    Hi all,

    I am building off grid solar systems that consist of:

    2 - 100 watt panels
    1 – 12 volt, 30 AMP battery charger- Max solar input 450watt
    1 - Pure sine 2200 power inverter – 4400 peak
    8- 35AH seal batteries

    Can anyone tell me what will be my back feed breaker AMPS?
    Maximum allowed PV breaker?
    Do I need a service panel or just a disconnect switch?

    Thanks for your help
  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #2
    As stated in your other thread the system is poorly conceived and designed and will not work.

    But to answer your question assuming the panels are wired in series there is no requirement for a breaker between the panel and CC.
    MSEE, PE

    Comment

    • inetdog
      Super Moderator
      • May 2012
      • 9909

      #3
      Originally posted by Willdog
      Hi all,

      I am building off grid solar systems that consist of:

      Can anyone tell me what will be my back feed breaker AMPS?
      Maximum allowed PV breaker?
      Do I need a service panel or just a disconnect switch?
      "Backfeed breaker" is use for grid tie, not for off grid.
      PV breaker? On the AC or DC side of the CC or on the inverter?
      You need a main panel of some sort for a totally off grid system, but since the source is not POCO it would not be called a service panel or disconnect.
      SunnyBoy 3000 US, 18 BP Solar 175B panels.