corrected hydrometer reading, then record the loaded voltages down as each data point is reached.

        Secondly you are getting the bounce effect because you need 2 set points:

        1. LVD or low voltage disconnect, say 11.9 volts
        2. LVR or low voltage reconnect which has to be higher than LVD, like 12.3

        If the two are equal or too close, you will just sit there and bounce.
        MSEE, PE

        Comment

        • DSII
          Junior Member
          • Mar 2010
          • 7

          #5
          Theory great actual circuit ?

          Dear SunKing,

          In theroy I understand but not sure how to connect circuit. Could you steer me in a direction to make a circuit that would do this?

          Thanks.

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #6
            My suggestion - use a manual reset, or a 4PDT 120VAC relay, and route the relay coil wire thru the NO cntact. Then you HAVE to manually reset it, the battery recovering won't trip it back on
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • opanin17
              Junior Member
              • Jun 2016
              • 4

              #7
              Low battery protection is good for all solar inverters as well as every battery powered device. But using just a relay and a trimpot wouldnt solve the problem fully because when the battery voltage is close to the switching point, the relay will be bouncing. In some cases, the bounce can be stopped by connecting 100uf capacitor accross the coil pins of the relay.
              In other cases as the one we have here, bouncing can be stopped by using a comparator with hysterises as in this link circuit







              The hysterises function sets two operating points for the relay turn on and turn off. In that case bouncing is overcomed and the circuit is made automatic.
              Last edited by opanin17; 09-11-2016, 02:16 PM.

              Comment


              • Mike90250
                Mike90250 commented
                Editing a comment
                This is an ALERT function, and requires a human to intervene and protect the batteries (start the generator or shut off the inverter)
            • Sunking
              Solar Fanatic
              • Feb 2010
              • 23301

              #8
              Originally posted by opanin17
              Low battery protection is good for all solar inverters as well as every battery powered device. But using just a relay and a trimpot wouldnt solve the problem fully because when the battery voltage is close to the switching point, the relay will be bouncing. In some cases, the bounce can be stopped by connecting 100uf capacitor accross the coil pins of the relay.
              In other cases as the one we have here, bouncing can be stopped by using a comparator with hysterises as in this link circuit

              Blogger is a blog publishing tool from Google for easily sharing your thoughts with the world. Blogger makes it simple to post text, photos and video onto your personal or team blog.


              The hysterises function sets two operating points for the relay turn on and turn off. In that case bouncing is overcomed and the circuit is made automatic.
              Really? Please inform us. I mean really this is a 6-year old post we have been waiting 6-years to be answered. Please enlighten us with your superb knowledgge.
              MSEE, PE

              Comment

              • opanin17
                Junior Member
                • Jun 2016
                • 4

                #9
                Mike, this is not an alert function only, the circuit in the link has an alert for low battery and a disconnect function using either a relay or P mosfet. You only adjust the variable resistor when your battery is close your stop voltage to start your beeping notification.
                When the battery level reaches your desired turn off, you adjust the other variable resistor to switch your relay off. In this case because of the positive feedback, the relay will turn on after the battery voltage has been made to rise a little through charging.

                Comment

                • Mike90250
                  Moderator
                  • May 2009
                  • 16020

                  #10
                  I don't think a relay or mosfet is going to control a serious inverter. Maybe a small 5-20A load. after 20A DC relays get expensive, and 4Kw mosfets even more.
                  Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                  || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                  || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                  solar: http://tinyurl.com/LMR-Solar
                  gen: http://tinyurl.com/LMR-Lister

                  Comment

                  • opanin17
                    Junior Member
                    • Jun 2016
                    • 4

                    #11
                    No mike. You are not going to switch or control the main DC . You are only going to use the circuit to control either the switch cable or even connect it directly to your inverter IC shutdown pin. Check this post and see how its done.






                    Every inverter uses either of this.
                    Last edited by opanin17; 09-11-2016, 02:15 PM.

                    Comment

                    • bcroe
                      Solar Fanatic
                      • Jan 2012
                      • 5198

                      #12
                      Originally posted by Mike90250
                      I don't think a relay or mosfet is going to control a serious inverter. Maybe a small 5-20A load. after 20A DC relays get expensive, and 4Kw mosfets even more.
                      The good approach would be an electronic control if available to shut off loads, instead of just breaking the main
                      feed. Actually low voltage MOSFETS have gotten cheaper these days. Find cheap ones, and just parallel a bunch
                      of them; no issue with sharing in saturated mode. And use a simple Op Amp + Voltage Ref set up as your detector,
                      with either a flip flop or a lot of hysterises to drive the MOSFETS. Did this at work at the 48V 180A level. Bruce Roe

                      Comment

                      • clinecustoms
                        Junior Member
                        • Oct 2018
                        • 4

                        #13
                        Has anyone yet found a reasonably priced in line adjustable low voltage cutoff, like the battery savers on trucks? for 24v 60 or 80 amp max draw. looking for something independent to the inverter or CC cutoffs to really just protect the battery from going below say 22.5v at any given time like either under load or resting.

                        Comment

                        • Mike90250
                          Moderator
                          • May 2009
                          • 16020

                          #14
                          Most inverters have a built in LVD. Better ones have programmable ones. Your manual will state what the disconnect voltage is
                          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                          solar: http://tinyurl.com/LMR-Solar
                          gen: http://tinyurl.com/LMR-Lister

                          Comment

                          • clinecustoms
                            Junior Member
                            • Oct 2018
                            • 4

                            #15
                            Originally posted by Mike90250
                            Most inverters have a built in LVD. Better ones have programmable ones. Your manual will state what the disconnect voltage is
                            looking for something independent to the inverter or CC cutoffs. on occasion there are things connected to the battery not through an inverter or CC, in my case I have one system that is for a dvr and cameras, which I run direct to the battery as I do not want the controller shutting them off unless really needed, now that particular one is on 12v and not more than 7a however I am using a cheaper 24v which I would like a secondary backup shutoff if things go bad. this would be a total safety for the batteries and shut everything off until manually recharged above a set voltage.

                            Comment

                            Working...